|
We have a project where the architect wants the combination sprinkler/standpipe riser installed within a rated shaft with a rated door to access both the system control valve and standpipe hose valve.
Aside from the gymnastics of the installation, we can't find anything in NFPA referencing standpipes within a shaft. The AHJ is considering it without an opinion just yet. Does anyone know if this is acceptable? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Glenn Berger
9/22/2022 08:07:07 am
It is permitted. Architects loves to hide this piping from view. Need to ensure that the valves are accessible with the panels being located correctly.
Reply
Dan Wilder
9/22/2022 08:10:06 am
Allowable, yes. Just need to provide signage accordingly.
Reply
Jesse
9/22/2022 08:10:53 am
Yep, this isn't uncommon. I have two projects ongoing in which we're doing this. Just make sure the AHJ is involved in the determining the hose valve access cabinets or panels.
Reply
Alex
9/22/2022 08:14:35 am
As others have mentioned, this is common. Need to ensure valves are accessible and any openings are rated.
Reply
Travis Mack
9/22/2022 08:26:57 am
Think about operations for a minute. Will the fire crews be able to connect to the hose valve and still stay in a protected space? They are in stairs because that is a rated shaft. The crews can be protected while hooking equipment and then exit the stair ready to attack the fire.
Reply
Todd E Wyatt
9/22/2022 09:34:25 am
See “NFPA 14 Standard for the Installation of Standpipe and Hose Systems” for minimum clearances (e.g. 3 Feet) of standpipe hose connections (handle of the valve) and any adjacent object ranging from fully open to fully closed.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
