Classifying Shipping Pod with Undefined Storage?

1/7/2022

10 Comments

 
What is the proper approach to classify a storage container that could be filled with any handful of miscellaneous materials?

We have a project and can't seem to get a straight answer from anyone, including the local plan reviewer. 

These are basically 8-foot tall steel shipping containers that are pod-type portable storage units, where people can load their belongings into them and these pods get collected inside this warehouse until the original owners need them.

The existing warehouse building has a CMDA system, designed at 0.38 gpm over 2,000 sqft. 

Has anyone here had experience going about classifying these shielded hazards with non-defined storage inside?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
10 Comments
Paul Pinigis
1/7/2022 08:08:49 am

So, what the sprinklers will see is a metal box with a fire inside. Since the contents are any mix of household goods, I would consider it a Class IV commodity.

Reply
Franck
1/7/2022 08:33:00 am

What you describe is part of the "grey area", where no straightforward solution exists. And is out of the scope of NFPA 13.
You cannot identify a proper commodity class, as some of them may be a class II or class III, while other could be a group A plastic, or even worse if they contain flammable liquids with no retention means, for example, or barbecue with gas containers that may explode, or ammunitions and fireworks...

But there are some good news.
What is the probability to have a fire inside ? Very very low as there is normally no source of energy (even though not nil, as you may have Li-ion batteries with a potential failure, or possible slow developing fire when you pack the stuff inside the container).
What is the probability to have a fire within the container to go out and spread to other one?
Very limited as well.
Why ?
Because when the fire inside the container will spread out of it, it will activate the sprinkler system at the ceiling level and if the other exposed materials are themselves inside metal box containers, the wetting and cooling effect from the ceiling sprinkler system, with the density you indicate, is much more than what would be required for an exposure protection of a building.
This means that everything inside the burning container will be lost, and items stored in containers directly agaisnt may be damaged to a certain limit (fire damages by conduction).

It is difficult to say that you don't have a potential issue. The only problem is that you normally don't know what is inside the box. But the probability to have a situation out of control is, to my personal point of view, very limited.
Just be sure to keep some seperation distance between the containers, so that the sprinkler protection from the ceiling can act as a cooling effect for exposed containers.

Reply
Alex
1/7/2022 10:30:44 am

To add onto Franks comment regarding the limited to no fire ignition, if you have lithium batteries, ensure you have thermal runaway measures. This is off topic but key when it comes to limiting hazards.

Reply
Dave
1/7/2022 11:15:02 am

For all we know, Schrödinger's cat could be in the box.

Reply
Casey Milhorn
1/7/2022 02:43:04 pm

And to make it worse, the storage classification for live cats is completely different than dead ones.... Dave, you just added a whole other level of complication to his issue.... lol

NK
1/7/2022 08:52:45 am

We wound up turning down a project like, but the plan we were proposing was to establish a floor plan with predetermined layouts of the pods, paint the layout on the floor, run a dropdown system with flex drops with sprinklers located in the places where you would be able to protect the pods if they were there. You would have to drill holes for pendents or sidewalls into the pods that can be used for sprinklers while inside, but can also be plugged while the pod is being used. Most pods I've seen are metal and be protected by 2 sprinklers. It's not covered by NFPA 13 or FM Global that I am aware of so I would talk to the AHJ and propose a calculation of 1 or 2 pods flowing at a time for storage up to 18" down from the deflector. In our area this would need to be signed and sealed by an FPE as well so their input would be needed. The best bet for a tenant like this is to lease space in a building that does not require sprinklers. I'm interested in hearing the results.

Reply
Glenn Berger
1/7/2022 08:55:59 am

Congrats - You are getting the same run-a-round that has become a standard practice. While there should be no ignition sources within the POD, AHJs do not accept this scenario.

For your particular set-up: Are the PODs stack on each other or are they placed within a rack assembly? What is the configuration that is proposed? How are the PODs moved around when they are received and then ready for transport out? What is the gross square footage of the facility?

These are just the basic questions that needs to be determined prior to picking sprinkler system configuration for this potential scenario.

Reply
Jesse
1/7/2022 08:59:54 am

This has been the bane of many of our existence for a long time.

Franck has a great answer.

Reply
Brian Gerdwagen FPE
1/7/2022 09:44:11 am

I have always used Factory Mutual Data Sheet 3-26 when I have had to design for something like this. "Highway trailers, trucks, boxcars, or similar metal vehicles with combustible materials with the potential for a shielded fire." It uses HC-3, 0.3/2500 if the ceiling is up to 30', and 0.5/3000 if over 30' to the roof. Last time I used this was for indoor RV storage, but it may be appropriate for your scenario if the containers are one level high.

Reply
Storage Services link
6/16/2023 07:54:20 am

Impressive! Thanks for sharing this.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT