MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Always-Running Domestic Pumps OK with Fire?

11/30/2022

3 Comments

 
I am doing some work on a combined fire-fighting/domestic pump house for a small community.

A couple things look odd to me.
  1. They have a 12-inch flanged basket strainer after the pump discharge just before the mains. I was under the impression that any devices or fittings between pump discharge and need to be listed for fire protection use.
  2. Instead of a jockey pump, they have three potable water pumps which run all the time pushing potable water to the mains. The primary fire pump automatically operates when the pressure drops to 4.5 bar and the backup pump at 2.3 bar.

There seem to be two deviations from NFPA standards here:

First, the jockey pump should be small , so that in case of fire it is the fire pump taking the load, and second, the starting sequence requires the jockey pump to start above the fire pump churn, the first fire pump a little lower and so on.

Is there any exception for such combined domestic/fire protection systems in the NFPA line of standards?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
11/30/2022 08:07:34 am

I had a similar setup with a house on a hill with the feed main serving both a hydrant (long road up the hill and the FD did not want to run supply hoses up/down the hill during winter and possible snow/ice), fire protection residential system, and domestic.

The fire pump house at the base of the hill included 2 domestic pumps (primary and backup) that acted like the jockey pump. We did need to adjust the FP/JP on/off pressures to be lower than the working domestic pump to avoid the JP running full time and false starts from the FP. The domestic pumps were strong enough to run the FP system on their own.

Our solution (with FD/FM approvals) was to still provide the jockey pump in case the domestic pumps were not operational (still knowing that the fire pump would likely kick on about the same time the JP would, and later confirmed during one of the commissioning scenarios...only about 5PSI difference with a delay). The domestic pumps did most of the work and there was discussion about an interlock to shut down the domestic pumps when the fire pump kicked on, but the FD/FM wanted to keep all available resources (water supply was not an issue due to the lower overall demand for the single hydrant, domestic demand, and FP system)

As to the strainer AFTER the pump....seems a bit backwards as this does nothing to protect the actual device providing the pressure and flow from damage. There are listed strainers available however this wouldn't be a big sticking point to me as long as a ITM schedule was followed.

Reply
Panos
12/1/2022 04:08:57 pm

Thank you Dan and Glenn! Valuable information!

After reading your replies, I spent some time on NFPA 20, and found some interesting things:

"Fire pumps that are installed in parallel with domestic pumps on a combined fire/domestic water distribution system require special consideration.
The domestic pumps should operate at or close to the fire pump pressures.

For systems that use fire system piping for both domestic and fire protection purposes, the domestic pumps typically maintain the system pressure. (4.27)
The operating pressure should be maintained close to the fire pump churn discharge pressure to minimize pressure surges.

The pressure maintenance pump shall be sized to replenish the fire protection system pressure due to allowable leakage and normal drops in pressure. (4.27.2.1)

Pressure maintenance pumps shall have rated capacities not less than any normal leakage rate. (4.27.3)

Pressure maintenance (jockey or make-up) pumps are generally low-flow, high-pressure pumps. For sprinkler systems, jockey pumps are usually sized to flow a quantity of water less than or equal to that required by a single sprinkler.

The pressure differential between the pressure maintenance pump and the fire pump should be a minimum of 10 psi (0.68 bar) to avoid false starting of the fire pump due to pressure fluctuations in the system piping.

A rule of thumb for sizing jockey pumps supplying underground piping is to use 1 percent of the fire pump rated capacity and add 10 psi (0.68 bar) to the pressure rating of the fire pump.
The fire pump system, when started by pressure drop, should be arranged as follows: (A1.4.2.6)

(a) The jockey pump stop point should equal the pump churn pressure plus the minimum static supply pressure.
(b) The jockey pump start point should be at least 10 psi (0.68 bar) less than the jockey pump stop point.
(c) The fire pump start point should be 5 psi (0.34 bar) less than the jockey pump start point. Use 10 psi (0.68 bar) increments for each additional pump."

So, the existing setup definitely defies NFPA 20 in terms of pump sequence pressure settings.
Regarding the strainer, NFPA 20 does not specifically address strainers after pump discharge, but there are quite a few indirect recommendations:

"The discharge components shall consist of pipe, valves, and fittings extending from the pump discharge flange to the system side of the discharge valve. (4.17.1)"
(nothing else I may add)

"Listed sprinkler system strainers are installed within a sprinkler system to help prevent the flow of foreign debris, such as grit, stones, leaves, etc., beyond it. It is typically required in sprinkler systems equipped with small K-factor sprinklers and the strainer must be cleaned after every operation, including flow tests. "

So the intent of the Standard is not strainers with flowing water continuously.

Reply
Glenn Berger
11/30/2022 08:24:18 am

In my read of the comment, you have a pump that provides additional pressure when a fire flow event occurs. I do not see conflicts with NFPA standards.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT