Can ESFR Be Used for Extra Hazard Group 2?

2/8/2023

13 Comments

 
I have a situation where I need to protect a modular home manufacturing facility.

It has a paint both that's self-contained with its own sprinkler hookups, all the regulars of a tiny home making shop basically. They will have rack storage of wood products up to 20' high and wanted the design to be such that they could move the storage rack locations in the future if they wished.

NFPA 13 (2016) A.5.4.2 gives a list of some Extra Hazard Group 2 occupancies and it specifically lists (4) Manufactured home or modular building assemblies (where finished enclosure is present and has combustible interiors) I had made the assumption that ESFR was a worst case, safe bet design for the entire facility due to the amount of water you get from heads opening up.

The contractor is concerned with how code says one thing in one place and something open to interpretation in another place. Section 8.4.6.6 says "ESFR sprinklers designed to meet any criteria in Chapter 12 through Chapter 20 shall be permitted to protect light and ordinary hazard applications."

That's fine, but I just see that as just a statement.

When you get to the requirements for Storage, Section 12.6.7.1 says the following: "ESFR sprinklers designed to meet any criteria in Chapter 12 or Chapter 14 through Chapter 20 shall be permitted to protect any of the following: (1) Light hazard occupancies (2) Ordinary hazard occupancies (3) Any storage arrangement in Chapter 13 referencing OH1, OH2, EH1, and EH2 design criteria"

Item 3 is where I want to make the argument that we can in fact use ESFR sprinklers in an Extra Hazard Group 2 scenario.

Can ESFR be used for an Extra Hazard Group 2 situation like this?

I need some expert opinions/interpretations. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Dan Wilder
2/8/2023 07:45:30 am

Hoping to learn from this one but my thoughts...

I don't see a correlation between an EH design and the Storage Chapters to apply an ESFR design criteria? The allowance for Light & Ordinary designs with ESFR came more from storage buildings being designed with ESFR sprinklers and then having offices move in and not requiring a change out of sprinklers (Need to look in the meeting notes from 2013 when the text changed going into 2016).

I think that the shielding created by the buildings in construction below would exceed a typical calculation area of an ESFR design (4x3). ESFR also isn't allowed with solid shelf storage without additional protection in place. As you stated, the amount of water from an ESFR sprinkler would seem to be enough for an incident however this also can be a hinderance when more sprinklers open and the water supply is exceeded.

Most of the ESFR storage sprinklers I quick checked have no mention of Extra Hazard and are specific to different criteria within the storage chapters, but other large K-Factor sprinklers (CMDA K25 sprinklers) do list EH as an option per NFPA 13 criteria.

Reply
Glenn Berger
2/8/2023 08:14:30 am

In addition to the excellent statements made by Dan above, I recommend contacting various mfg of ESFR sprinklers as the allowable conditions do differ. With that said, you did not provide any information on the building construction for which you are protecting. That is another variable that needs to be considered.

Reply
Mike Morey
2/8/2023 08:16:57 am

As Mr. Wilder stated, the allowances to protect "occupancy group" designs with ESFR is limited to LH and OH. The later reference in the storage chapters is specifically for Low Piled/Misc storage and any other storage occupancy in the storage chapters that calls out an occupancy group protection scheme as being sufficient. Manufacturing and similar extra hazard facilities differ greatly in their fire loading and development and were not contemplated when ESFR was extended to protect other occupancies. As mentioned, LH and OH were added for ESFR warehouses with office, break, restroom, mechanical room, etc occupancies peppered throughout with and without ceilings to be protected without having to remove and replace ESFR sprinklers that would clearly put out a fire in those scenarios. It also helped ensure Shell/TI buildings were fully sprinklered at final inspection rather than owners trying to convince AHJs to accept wait and see on office shell areas etc.

Reply
Anthony
2/8/2023 08:29:21 am

ESFR isn't a better sprinkler it's a specific sprinkler. If NFPA 13 calls out EH2 specifically then you need to engage with your AHJ at a minimum. ESFR is specifically designed and tested for storage arrangements not open floor space and manufacturing.

There are 2 differences between EH2 and ESFR.
EH2 will have a remote area 2x larger and hose stream 2x larger.

Here's my best go though:

ESFR will have an effective density that's 2x (or more) as large.

eg: K25.2 @15 psi = 97.6 gpm --- over 100 sqft = 0.976 gpm/sqft

Total minimum flow for EH2 + 0.4gpm/sqft * 2500 sqft = 1000 gpm

Total minimum flow for our example: 12 head s* 97.6 gpm = 1171 gpm

You could argue the stringent installation obstruction requirements, total greater volume of design flow and increased per head discharge would make for a reasonable acceptable approach of using ESFR over EH2. If there is storage there already, you could extend the storage system over the production area without the use of draft stops for one contiguous system.

I, however, would not make this argument. Simply because you cannot properly classify which ESFR discharge criteria you are working with. Building height is easy, obviously, but the commodity class and storage height is hard not nonexistent for your case.

I'll end where we started: ESFR isn't a better sprinkler it's a specific sprinkler.

Reply
Jesse
2/8/2023 08:34:40 am

ESFR is a completely different design approach. So whereas, NFPA 13 allows ESFR to be used in OH2 occupancy hazard class areas, its doesn't for EH.

The sprinkler is the other issue. I'm not aware of any ESFR sprinklers listed for EH areas.

Reply
Casey Milhorn
2/8/2023 08:54:11 am

I think I'm in agreement with everyone. If you are the EOR for this project, I would be hesitant to make the assumption that ESFR's are equivalent. If you are the fire protection contractor, I would DEFINITELY not make this leap.

If you are the EOR and have the resources and time, I would investigate any fire testing that was done on mobile home production (I would imagine there has to be some out there). Even though tiny houses are somewhat of a new trend, especially building them in interior production facilities, mobile home construction has been around for 60+ years. Some of these units can be up to 2000 sqft or more, but if I had to guess typically are never more than 1000 sqft per "half". The production process and materials used should be very similar. I would also want to know how close in proximity they are being stored to each other, and on the other end how the raw materials are being stored (where ESFR might be the correct call).

I would think separation of the finished units would be key here as to give the roof system a chance to activate before the fire could spread to additional units. These tiny houses would do a great job of shielding the fire from the sprinkler system, giving a chance for the unit to become fully engulfed. If a case could be made that units were adequately separated, then ESFR might be the correct call to allow for future modifications to the assembly/storage areas.

Just my two cents and I would definitely get some additional insight from someone that has experience in protection of mobile home or tiny home manufacturing.

One last thing, just because someone has a great idea on how to manufacture or store something, doesn't mean there is a correct/adequate solution from the fire sprinkler industry. Sometimes the owner just needs to stop and change the way they want to do things, or get everyone to accept the increased risk which is rolling the dice for everyone involved.

Great question!

Reply
Brad K
2/8/2023 09:00:32 am

Interesting question. One consideration when comparing OH/EH design density with ESFR calculations. Recall that Quick Response / Fast Response elements are not permitted for use with Extra hazard occupancies. Ref 2019 NFPA 13-10.2.3 and 19.3.3.2.2.2. Perhaps arguments can be made either way since 10.2.3 mentions density/area design method. This could become a sticking point in negotiations.

Reply
SAFPI Sebastian Stecyk
2/8/2023 09:12:27 am

In my opiniom, IT is not possibile.
Acc. with point 19.3.3.2.2.2 and 10.2.3 od the NFPA 13 is not permitted to use QR sprinkler.

RTI of the QR sprinkler is below 50 and the same or very similar like ESFR.
Regards

Reply
JI
2/8/2023 10:37:42 am

While I think the advice here is pretty much on the side of ESFR protection and Extra Hazard are different hydraulic designs, I do have a recommendation.

I would design the piping system so that way the lines and mains can handle both the EH2 and ESFR situations hydraulically, along with using the more stringent ESFR installation criteria for obstructions. Depending on the sprinklers to be used, I would install 3/4" or 1" outlets (and maybe use 1" outlets with 3/4" bushings) in the pendent position so the only modifications in the future would be to swap out sprinklers assuming the right elevations for the different deflector requirements can be work on site. Most sprinkler manufacturers provide a pendent version of their extra large orifice sprinklers. The same can be done with uprights, but the upright ESFRs are not always allowed in all storage arrangements.

Reply
Jonathan Worden
2/8/2023 10:43:53 am

Great question! Definitely learned something myself on this one. I, like many others probably immediately assumed more water = ability to protect higher hazard. It appears it's not that straight forward.

I think the key word here is "storage"... (3) Any storage arrangement with OH1, OH2, EH1, and EH2 design criteria.

While the type of occupancy you described may be EH2, it is not storage. Think of it more in terms of arrangement of commodity and less in terms of what's actually burning. NFPA storage standards are based on full scale fire test and past loss fires. A number of factors go into developing the standards related to storage such as commodity class, storage arrangement, storage height, clearance from top of storage to sprinkler just to name a few.

With the occupancy you described (manufactured home or modular building assemblies), you will certainly have shielding of combustibles. NFPA 13 recognizes this as severely impacting the performance of ESFR sprinklers.

The following was taken from NFPA 13 (2022) Section 23.1.1 Commentary:

Systems protecting extra hazard occupancies are specifically left out of this discussion because ESFR sprinklers are not permitted to be used in systems protecting extra hazard occupancies due to the potential for shielding of combustibles. Many extra hazard occupancies have equipment or construction that will shield the combustibles from any fire sprinkler discharge at the ceiling/roof. ESFR sprinklers are not designed to protect hazards where the combustibles are shielded. Therefore, extra hazard occupancies have been specifically left out of the list of permissible ESFR uses.

ESFR sprinklers are also permitted to be used for the protection of storage arrangements requiring protection as an ordinary hazard Group 1 (OH1), ordinary hazard Group 2 (OH2), extra hazard Group 2 (EH1), or extra hazard Group 2 (EH2) design under the provisions of Chapter 4. While the design criteria for EH1 and EH2 are quite similar to that prescribed for extra hazard occupancies, these storage applications under Chapter 4 would not include a shielding hazard as might be the case with other extra hazard occupancy designs.

Cheers!

Reply
Sebastian Stecyk
2/8/2023 11:28:07 am

I found in NFPA 13 some additional information regarding use ESFR sprinklers in EX1 i EX2 hazard. You can also see point 14.2.7 and point 23.1.1 - NFPA 13, edition 2022,
Especially additional comments in Handbook of the NFPA13 for 23.1.1 point is very important.
I think that is problem with protection of flammable liquids and materials with similar properties and occupanncy defined in EX1, EX2 or shielding hazard.
Acc. to 23.1.1. point, ESFR sprinklers could be used in storage arrangement under Chapter 4 if you have classification EX but only for storage area.

Reply
Franck
2/8/2023 02:58:15 pm

ESFR are specific sprinklers (as indicated above) to suppress fire over a small area with storage occupancy.
They are not designed to control a fire for a process occupancy.
As stated above, small less hazardous occupancy in a storage area is acceptable, but this is not your case.
Too many possibilities to open more ESFR than the design and overtax your system.
A simple sketch would show you how it works for the requirement of 12 ESFR. If the fire starts in the center of the rectangle made by 4 ESFR, you may expect to open the 4 of them. And if the fire extends a bit beyond, you will open the second rows, resulting in… 12 sprinklers (not 16 as you consider an expansion as a circle from the start point).
Now, if there is any condition that could require the opening of sprinklers beyond this “second row”, your fire is out of control…
This is also why they need to be fast operating : suppress the fire as soon as possible, don’t open sprinklers beyond…

Reply
Chris
2/13/2023 10:17:59 am

I agree with basically everyone else, ESFR's are only for storage applications, so if you have an area that isn't storage and is EH you cant use ESFR in that area, and I would say it also needs to be in a separate compartment from the ESFR's so you are not mixing SR with QR/FR.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT