Are Multiple FDCs Allowed on One Building?

3/12/2020

12 Comments

 
Hi there, just reviewing NFPA 13 for the number of Fire Department Connections allowed on any one building.

I see NFPA 13 16.12.5.6 indicates that sign is required if an FDC only serves a portion of the building. Does it state that only one FDC per building is allowed, or can you have multiple FDC's on one building? Thank you.

​​​​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
Wayne Ammons
3/12/2020 09:21:07 am

NFPA 13 (2019 Edition) does not state only one FDC per building is allowed, but your local fire or building code may require multiple FDC's to be interconnected.

Section 16.12.5.4 states "For multiple systems, the fire department connection shall be connected between the supply control valves and the system control valves.".

Section 16.12.5.6 states "Where a fire department connection services only a portion of a building, a sign shall be attached indicating the portions of the building served.".

There are numerous options to locating and configuring FDC's, but the sections I referenced, to me, imply that where multiple system risers are supplied from a single underground supply and an FDC is to be located at that location, the connection shall be such that the FDC supplies all systems. If there is another underground supply on the other end of the building serving one or more systems, an FDC can be located there as well, but both FDC's would require a sign indicating the systems and areas they serve. It is not good practice to have multiple FDC's on a single building as it can lead to confusion and/or incorrect connection by the fire department in the event of a fire.

Reply
Darrell
3/12/2020 10:13:10 am

We have a large high school in our area that is split into 4 zones. There is a riser room with an FDC at opposite corners of the school. Each riser room supports 2 of the zones for the school. Each riser room has its own underground water supply.

A fire department needs to preplan the buildings in their response area to understand which FDCs support certain areas of a building.

Reply
Casey Milhorn
3/12/2020 10:41:46 am

In some cases (2) FDCs are actually required. So I couldn't imagine anywhere that it would state that multiple FDCs aren't allowed.

Reply
CJ Bonczyk
3/12/2020 10:53:11 am

Wayne is correct. In some jurisdictions here in Texas the fire marshal may have 3-4 FDC's feeding the same building due to accessibility and footprint of the building for the fire department. Sometimes its overkill but they are more concerned about making it easier for the responding departments to gain quicker hook up to the building systems. Those locations MUST be pre-located with the Architect/Engineer of record and the building owner prior to construction. Note that if multiple FDC's are installed they must have dedicated signs indicating the systems and or buildings they feed to avoid confusion by the fire department. In one instance I have had to install a separate FDC that pumped into a standalone helipad system and provide signage regarding pressure limitations from the pumper to not deplete the foam supply to the helipad too fast. I cannot stress enough that the location(s), size, style and quantity must be planned prior to documents being issued for construction as I have seen some very odd configurations and requests from various jurisdictions.

Reply
Randy
3/12/2020 11:07:12 am

If you have standpipes, NFPA 14 explicitly calls out 'one or more' fire department connections may be required

Reply
chris
3/12/2020 11:17:21 am

The size and number of FDC inlets shall be determined by the fire flow of the sprinkler system and/or standpipe system.Interior hose streams shall be included in the sprinkler demand for determining the number and size of inlets when standpipes and/or hose stations are part of the sprinkler system.

a - Any sprinkler system with a required water flow below 750gpm requires that the FDC be equipped with 2 2-1/2" female swiwel inlets.

b - Any sprinkler system with a required flow greater than 750gpm requires that the FDC be equipped with 4 2-1/2" female swivel inlets.

c - If the on-site water main supplies both the fire sprinkler system and the on-site fire hydrants, an FDC as noted in b above is required.

This is the standard in Ontario, but you can see where are they coming from.
If you have a huge fire system (see above) you can not help it much with only one set of inlets.

Reply
Michael Millman
3/12/2020 10:30:34 pm

Yes, it is possible to have more than one FDC on a building (and sometimes required by code, usually based on size/distance and use of the building).

Reply
Max
3/13/2020 05:54:34 am

I believe in the IBC multiple FDCs are required for high rises with exterior glazing. The reason is a historic fire saw glazing fall off the building and cut the hose lines to the single FDC.

Reply
nairn robertson
3/19/2020 08:19:16 am

My apologies for not being clear on the subject. It was not the size or number of hose connections located within an FDC that I was referring to. Thank you all for your input and support, stay healthy.

Reply
Scott Wyatt
8/17/2021 07:02:01 am

Glad I found this. In Philadelphia, our project has two street levels, with a single existing FDC on the lower level. Fire Marshall requested an additional on the upper level for faster response time.

Reply
Ruby Layak link
11/30/2021 04:25:10 am

Thanks for the feedback that you manage to work with given example.

Reply
AHJ
6/5/2023 11:56:12 am

Hello! I am looking for any guidance on whether or not I can require independently activated horn strobes above FDCs on buildings with multiple systems. I don't want both H/S to activate because I want responding crews to know exactly which system to connect to without wasting time. I saw NFPA 72 said you can have up to 5 WF switches on the same initiating circuit. It just makes sense to have crews know exactly where to connect as soon as they get on scene. Any help is appreciated! Also I know someone will say "You're the AHJ just require it" but I would prefer to find some sort of basis in code in order to ask for something like this. If it's not in code, then maybe that's something I can work on changing in the future. Thanks everyone!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT