Compressor Runs Frequently: Too Much Leakage?

1/31/2019

8 Comments

 
We recently moved into a townhouse in a 5 unit complex. It consists of 2 buildings, each of which has both a wet and dry system.

Our unit's basement houses the equipment for one building and we have found that the riser-mounted air compressor serving the sprinkler system goes off approximately every 3 hours for 3-4 minutes. It's incredibly noisy.

The option of a Quiet-Series, tank mounted compressor is appealing, but I wonder if there's a significant leakage problem we should focus on first, given the short intervals.

Posted anonymously by a member for discussion. Discuss this  | Subscribe 
8 Comments
Douglas Krantz
1/31/2019 10:29:49 am

First off, check the size of the air tank on the compressor. If the motor runs only a few minutes at a time, that means that the air space inside the air tank is very small.

One possibility is that the dry system is leaking air.

If there is a big air tank attached to the compressor, however, and the compressor is able to fill it with air in just a few short minutes, then the air tank probably has a lot of water in it. The space that the water in the take takes up reduces the amount of space that the air can use.

Reply
Landon Veitenheimer
1/31/2019 11:32:59 am

He states that the compressor is riser mounted. I would think the the compressor has no tank at all.

Reply
James Armentor
2/1/2019 12:48:12 pm

Be sure to check all the air line connections on the riser with soapy water. In my experience most leaks are in the trim caused by vibration when the compressor runs. Therefore, the leak tends to get worse overtime. Pay special attention to any relief valves depending on the trim of the air maintenance device (regulator and trim) there will be a 1/4" relief valve that looks like a small pipe with a cap with a hole in it. It's adjustable. If set too low it will allow air to bleed down before the check valve that separates the air tank from the system. If all other possibilities are spent. A hydro test of the piping can show where the leak is. That's a last resort though.

Reply
Andy Kaempfer
1/31/2019 01:34:12 pm

Not sure on 13D/13R systems but if memory serves me existing sprinkler systems are allowed to leak 3PSI every 2 hours on commercial installations. Running 3-4 minutes every 3 hours doesn't seem like a very long run time or frequency for that matter. That's running for a culmitive of 32 minutes a day across 8 separate on/off cycles. If you know the capacity of the sprinkler system and the supervisory pressure you can calculate the allowable leak rate and make the judgement if a repair is needed. Typically riser mounted air compressors are sized volumetrically for system capacity (in gallons). If undersized the run times can get extended. If indeed a riser mounted compressor then it's likely an oil free compressor and oil free compressors are typically loud by most comparison. With all that said, the Quiet Series (I assume you're talking about the Q-Series by GAP) are very quiet. Almost unnoticeable if you're in the same room with it. Sounds more like the volume is complaint not the frequency or run time.

Sorry for the long winded response. Hope this helps.

Reply
Bruce O'Such
2/3/2019 11:26:52 am

Andy, Definitely... the volume of the compressor is a nuisance, it being a residence and especially as my wife's home office is directly above. Even a single start-up is a problem if it falls in the middle of a client call. So it seems the best course is to plan on replacing the compressor, following up with an investigation on possible leakage. Many thanks for the considered response

Reply
PETE link
1/31/2019 01:43:19 pm

The compressor may be responding to pressure changes in the system piping resulting from temperature differences in the air surrounding the pipe throughout the day. This would be exacerbated if the piping was directly beneath a metal roof or exposed to direct sunlight. Throughout the night, the temperature continues to drop, especially on a clear day/night, there is no cloud coverage to buffer the radiation from the earth to black-body space. Because it is riser mounted and there is no tank, the system piping is the tank for the compressor. You may be able to adjust the compressor maximum pressure limit up or down, as long as it is within the listing of the dry valve ratio to water pressure. Another option, depending on the size of the riser room, sound proofing the riser room may be less expensive than buying another compressor.

Reply
PETE
1/31/2019 01:45:08 pm

https://www.acoustimac.com/soundproofing-massloaded-vinyl-1lb50sf?gclid=Cj0KCQiA1sriBRD-ARIsABYdwwEEgc2XMh6Ov74Ic5qR-pwEfL_mpgXqGOshqYeDVuw7l3TEeiErukMaAkb7EALw_wcB

Reply
David link
9/1/2023 08:48:44 pm

It's definitely worth looking into potential leakage issues considering the frequent compressor cycling. Addressing any leaks could not only reduce noise but also improve the overall efficiency of the system. A quieter compressor sounds like a great idea too!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT