Can Sprinklers Be Installed In Gap of Ceiling?

1/10/2023

10 Comments

 
The architect has specified a solid panel ceiling in an 8-ft wide corridor.

The ceiling has a 4-inch gap that extends the width of the corridor. The gap is spaced every 8-ft.

The architect would like us to locate the sprinklers in the gaps so the ceiling has a clean look. The gaps are open to above. There are no sprinklers above the ceiling.

I believe the sprinklers should be installed in the solid part of the ceiling, not the gap, so heat can collect and activation is not delayed.

Am I correct?

​Thank you in advance for your responses.
10 Comments
Dan Wilder
1/10/2023 07:30:36 am

You can provide sprinkler protection within the gap based on 13-22 9.5.5.3.1.2 (2). It shall be within 3" to the side of the obstruction and it must utilize a water shield.

But as I write this, your statement indicated no protection above, making this a ceiling with small openings or maybe a cloud ceiling scenario not an obstruction to discharge issue. So assuming you have all the criteria met for the space above to be unprotected...

9.2.1.1.1 states the space above can still be considered concealed with small openings
9.2.1.1.2 limits these openings to 20% of the overall ceiling total area(or plane...assumed to be flat) and gaps greater than 4' long (the 8' wide corridor) shall not be more than 8" wide (your scenario states 4").

So now continuing to "Cloud Ceilings"...I don't think this would directly apply with the gaps already complying with 9.2.1.1.1 but in case some additional back up is needed.

9.2.7 - 20' max, smooth construction, gap no greater than 1" per foot of elevation, QR used, EC no greater than 16' O.C.

I don't think heat collection is a concern with this design scenario.


Reply
James Job
6/14/2023 02:10:43 pm

What size gap is allowed in ceilings based on NFPA 13, 2013 EDITION for us not to provide sprinklers above ceilings?

Reply
Anthony
1/10/2023 07:39:31 am

If you've met the cloud rules of NFPA 2016/19 you'll need to be in the cloud I believe though the code does not explicitly say so.

The code does require all sprinklers to be installed per their listing. So, for a recessed head that means in a ceiling same for a concealed head.

If you provide sprinklers above the clouds you can use the code below to provide sprinkler below and obstruction. However, I don't think this would be considered "best practice"

13-16:
8.5.5.3.1.1 Sprinklers shall be located below the obstruction
and not more than 3 in. (75 mm) from the outside edge of the
obstruction.

Reply
Anthony
1/10/2023 07:41:23 am

I'd add if the cloud is at 11'' from the deck its moot because the sprinkler deflector will be at 12'' and below the obstruction and within the code. Unless I'm missing the 3x rule here?

Reply
Glenn Berger
1/10/2023 08:39:24 am

I suspect the "gap" has been provided for some form of ventilation without physically supply diffusers or grilles. I do not believe that cloud ceiling rules apply to this circumstance.

I would agree with you that the sprinkler should be placed on the solid portion of the ceiling assembly.

Reply
Casey Milhorn
1/10/2023 08:41:03 am

Dan nailed it again. I would approach it the same exact way he has stated. This "3 inches from the side of the obstruction" thing is either new for the 2022 edition (maybe it showed up in 2019, can't remember). So the only issue you may have is if the project is under an older NFPA 13, and the AHJ doesn't recognize newer editions.

Reply
COLIN LUSHER
1/10/2023 02:58:42 pm

Been there since at least 2016 version....one of those things you don't notice until you need it.

Reply
Casey Milhorn
1/10/2023 05:00:44 pm

Well NFPA 13 2007 edition still seems new to me if that tells you anything.... lol. I'm not good with time...

I think I cut my teeth on the 1991 edition, or whatever was before 1996 ed.

Jesse
1/10/2023 08:57:44 am

Not much to add to what Dan wrote, other than lamenting about the problems architects create for us.

Reply
Mike M link
1/10/2023 11:01:57 am

Request additional information from writer, how long is the corridor, 4” wide by 8 ft gaps can add up to a large open area. Is it a return air plenum above, do the corridor walls extend to the deck above?
More than sprinklers involved with this scenario.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT