MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Can a Hydrant Flow Test Use Only One Hydrant?

11/29/2023

16 Comments

 
Can a hydrant flow test (for the purposes of a fire sprinkler design) be conducted using a single hydrant?

If so, how is this actually done? Is it recommended?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Dan Wilder
11/29/2023 07:38:56 am

NFPA 291

4.4 should be followed where 2 (or more) hydrants are utilized to define water supply as shown in Figure 4.4.4.
 
Can you perform it in this fashion, yes and the process would follow 4.5.

Should you, IMO, no as it does not accurately define a water supply, only the ability of that hydrant to flow the measured amount at the measured static/residual. It's the butt gauge on one 2½" outlet and the pitot/diverter/hose monster on the other 2½"/pumper outlet.

Quick search for a pic gave me this: https://bigislandgazette.com/fire-hydrant-flow-tests-scheduled-for-hilo-shipman-areas/

However, there are times when this is the only method available. It's typically worse than performing the test with 2 hydrants. If at all possible, try to find a nearby domestic/commercial backflow (test port #1 on the supply side or #2 if you need to close the valve to take the plug out) or other direct connection to the water supply to pull the static/residual.

Reply
Glenn Berger
11/29/2023 08:08:31 am

Dan gave an very good detailed answer. In Summary:

Can it be done? yes

Should you trust the results? NO

Reply
Anthony
11/29/2023 08:27:16 am

I agree with Glen and Dan here.

Reply
sean
12/31/2023 06:55:12 pm

the one hydrant method throws so much into that one point makes an issue that I really don't trust the numbers that come from it.

a two hydrant test can be messed up so easily that a one hydrant test is just that much more fraught with issues.

Reply
M. Newell
11/29/2023 08:19:14 am

AFSA just put out a posy about this on linkedin/facebook. It can be used to verify capacity of the hydrant but should not be used as a water supply evaluation. I would recommend following them on social media they have good informative posts about questions they get.

Reply
Alex
11/29/2023 01:22:53 pm

Agreed! I just read that. Highly recommended.

Reply
Chris
11/29/2023 08:30:17 am

If you are doing a flow test and by yourself, there are ways to do this and still flow 2 hydrants. What I have "heard" before was to use your phone to video the test hydrant while you flow the other. Then you can review the video after to determine the before, during, and after pressures.

***Note, in the summer heat you may need to make sure that your phone doesnt overheat!!!

Reply
Dan Wilder
11/29/2023 08:41:54 am

I've done this several times....just make sure that when you start the recording and set the phone down, you don't turn the recording off or the phone isn't angled to pick up the gauge or being pointed into the sun AND you check the recording prior to packing up....or plan on redoing the test (practice makes perfect I'm told...)

Reply
Jesse
11/29/2023 08:35:56 am

Dan is on the money here.

"Can" it be done? Yep. Should it be done? Probably not.

Reply
Casey Milhorn
11/29/2023 08:49:51 am

Yes, can be done and sometimes it's your only option. Will everyone accept it, no. Would I do it for an ESFR system, or other high demand system, no. Would I do it for sizing a fire pump, no. Would I use it for a residential or light hazard project, yes, but only if that was the only hydrant available. Also, there are situations where the city doesnt have reliable info on their system arrangement, closed valves, etc and the gauge or flow hydrant can't be verified if on the same system/zone. In this case I do a one hydrant and a two hydrant test and compare results. I really think the most important thing is to use commonsense in all situations, do your homework, and cover your tail. If you or your team doesn't understand the purpose and nuances in performing a flow test, stick to the book and ask someone if you run into a new situation or have concerns.

Reply
Jack G
11/29/2023 09:03:56 am

Agree that it is a bad idea.
What I found ( hydrant with 2 outlets at least ) is :
When you have no choice:
Gauge one side - treat it like it’s on a separate hydrant.
Collect the static pressure.
Open the other side ( in theory this should give you the pitot pressure for flow , but not the true residual pressure ) - pitot psi equal or near gauge psi, pressure there treat as residual pressure.
The resultant test will give you something to approximate a calculation, however the “ residual pressure “ will be lower than the actual residual pressure. This test could be used to get a permit but another flow test should be done.m
This is what I was shown when first breaking into the industry, 57 years ago, by an FM inspector in the Phillie area. ( FM had properties in the area, lower Delaware with nothing around.
I only ran into a one hydrant situation a couple times.
In those cases, after bringing in the underground supply, I would gauge the hydrant and flow the stub up ( placing a test header on it ) for actual flow at the base of riser. The Fire Marshals loved that test, for accuracy.
The one hydrant test is not recommended for a final hydraulic calculation.

Reply
Patrick Spillane link
11/29/2023 09:21:19 am

Just to clarify, NFPA 291 is a recommend practice, and not a standard, so there is a grey area.

For the purposes of design work, the Main Capacity Test (2+ Hydrants) should be performed.

The Hydrant Capacity Test (single hydrant) should be performed when evaluating and marking the hydrant for Fire Fighting purposes. (AA- Green, 1500GPM+, etc..)

Performing either test, you are always looking for 3 data points. Static Pressure, Water Flow in GPM and Residual Pressure.

When perform a single hydrant test, you will need a Gate valve (For steamer port, or 2.5" port), a Test Gauge Cap, and your water flow measuring device (ie Hose Monster).
Once you have all three data points, you can enter it at the free Fire Hydrant Flow Calculator on https://hosemonster.com/resources/hydrant-flow-test-calculator/
to determine with Main or Hydrant capacity at 20 psi.

Reach out if any questions. [email protected]

Reply
James Art, FPE
11/29/2023 10:33:33 am

Perhaps you can get the static somewhere else that is close ?

Pressure is pressure, so IF there is another connection,
like a Fire Sprinkler riser or water service* you may be able to get residual pressure from before *upstream" of other devices, like a backflow.
Some check valves are also equipped with plugs upstream of the clapper, so sometimes you can remove and use that.

Industrial: IF this is on a private fire loop, with hydrants, pressure on a riser, below the alarm check will do well.

*If this is a neighbor, you may need permission, and to be sure it is on the same line.
--------------------------------------------------------------------
Residential: For small 13D systems I sometimes ask for a domestic pressure, measured at a faucet or hose outlet (also sometimes at a neighbors) as a Preliminary, just to get an early idea of what pipe sizes may be needed.

Note for large houses, if you are sprinklering anyway it makes sense to go to a 4 sprinkler** calculation (or use 13R) to also protect the building.
I recommend that,
and several AHJs that I support have that in their Code Adoption.
Often the line is at 5000 sq. ft, or three stories.

**These are fire "sprinklers", not "heads"
A head is the bathroom on a ship!
Or an indication that a plumber may be in over his head!!

Reply
Fred Walker
11/29/2023 08:51:28 pm

Let add my concurrence to everyone above.

Mutiple hydrant (test and separate flow hydrant) should always be used for design and for network analysis.

Single hydrant test/flow may be used for system health testing and hydrant ITM efforts. But anytime significant variations between test occur, additional analysis is always prudent especially if you are providing an engineering report (signed, sealed, or stamped).

Reply
Chris
12/1/2023 02:26:49 pm

I would say a single hydrant should not be used for supply analysis if there are other options. Videoing a static/residual gauge is easy to do. There are some people that will recommend gauges that are digital with a "minimum pressure" recall feature to obtain the residual pressure on the gauge hydrant. But after evaluating that, against a regular gauge that is being observed, the "recall" gauge will read a lower pressure than what is observed on the regular gauge after the pressure settles once all the water is moving, and in my experience it can vary between 5% and 20% of a difference. So I used to tell guys it was fine for doing a pre bid flow test for estimation purposes but for the actual design it wasn't to be used.

Reply
Jim Amy
1/13/2026 03:01:04 pm

A single hydrant test is not a good measure. I have an old insurance manual with an appendix where this is discussed and they provide corrections for the residual pressure to account for turbulence in the hydrant (e.g. increase residual pressure by 7 psi for a flow rate of 625 gpm). That is beside the point though since the pressure in the hydrant is not the same as the pressure in the main. The pressure in the hydrant incorporates the pressure drop from the water flowing from the main to the hydrant and that value can vary based distance of the leg to the hydrant and elevation of the hydrant as compared to the main. While the elevation issue also shows up at the test hydrant when using a two hydrant flow test, we can at least find that elevation and account for it. We cannot add back in the pressure lost from the main to the hydrant. Bottom line is that is is a bad idea and should be avoided at all costs. Having completed over 1,000 fire hydrant flow tests, my team has never had to resort to a single hydrant flow test. There has always been another option.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT