Combined Domestic/Fire Pump for NFPA 13R?

9/9/2021

9 Comments

 
I'm reviewing a apartment building that meets the requirements for an NFPA 13R system.

My questions: A pump is going to be required for this project and they are proposing to use a booster pump on the incoming waterline at the property line to reach the required pressure for domestic and fire demands.

Is a combined domestic/fire pump like this allowed?

It would be a private pump.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
9/9/2021 07:09:48 am

HI Anonymous,

NFPA 20 (2019) 4.7.1 states that “fire pumps shall be dedicated to and listed for fire protection service”. If you stop there, then you would simply install two pumps (one domestic, one fire) in parallel.

Although, reading further leads you to section A.4.7.1, which states that the above code section is not to “preclude the use of pumps in public and private water supplies that provide water for domestic, process, and fire protection purposes”. It states that combined pumps are not called fire pumps and are not required to meet all requirements of NFPA 20. The combined pump is permitted for fire protection only if “they are considered reliable by the analysis mandated in Section 4.6”.

In the end, since you won’t be providing a dedicated pump, I would reach out to the AHJ early on to discuss your design approach and make sure you don’t have any issues when it comes to receiving your permit.

Best of luck with your design!
Alex

Reply
Paul Pinigis
9/9/2021 08:13:10 am

Alex beat me to it. A single pump is permitted (as Alex explained in detail) and often has a reliability advantage because when there is a problem, it is immediately detected by those using the domestic water in the building. Therefore, it is more likely to be fixed when there is a problem.

Reply
Peter
9/9/2021 08:28:33 am

If the pump isn't dedicated to fire protection is it still inspected, tested, and maintained according to NFPA 25? The reliability of the pump is one thing in terms of "I know the pump turns on because my toilet still flushes", but NFPA 25 has prescriptive requirements for measuring flow and pressure (amongst other requirements) and comparing those readings against system demand and nameplate/original curve data. Not performing those inspection and test requirements wouldn't identify that the pump has degraded performance and now potentially does not meet system demand. In my experience with the hundreds of pumps we provide ITM on, the pump almost always "turns on and moves some water" but then fails to meet the requirements prescribed in NFPA 25 for performance.

Additionally, a number of states have different licenses for plumbing and fire protection contractors. Since the pump isn't dedicated to fire protection, would it be the plumber responsible for ITM or the fire protection contractor? Not having it dedicated would appear to be a long term nightmare.

Reply
Peter
9/9/2021 08:17:10 am

To piggyback off of Alex's comment,

NFPA 13R, 2016 9.3 The Water supply source shall be one of the following:

(1) A connection to a reliable waterworks system with or without a pump, as required.
(2) An elevated tank
(3) A pressure tank installed in accordance with NFPA 13 and NFPA 22
(4) A stored water source with an automatically operated fire pump

NFPA 13R, 2016 9.4 "Where a fire pump is installed, the fire pump shall be installed in accordance with NFPA 20."

To add some more color the A.9.3(1) states that "Private pumps taking suction from the waterworks system need to comply with NFPA 20, even if they supply both fire protection and domestic water uses, unless they comply with the same waterworks
industry standards for reliability and redundancy as the pumps owned by a waterworks utility"

The NFPA 13R handbook then also states "Subsection 4.7.1 of NFPA 20 mandates that fire pumps be dedicated to fire protection service. Therefore, it is unacceptable to supply domestic systems with a fire pump installed in accordance
with NFPA 20."

Since a combined pump wouldn't be considered a fire pump, it would also not have any of the ITM requirements for pumps in NFPA 25. I think you'd have a very difficult time convincing an AHJ that you want to put in a combined pump rather than a dedicated fire pump especially since NFPA 13R requires it.

Reply
Jesse
9/9/2021 08:35:07 am

Alex beat me as well.

I would highly recommend consulting your AHJ before doing anything though.

Reply
Bill
9/9/2021 09:08:07 am

As an AHJ my first question would be, is the pump required to meet the demand of the sprinkler system, or is it required to meet the demand of the domestic water? If it is needed to meet the demand of the sprinkler system, then I think NFPA 20 would apply.

Reply
John G
9/9/2021 11:19:27 am

They make domestic water automatic shutoff valves when the fire system activates.
I don’t know why, unless you are pumping from a tank, that you would want a pump on your domestic. Too high a pressure without pressure reducing valve would blow out your plumbing fixtures ( so boost pressure then reduce pressure ? Crazy) and a 4 head design can be accomplished with relalitively small piping with 40 psi which is average almost everywhere.
A fire pump……. I mean for 13d, or r , off domestic…..yikes. Waste of money.

Reply
Pete
9/10/2021 12:44:35 pm

Maybe check the Econo RFP System residential fire protection pump? It's designed for 13D systems more than 13R, but it's a specific residential fire pump.

Reply
Pete
9/10/2021 12:50:54 pm

Disregard this. 13R 9.4 directs fire pumps to be in accordance with NFPA 20. 13D does not have as strict requirements.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT