Adding Loss for Flex in Pipe Schedule System?

7/7/2022

10 Comments

 
NFPA 13 makes provisions for the addition of a backflow preventer to a pipe schedule system (i.e., device pressure loss must be taken into account for minimum residual pressure available, per Section 19.3.2.6.2 of the 2019 Edition). 

When adding flexible sprinkler drops to a pipe schedule system (1 for 1), is a recalculation necessary, or wouldn't the basic addition of that extra pressure loss to the residual pressure for the pipe schedule system be all that's needed?

The AHJ is requiring a recalculation rather than simply adding the pressure loss to the residual pressure as we would do for adding a backflow preventer. 

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Danefre
7/7/2022 07:30:26 am

We're in MA. Typically, recalculation is required. We use a specific flexible braided hose manufacturer and calculate it at 55 equivalent feet to be conservative. Max length & number of bends.

Not as simple as adding a flat PSI loss to your residual pressure and most AHJs would agree.

Reply
Glenn Berger
7/7/2022 08:10:16 am

There is a limit to the amount of modifications made to an old pipe schedule system as still be considered viable. You might have found this AHJ's limits.

Reply
I <3 Sprinklers
7/7/2022 08:16:10 am

We would definitely require a recalculation for adding flex drops to a pipe scheduled system in our area outside of very specific circumstances (matching another floor of an existing building that was previously calculated or something like that).

If not for this situation, where would you draw the line about where full hydraulic calculations should be conducted compared to when preliminary theoretical calculations suffice?

The Victaulic AH2 shortest hose (31") with the fewest bends (3) has a 15'-0 equivalent length. Do you think the plans reviewer and inspector would raise any concerns if you had 15'-0 arm overs for every sprinkler on an add/relocate project?

Reply
Dan Wilder
7/7/2022 08:35:26 am

So (spit-balling here, I've worked on about 5 pipe schedule systems in my career), tricky subject as this isn't specifically mentioned in the "Revamping" section and how would you justify pressure loss differences between a hard pipe and a flex hose? If using the SxL x Density to get PSI loss though 1" hard pipe/fittings then applying that to the EQ length of a flex hose, you're effectively applying hydraulic calculation procedures to justify not using hydraulic procedures....

However, the one condition I would stress to make your argument (or not allow it), is to verify that all components of the flex hose are a minimum 1" ID to match a Sch 40 pipe (1.049" ID)...some hoses are a lesser ID.

There is nothing in the current NFPA about how the 1 sprinkler fed from 1" pipe is limited by the number of feet, elbows, or tee's in the line so you may be able to argue that point (again, providing that the hose is at least 1" ID throughout).

Reply
Casey Milhorn
7/7/2022 09:00:49 am

I agree with the AHJ on the need for a calc in this situation (being an old pipe schedule system means it's possibly never had a calculation performed on the system). Water supplies can change a lot over that many years.
On an existing calculated light hazard system, I'm not in favor of asking for calcs every time a change is made, even when adding flex drops. When you factor in 2 to 4 90s, tees, X amount of pipe, etc. you can actually exceed the pressure loss vs some flex drops. Also, sometimes a little more friction loss is a good thing and can help balance systems, especially when 5.6k heads aren't maximized in their spacing. I also have an issue with the fact that we calculate down to a tenth or hundredth of a PSI yet flex heads are all over the board in real life friction loss, dependent upon how many bends there are. Long story short, I think there are bigger fish to fry than worrying about a little extra friction loss in flex heads. BUT, if there are any concerns with water supply change, occupancy change, EC heads being used, etc.... that would warrant a calc, I'm always in favor of erring on the side of caution in those cases. Great question.

Reply
schulman
7/7/2022 10:18:24 am

I would require full recalc.

Reply
Anthony
7/7/2022 03:09:17 pm

Pipe schedule systems came before flex drops. There's no prevision to using them or not using them per code. That being said I would require a calc as it is not "like for like" replacement or repair. Especially if corrugated hoses was used as those have a higher tendency to crimp and restrict flow as compared to a braded hose.

Reply
Jesse
7/8/2022 07:37:42 am

Every AHJ we deal with would require a full calc. Even if they didn't, I would require my designers to hydraulically prove adequacy before I sealed it.

Reply
Alex
7/9/2022 09:48:17 pm

Hi,

Responding a few days late here - took the week away with family for the 4th.

I agree with all the comments above requiring calculations. If you are replacing a sprinkler with the same sprinkler, different story. If you are replacing a pendant with a flex head, I would require calculations.

Alex

Reply
sean
7/11/2022 06:28:53 am

you cant mix and match calculation methods either pipe schedule or hydraulic.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Dec '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT