Applicable Code for Sprinklers in Dust Collection?

10/11/2023

4 Comments

 
A client of ours operates a printing press facility and has installed a machine to collect and form dust into "bricks" to avoid venting them to atmosphere.

The machine is fed by ducts that tap into an existing dust collection system. 

The client asked for a quote to adjust the overhead sprinkler system because of the new ducts but I think the new ductwork and machine might require suppression of some form, as well as interacting with the existing sprinkler system at the roof. 

(1) Does NFPA 13 (2016 Edition) Section 11.2.3.2.2.2 indicate that the existing roof system cannot have quick response sprinklers?

"Quick-response sprinklers shall not be permitted for use in extra hazard occupancies or other occupancies where there are substantial amounts of flammable liquids or combustible dusts."

It's hard to tell from the floor but I believe at least some of the systems have quick response. 

(2) Is the dust collector ductwork governed by NFPA 13 at all?

Section 22.33 Exhaust Systems for Air Conveying of Vapors, Gases, Mists, and Noncombustible Particulate Solids would not seem to apply since the particulate dust is a paper product and inherently combustible.

(3) Are dust collector machines like paint booths in that manufacturers pre-coordinate requirements and access for sprinklers into the filter media?

Thanks for all the guidance; I haven't seen this application before.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
10/11/2023 08:54:22 am

My thoughts...but without a review of the building and it's classification.

Printing & Publishing is classified as an F-1 occupancy

There are some sprinklers that carry a standard response listing while utilizing a quick response element....verify the type of sprinkler if at all possible.

1) No, the ductwork/equipment is the high hazard issue not the space as most spray operations occur within equipment or enclosures (again, really need the occupancy defined). The collection system likely allows the lesser design basis by removal of the high hazard combustibles. As 13 does not allow quick & standard response sprinklers within the same compartment without some sort of separation, again, verify the QR/SR type.

2) There is a long list but NFPA 13 (Section 22.4 has some guidance and references NFPA 33) isn't the guiding standard on combustible vapors with ducts...some recent notes
--NFPA 91 Standard for Exhaust Systems for Air Conveying of Vapors, Gases, Mists, and Particulate Solids - Section 9.1 just says provide protection...Section 1.1 says it's not within scope for exhaust systems for conveying particulate solids.
--NFPA 34 - Standard for Dipping, Coating, and Printing Processes Using Flammable or Combustible Liquids (applicable but no FP criteria for ductwork)
--NFPA 33 - Standard for Spray Application Using Flammable or Combustible Materials - Section 9.5.1.6

3) Sometimes....There may or may not be ports already for collector machine (heavily dependent on MFG) that occur at the intake collar, within the filter media bed if any, plenum prior to the filters and the plenum after the filters (clean air) but not always. The ductwork, including hood capture systems, the associated collar connections, wye fitting increasers, and bulk duct runs back to the collector rarely have precoordinated ports so that is on the installer (Check out the Victaulic AQD or Flexhead 1000, 1100, 1200, 1300 Series for possibly avoiding the access panel requirement)


A good writeup - https://risklogic.com/fire-protection-at-printing-plants/

Reply
Dan Wilder
10/11/2023 08:56:25 am

Looking back, I know the intent was combustible dust, but vapors generated by the spray application will also play a part.

Reply
Anthony
10/11/2023 12:10:05 pm

1) Can't use QR sprinklers if you're in extra hazard. So, your new routing should take that into account. Even if it's still ordinary hazard you can use std response sprinklers and be in compliance. the only reason QR sprinklers would be a good idea in a setting like this is for area reduction in the hydraulic area which I would guess isn't used.


2) Not really. NFPA 13 is about open floor plan sprinkler coverage not internal duct or machinery sprinklers.

3) Generally if FP is required for the use case the duct or dust collector is designed for then, yes, there will be ports for sprinklers and the like. However there are plenty of cases where a dust collector or otherwise has no FP and that is determined by the final instillation.

FYI:

NFPA 61, NFPA 484, NFPA 652, NFPA 654, NFPA 655, and NFPA 664 are all being rolled into NFPA 660 dealing with dust control

Reply
John Foster
10/9/2025 01:56:44 pm

Need a water sprinkler fire suppression system for a 6 compartment baghouse with the sprinkler system triggered by a sudden rise in temperature from inlet to outlet of the baghouse. System to be NFPA compliant and include water valve, temperature detection and sprinklers.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT