MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Any Contact Allowed with Sprinkler Pipe?

10/23/2018

19 Comments

 
Have a project which requires very tight coordination between sprinkler and ductwork. The ductwork will be lined with insulation which could come in contact with the black steel fire sprinkler pipe. Is there a minimum clearance required that wouldn't permit this contact by code?

​Posted anonymously by a member for discussion. Discuss this here.
19 Comments
Bruce Seiler
10/24/2018 09:14:50 am

Recently, we have had inspectors site other items touching sprinkler pipe as a violation. This wasn't a case of something laying on top of the pipe adding, albeit small, weight to the sprinkler system. They were instances of other systems touching the sprinkler pipe, whether it be duct, insulation, wire. I'd be interested in thoughts and code references on the matter as well. Good question.

Reply
Scott Walter McBride
10/24/2018 09:27:38 am

there is a clearance section, which is 9.3.4.

Reply
sean
10/24/2018 10:58:22 am

The section does not appear to address other building systems but structural and framing items.

Burnet Glover
8/19/2020 10:00:46 am

I have a similar condition where structural members and electrical conduit greater than 2” dia. are in contact with the sprinkler main supply piping, greater than 6 inch in diameter. I was only able to find clearance requirements under Section 9.3 of the 2016 edition of NFPA 13 under Protection of piping against seismic conditions. Is there a requirement in NFPA 13 for a minimum clearance around sprinkler piping.

Anthony Alarcon
7/30/2020 09:47:04 pm

Is there a code requirement that says Sprinkler Piping must maintain a certain distance from fireproofing sprayed onto structural steel?

Reply
zubair ahmed
8/25/2021 01:03:41 pm

Hi Anthony
i am interested in knowing the answer to your question

please let me know


regards

Rebecca
5/2/2023 09:52:06 am

Chapter 17.1.3.1 of NFPA 13- "Sprinkler piping or hangers shall not be used to support non-system components."

Reply
Michael Watkins
3/1/2024 01:33:01 pm

Required clearance from OH Sprinkler pipe is 3 inches.

ASCE 7 - 13.2.3.1 Clearances between Equipment, Distribution Systems, Supports, and Sprinkler System Drops and Sprigs. The installed clearance between any sprinkler drop or sprig and the following items shall be at least 3 in. (75 mm) in all directions:

Reply
Dave L.
10/24/2018 11:30:03 am

Interesting point, and agree with Sean - Although some common sense and judgement should prevail, I am not away of any code reference pertaining to clearance to other mechanical systems; just structure. It is assumed if this is in a seismic zone, that the mechanical systems are properly restrained, and that the sprinkler system piping is braced and branch lines are properly restrained, vertically and laterally. And of course things cannot be resting on the pipe; NFPA 25 comes to mind on that. And on CPVC pipe there are compatibility issues with anything touching the pipe.

Reply
Michael Watkins
3/1/2024 01:37:21 pm

ASCE 7-16 Section 13.2.3.1 requires 3 inches minimum in all directions.

Reply
EdwH
10/24/2018 01:36:00 pm

NFPA 13-2016

9.3.4.9 The installed horizontal and upward vertical clearance
between horizontal sprinkler piping and structural members
not penetrated or used, collectively or independently, to
support the piping shall be at least 2 in. (50 mm).

This addresses structural members or anything supporting the pipe.

Reply
HARRIS link
3/10/2020 09:50:41 am

As far as my research into this original question, there is no reason pipe cant have duct touching the bottom side (nothing in fire code prevents this unless it is CPVC). It seems fire marshals who arent 100% sure will fall on the side of safety and uphold the CPVC pipe requirement (not touching anything) for steel pipe. I do know it is an issue if inspectors cannot visually see the pipe from below for inspections, but otherwise most dont mind.

Reply
Jonathan Key
5/19/2020 08:48:47 am

Expanding on this, I have a question. Referencing 9.3.4.9 Does this mean that if i run a sprinkler line underneath an I beam or Bar joist i cannot be within 2" of any structural member with the top of the sprinkler pipe? Say 1" below the beam?

Reply
Shawn P Jones
8/27/2021 09:25:09 am

Unless you are in an area prone to earthquakes that code section would not apply.

Augustine Moreno
5/18/2021 11:52:56 pm

I have a sprinkler system in obstruction with my hvac unit
I need to be sure of how much clearance away from the water pipe i need for clearance

Reply
Michael Watkins
3/1/2024 01:39:31 pm

ASCE 7-16 Section 13.2.3.1 requires 3 inches clearance in all directions.

Reply
M.Alaniz
12/15/2023 10:38:24 am

I found this: NFPA25 Inspections- 5.2.2.2 : Sprinkler piping shall not be subjected to external loads by materials either resting on the pipe or hung from the pipe.

If there is duct/ duct wrap resting on sprinkler pipe, has anyone used a corrosion control tape to keep the friction from reducing on the pipe? something similar to Polyken 826? Would this be applied to the duct work above the pipe?
nothing should be stuck directly on the pipe...
Thoughts?

Reply
Michael Watkins
3/1/2024 01:42:58 pm

Required clearance from OH Sprinkler pipe is 3 inches.

ASCE 7-16 Section 13.2.3.1 Clearances between Equipment, Distribution Systems, Supports, and Sprinkler System Drops and Sprigs. The installed clearance between any sprinkler drop or sprig and the following items shall be at least 3 in. (75 mm) in all directions:

Reply
Richard G. Rael
9/23/2024 02:15:41 pm

With the understanding that wires, cables, piping, ducting etc.etc can NOT touch the fire sprinkler pipe my question is, can those items touch any of the struts, fasteners, all-thread OR is it anything that has to do with the sprinkler system can not be touched.

Thanks,


Rick Rael
505-252-1562

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT