Any Way to Partially Sprinkler New A-3 Church?

11/17/2023

17 Comments

 
We are building a church under the 2018 IBC. It's an A-3 occupancy. We're trying to figure out if we really need a fire suppression system in the whole building and if there are any alternatives given the exorbitant costs to cover the whole building.

Based on my research the only two things that would necessitate a system is the fact that we have a choir loft up a flight of stairs with no fire escape (except the staircase) and the main body of the chapel could possibly fit about 300 people.

We were wondering if we could just cover the fire areas without covering the whole building?

We've gotten differing answers from both the county and fire marshal. I contacted the state department for a final verdict but I could really use some expertise input. Our pastor is concerned that we may be getting upsold into a product that we may not need, especially since they wanted sprinklers in an inaccessible crawl space.

Thanks for all the help, this site has been extremely helpful. Do let me know if there are any viable alternatives and any other way to help on costs.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
Pete H
11/17/2023 07:40:18 am

Without knowing square footage and construction type it's impossible to say for certain.

But if it's got an occupancy of 300 people, and it's a church.... it's likely combustible wood construction, which is why you would have to protect the inaccessible crawlspace if you were to protect the entire building.

Reply
Dave
11/17/2023 11:27:35 am

Wouldn't the crawl space, combustible or not, fall under the NFPA #13 exception, meeting:

1. ...not accessible for storage...
2. ...contains no equipment...
3. ...tight construction...
4. No combustible or flammable liquids or materials...on the floor above

Reply
David Kendrick
11/17/2023 08:06:13 am

It's like paraphrasing the advice from your dentist.

"Only put fire sprinklers in the parts you want to keep."

Reply
Bob
11/17/2023 08:14:29 am

NFPA states entire premesis must be sprinklered.
Usually in cases where sprinklers ar not necessarily called for, your local Fire Marshal can sanction, at his duscretion, a limited area system.
Your underwiter will also need to be on board.
Most Fire Marshals are leery of second-guessing adopted construction standards, but some feel that some level of protection is better than nothing.

Reply
Alex
11/17/2023 08:18:13 am

If you are required to have a sprinkler system (based on area/height/occupancy), then you need to provide a complete NFPA 13 system. If you have combustible construction, that would require you to install sprinklers throughout concealed spaces.

Reply
Darin Golden
11/17/2023 08:21:21 am

903.2.1.3Group A-3.
An automatic sprinkler system shall be provided throughout stories containing Group A-3 occupancies and throughout all stories from the Group A-3 occupancy to and including the levels of exit discharge serving that occupancy where one of the following conditions exists:

1.The fire area exceeds 12,000 square feet (1115 m2).
2.The fire area has an occupant load of 300 or more.
3.The fire area is located on a floor other than a level of exit discharge serving such occupancies.
4. The structure exceeds 12,000 square feet (1155 m2), contains more than one fire area containing exhibition and display rooms, and is separated into two or more buildings by fire walls of less than 4-hour fire-resistance rating without openings.

Reply
Darin Golden
11/17/2023 08:25:55 am

Sorry, the above is from the IFC(scoping code) in your case. Your architect can alter the building to avoid fire sprinklers based upon the above and IBC Ch.5 (general heights, stories and areas). With that said, if a fire sprinkler is required, you might as well sprinkler the whole building as the majority of the cost is already spent on the supply, major components, etc.

Reply
Anthony
11/17/2023 08:31:45 am

This is the building code that will determine fi you need a system. It's possible to have a small church unsprinkled but anything in the ball park of high school auditorium is going to need a sprinkler system.

There is no building code option for "partially sprinkler" with A-3 new construction. You might be able to get a variance?

On the crawl space, yeah if its occupiable then it'll require sprinklers especially if you have combustible construction (wood.)

Reply
Darin
11/17/2023 08:39:47 am

Yes there is.

2 story building with Group A-3 on first floor with group B above and separated by fire barriers between floors. Assuming the Grouo A-3 exceeds the sprinklered threshold's and the building doesn’t exceed the general heights and areas analysis of IBC ch 5 to trigger sprinklers through. In accordance with the IFC code section above. The IFC and IBC ch.9 (scoping for sprinklers) is identical.

Jesse
11/17/2023 08:25:00 am

This is a really bad idea.

Partially sprinklering a building is essentially not sprinklering a building. Sprinkler systems are designed to contain a fire within a design area, preventing lateral spread.

So a fire originating in the non-sprinklered area is going to take the building - including the limited areas you have sprinklers.

Reply
Glenn Berger
11/17/2023 08:46:01 am

A complete code analysis is required here. Cannot give advice on the minimum amount of information provided.

Reply
Eric R
11/17/2023 09:19:10 am

Since everyone has covered the code requirement aspect I'll chime in on the other half of this coin: "exorbitant costs"

If this building is new construction there are tons of options available to a designer to reduce the cost of the system through smart design.

Some off the cuff ideas (that may or may not apply)
1. Can the attic sprinkler protection be made a wet system by moving the building's insulation shell from the floor of the attic to the ceiling. A wet sprinkler attic design has tremendous savings through removal of the dry valve equipment, and through lower design flow demand, which could reduce costs associated with your water supply.

2. Speaking of which, what is the water supply? If the building is rural and needs a tank and pump then there is even more incentive to insure that all available options are used to reduce the system's waterflow requirements which could significantly reduce tank size and fire pump horsepower.

3. Alternatively if you are on a good utility water supply where you have plenty of flow, a designer could go the opposite route and utilize the "below ground floors" exception to remove those sprinklers from the crawlspace with the trade-off of having to increase the design area in the space above, which for light hazard might not have a significant effect on sizing.

Reply
Dave
11/17/2023 11:43:59 am

Agreed - Involving a fire protection professional (from the engineering side or from the contracting side) in the building design can help mitigate costs of sprinklering. I have seen many creative approaches to solving the design and cost issues inherent in these types of buildings, such as eliminating dry-systems, the use of CPVC where allowed, and attic-style sprinklers. These types of projects often have funding issues, sometimes resulting in a phased approach, and committees that may or may not have construction experience. Just research how many fires there are in are nationwide, I believe it is in the best long term interest of everyone to have a fully sprinklered building.
http://www.nysafc.org/Religious%20Property%20Structure%20Fire%20Fact%20Sheet-NFPA.pdf

Reply
Dustin
11/17/2023 12:12:27 pm

Consider appealing to your community. We've done pro-bono engineering, design and installation for local churches and non-profits with smaller non-combustible occupancies. A problem right now is everyone who is worth using is busy. However, you might find a reputable and like-minded firm that would serve you at cost only. It's happened before!

Reply
Todd Wyatt
11/20/2023 09:13:11 am

SUMMARY
Yes, a building can be divided into separate Fire Areas (FA) by Fire Barriers (FB) that also serve as Occupancy Classification (OC) separations … some FAs can be protected by an automatic sprinkler system (ASPS) while others are not UNLESS one of the OCs requires the building to be protected “throughout”.

EXPLANATION
The scoping Code (e.g. IBC-2018) determines WHERE an automatic sprinkler system (ASPS) is required to be provide based on either the Occupancy Classification(s) (OC) (Sections 903.2.1 through 903.2.10) and/or "Specific Building Areas and Hazards" (903.2.11).

Parts of this church would be classified as a “Group A-3 Assembly”.

Section 303 Assembly Group A
303.1 Assembly Group A
Assembly Group A occupancy includes, among others, the use of a building or structure, or a portion thereof, for the gathering of persons for purposes such as civic, social or RELIGIOUS functions; recreation, food or drink consumption or awaiting transportation.
303.4 Assembly Group A-3
Group A-3 occupancy includes assembly uses intended for worship, recreation or amusement and other assembly uses not classified elsewhere in Group A including, but not limited to: Places of religious worship

Other parts of the church that do not have an Occupant Load of 100 occupants or more could be classified as another OC.

303.1.4 Accessory to Places of Religious Worship
Accessory religious educational rooms and religious auditoriums with occupant loads of less than 100 per room or space are not considered separate occupancies.

Once the OCs are determined, then Chapter 9 Fire Protection and Life Safety Systems determines WHERE an ASPS is required.

IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2.1.3 Group A-3
An automatic sprinkler system shall be provided throughout stories containing Group A-3 occupancies and throughout all stories from the Group A-3 occupancy to and including the levels of exit discharge serving that occupancy where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
2. The fire area has an occupant load of 300 or more.
3. The fire area is located on a floor other than a level of exit discharge serving such occupancies.

IF the A-3 OC portions meet ONE of the above (3) conditions, an ASPS is required.

Other OCs, like Group B Business, do not have requirements for ASPS protection.

Reply
Ron link
11/21/2023 11:45:40 am

We can protect the crawl spaces with condensed aerosol without running any piping etc. which makes the pricing much more reasonable.

Reply
James Art FPE
11/22/2023 10:45:39 am

Obviously this religious person doesn't believe in fire protection for his building or congregation,.
I met one pastor who said: God will protect him,
so he didn't need 2 exits from the large basement assembly hall!

This is where Laws and Code Enforcement save lives and property.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT