Butterfly vs. OS&Y Valves on Backflow Preventers

6/17/2019

6 Comments

 
Is there a reason why OS&Y would be better on backflow preventers for fire suppression systems over butterfly valves?

One application where we often must use the OS&Y is when the backflow serves a fire pump and we don't want to distort the flow and cause cavitation at the pump - but otherwise the butterfly valves are a major space saver. Just curious if others feel differently or if I'm missing a major benefit to the OS&Y type.

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Rusty Scott
6/17/2019 10:29:52 am

These are just my thoughts and don't have any real backing but most of the backflow preventers that have been submitted to me that had the butterfly isolation type (our specifications call for OS&Y type) the components appeared to have a lot of plastic components which as an engineer makes me hesitate. The name brands also tend to be of companies I've never heard of and for the main shutoff to the building I would not want it to be plastic component based. As an engineer you are protecting the client and we deal with a large variety of contractors that seem to be more concerned with saving on cost, labor, and easy of install since their contract prices are locked. Let me put it this way, I do specify the butterfly type but have allowed it on low budget projects after expressing the concerns to the owner/architect. Also I think if you have a butterfly type and a fire pump, it is required to be 50 ft from the suction flange of the pump. 10 pipe diameters away if its OS&Y type.

Reply
Rusty Scott
6/17/2019 12:09:32 pm

Correct on my poor typing skills, *"I DON'T specify the butterfly type"*

Reply
Jevarajan
10/7/2020 12:45:44 pm

Can show which clause stating 10 pipe diameter for OS&Y gate valve.

Reply
Paul
6/17/2019 11:18:37 am

Interesting perspective from Rusty's side, being on the design-build side I have heard it is because Consultants/Engineers don't trust them (furthering Rusty's point). He is also correct as far as the 50 ft rule (NFPA 20 ('16): 4.15.5.1).

Another reason I have heard is for ease of replacement (bigger and heavier but easier to align and man-handle... I dont know how much I subscribe to that school of thought).

And yet ANOTHER reason I have heard is there is they are much easier to see the valves status from a distance, and what most maint-engineers are used to.

So I would say a combination of specification and owners. I have received specs that initially called for OS&Y and after discussing with the owner and owners engineers I was able to go with BFY. in another similar situation I was not able to get them to change their mind because it was a large institutional setting where all their other systems and pump rooms had the same OS&Y and backflows and that was what they knew and "were used to". And the customer gets what the customer wants, even if that means charging them more on labor replacements down the line!

Reply
Cordell Beache
6/17/2019 07:57:43 pm

The OS&Y gate valve on the backflow device should never be used as the OS&Y valve on the suction side of the fire pump. The backflow device must be located a minimum of ten pipe diameters from the suction flange of the fire pump. If a backflow device is required I would recommend using a device with OS&Y valves rather than butterfly valves to reduce any turbulence in the suction pipe.

Reply
Anonymous
6/18/2019 10:36:58 am

Good question. Aside from fire pump applications, FWIW, personally, I prefer butterfly valve backflows for savings including in weight, size, and ease of installation, if the assembly has gone through the rigid USC testing. One argument I have heard for OS&Y is that it's easier to swap out or repair an OS&Y tamper switch without taking the system out of service than to repair a backflow butterfly valve. But how often have you seen a butterfly valve that is rarely operated fail? OS&Y tampers on the other hand can get knocked out of adjustment. Butterfly valves, though a special valve that one cannot purchase separately (and should not swap out from a listed assembly anyway) are serviceable/repairable. (Vault locations in areas prone to water infiltration I would still use OS&Y to raise the tamper higher.) So my personal opinion is that for in-building applications, the industry standard has shifted to butterfly valves, and at least in my local area, that is what is commonly stocked. I have colleagues in strong disagreement with this however, and specs are slow to evolve.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT