Ceiling Pocket Rules Apply to Sidewall Sprinkler?

3/1/2021

5 Comments

 
Can the ceiling pocked omission rules outlined in NFPA 13 for standard spray pendents and uprights be applied to standard spray sidewalls?

​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Casey Milhorn
3/1/2021 09:44:19 am

Great question. So without mention of applicable edition, I'm referencing 2016 (personal preference, because I don't want to learn the new format of 2019 yet....lol).

It appears as if it is the intent of the committee to allow omission of sprinklers at skylights for both uprights, pendents, AND sidewalls since the skylight comment is sitting in the earlier section before it breaks down into head types. So the way I read it, skylights of 32 sqft or less would be yes.

Other ceiling pocket exlusions are exclusive to uprights and pendents (standard and extended coverage). They appear to purposely be left out of the sidewall sections. BUT, what is interesting is that it does not have the same clarity on residential sidewalls. It appears as if by purpose (or oversight) that the ceiling pocket rules could apply to residential sidewalls.

Also, just a few other things to mention. Sidewalls are listed typically (if not always) for smooth ceilings. Per the definition of smooth ceilings, you could almost rule out ceiling pockets of all types for all sidewalls, but that could be a gray area. Also, remember that structural elements aren't necessarily defined as ceiling pockets if that is the scenario you have, BUT because of the smooth ceiling requirement, that shoots out the use of sidewalls under exposed structural construction (unless there is something I'm missing or sidewalls that are listed for his specifically).

Reply
CJ Bonczyk
3/1/2021 10:02:22 am

Referencing NFPA 13 2019: In my opinion I would say no because code specifically provides the exception elimination of sprinklers within the pocket rules applies to standard spray and EC spray uprights & pendents as well as specific rules of residential sidewalls. No rules are indicated for standard spray sidewalls. Notice that residential sidewall ceiling pocket exceptions are different than upright and pendent pocket situations. Standard spray sidewalls depending on listing are 4"-12" down from the ceiling and have specific installation requirements below ceilings and soffits. Also depth of unprotected soffits are allowed to be up to 36" which would be unacceptable for sidewall use.

A key exception would be that looking at the definition of ceiling pocket per NFPA 13 2019 Handbook as it discusses certain minor depressions in ceilings can be protected by adjacent sprinklers (not specifying which kind). A example of a ceiling depressions is 8 in deep that isn't protected but is protected by sprinklers at the surrounding elevations that are 4 in below the ceiling at their locations. Such sprinklers are within 12in. of the high ceiling of the depression and as a result are in compliance with 10.2.6.1.1.1 and 11.2.4.1.1.1 requiring sprinklers to be within 1in.-12in from the higher ceiling.

Reply
Dan Wilder
3/1/2021 10:09:33 am

Referencing the 13-19' Ed.

No they are specific to the type of sprinkler:

10.2.9 Standard Spray Uprights & Pendents
11.2.8 EC Uprights & Pendents - *notable that the section starts with including EC Sidewalls but is specific to Pendents/Uprights when allowing ceiling pockets.
12.1.12 Residential Sprinklers - *This section does not specify a specific sprinkler orientation, only "Sprinklers shall be..."

I think the caveat is the definitions of the ceiling types and how they play into the sprinkler uses:

3.3.26.1 - Flat - Continuous ceiling in a "single" plane.
3.3.26.4 - Smooth - "Continuous" ceiling free from significant irregularities (ceiling pockets)

VS

3.3.25 - Ceiling Pocket "...bounded area of ceiling located at a higher elevation that the attached lower ceiling" which goes against the previous two definitions...

Reply
Franck
3/1/2021 12:11:36 pm

Just a guess (which could be part of a possible technical explanation): it is maybe related to the way sidewall sprinklers are activated in case of fire.

If the fire is below the sidewall sprinkler, the operation is similar as for an upright/pendent sprinkler.
If the fire is not located below the sprinkler, the heat plume and than ceiling jet to reach the sprinkler location is longer (then less effective/reliable) for sidewall than for other sprinklers.
It is one of the explanations for not allowing sidewall for extra hazard occupancy (in addition to the specific water distribution pattern).
And one explanation to have the ceiling as smooth as possible (more efficient ceiling jet toward the sprinkler location to activate it quickly).

If you have this in mind, you can understand when the ceiling pocket rule applies to sprinklers.
Depending on the configuration, you will have a chance to operate a nearby sprinkler (quick response) and you can omit protection in the ceiling pocket.
With sidewall sprinklers located on one side of the wall only, the ceiling pocket(s) will collect most of the heat and by the time you will activate your sidewall you may:
- either activate an unecessary large number along the wall
- or activate them very late, resuting in a possible uncontrolled fire condition for a large area.

I would personnaly not apply the ceiling pocket rule with sidewall sprinklers.

Skylight is slightly different because it is smaller in size and there are usually enough distance between 2 adjacent skylights.

Reply
Mark Harris
3/1/2021 06:33:43 pm

Well said Franck. Had a hotel project that limited number of suites had beam ceiling features and GC did not understand why those rooms needed different protection than the single sidewall in most of the rooms. I said because we don't know where the fire will start and need smooth ceiling for the sidewall listings.. I

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT