Most cities require fire flow tests before design and calculation of a sprinkler system, but I have dealt with a few cities that instead use a water modeling system to calculate the pressure and flow at certain locations.
What is the reason for this? Are there benefits or downsides to one or the other? Is one more accurate? Thanks in advance - appreciate the input. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Ray Jackson
9/14/2022 08:07:17 am
I have not heard of this, but... I am old school, give me a flow test everytime. It's worked very well years. If it ain't broke, don't fix it.
Reply
Connor
9/14/2022 08:19:31 am
I would say the models are useful, and they can give importand data such as seasonal fluctuations. A flow test is necessary during the shop drawings phase to see the current condition of the piping and if there are any issues. The model doesn't know if a valve was closed since its last regular inspection, for instance.
Reply
Dan Wilder
9/14/2022 08:21:58 am
To prevent the loss of water from the system along with any potential secondary effects like water hammer and/or property damage is my guess.
Reply
Dwight H Havens
9/14/2022 08:32:25 am
Either method works. Both depend on the accuracy of the assumptions used to develop the data and results. My personal bias is to flow tests, but you must recognize that a flow test only represents a single point in time, and without broad knowledge of the operating characteristics of a water supply source may only be of limited value. A good model will allow one to evaluate water supply availability 24/7/365 and allow you project potential changes to the available water supply over time. Given the expected life of a fire suppression system, there are many factors that need to be watched to ensure viability of the fire suppression throughout its useful life. Water supply is only one of them.
Reply
Casey Milhorn
9/14/2022 09:05:05 am
Everyone pretty much covered it, but I will say it's probably going to be the way things are going so get used to it. I personally like the liability being on the water purveyor and I also like the fact that they are modeling (hopefully) daily, weekly, monthly, seasonal fluctuations that may be occurring. As someone else said, I just hope that the water purveyor is doing annual flows on their hydrants to verify what the models show.
Reply
Franck
9/14/2022 11:00:14 am
As indicated by Casey, if you go to modeling, check anyway if an actual flow test confirm the expectations.
Reply
Aviv
9/14/2022 11:02:59 am
Sometimes it's required due to draught conditions. For example, it is highly encouraged in California:
Reply
Chris
9/14/2022 11:16:24 am
How new are the models they give you? The only locality I deal with that does water modeling will sometimes provide a model that is 3-4 years old so I am not a fan of that, so we will go do an actual flow test when possible.
Reply
Kelsey
9/14/2022 11:16:49 am
In my area, we almost exclusively use municipal models. Very rarely do we have to go out and do a flow test ourselves.
Reply
Glenn Berger
9/14/2022 11:52:38 am
Modelling is not accurate. Modelling may or may not be validated by a flow tests. Hydraulic models are only as good as the input assumptions that cannot be verified.
Reply
Jesse
9/14/2022 12:21:15 pm
Flow characteristics are the foundational basis of AS design. I don't like using exclusively modeled data as the basis of design. I will always opt to physically flow water.
Reply
Bill
9/14/2022 12:46:33 pm
I’d plan on getting used to models, if for no other reason than water conservation alone. Consider all the water discharge from a fire sprinkler system in one year, then multiply that by how many systems, and you have a lot of discharge! Then throw on flow tests… it’s a lot of water that we can use for fire fighting, etc.
Reply
Jim Buchanan
9/14/2022 02:23:57 pm
All are solid points. However, Bill’s thoughts regarding water conservation address our future, which is reality, or soon will be…
Reply
Travis Mack
9/14/2022 01:00:35 pm
Model is the way to go. If you are only accepting physical flow tests, why are you accepting fire sprinkler systems without flowing the design area fully?
Reply
Jay
9/16/2022 10:39:16 am
Chicago flow tests their water supply system. If your requesting flow info in an area they haven't tested in a while, they run the test and send you the results.
Reply
schulman
9/20/2022 01:38:19 pm
i've never seen water leave the atmosphere ... and Flow Tests are real
Reply