I have an inspector who wants me to prove that calculating run or through tees is appropriate for 13 Residential systems.
I showed them that run tees are in 13D, he thinks they should be calc'd in 13? How do I prove something is not in a code? Any help would be appreciated. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Jorge Diaz
10/3/2019 10:59:34 am
Is this what you’re looking for?
Reply
Wayne Ammons
10/3/2019 11:25:44 am
I think what he/she is asking is, since NFPA 13D (2019 Edition) Section 10.4.2.3(6) states that "The system shall be hydraulically calculated in accordance with the provisions of NFPA 13, except that the friction loss straight through a fitting shall be included", why wouldn't you have to calculate that loss in a 13R system?
Reply
Shannon
10/3/2019 01:22:22 pm
10.4.2.3 refers to the use of 1/2" nonmetallic and copper piping. I've always read that section as "you only calc TRs if using PEX or flex copper".
Shawn
10/4/2019 09:19:27 am
If the fittings are CPVC the ID is reduced due to the way the fittings are constructed.