MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Calculate Refill from Existing Well?

6/5/2023

6 Comments

 
We have a Fire Marshal that is asking us to "show how the fill line can refill the [water supply] tank in a maximum of 8-hours, per NFPA 22 Section 14.4.2". 

The tank we're proposing will be supplied by an existing well, but we do not have information on well capacity.

What parameters should we be looking for on well capacity? Do we have to test for both flow and time? 

Is the computation on refill as simple as the flow rate (gpm) x time (8-hours) to get the contribution from the well?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Use Refill to Downsize a Water Storage Tank?

5/22/2023

15 Comments

 
This may sound like a strange question, but here it goes.

Is there a way to downsize a fire water storage tank based on the refill rate supplied by the city?

I know that in Houston there was a company that supplied calculations showing that the refill rate could supply the tank at a refill rate based on the flow test.

Could anyone substantiate this principle?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments

Required Duration for Secondary Water Supply?

1/26/2023

8 Comments

 
What is the required duration for a Secondary Water Supply within Seismic Zone?

IBC Section 403.3.3:
​
"The secondary water supply shall have a duration of not less than 30 minutes as determined by the occupancy hazard classification in accordance with NFPA 13."

Does this mean minimum 30 minutes, with the gpm/demand determined by NFPA 13?

Or the minimum duration is also determined by NFPA 13, such that the secondary water supply could require an even longer duration, like 60 minutes?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Why Discharge Fire Pump to Water Storage Tank?

12/5/2022

13 Comments

 
I'm looking at a few projects that have fire pumps and above-ground cylindrical storage tanks for fire protection.

Some projects I have seen have recirculation after the fire pump discharge underground and back into the storage tank. Frustrated I can't find much on this in NFPA 22 or elsewhere.

Is this part of a means for freeze-protection, or to keep the water from getting stagnant, or for pump testing (in which case I guess it would have to branch off from the flow meter)?

Or is it likely engineer preference? Is it a military requirement?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Prevent Fire Pump Start with Low-Water Levels?

9/2/2022

12 Comments

 
Is there any NFPA provision for forbidding a fire pump to start in the event a water storage tank has a water level that is too low?

I'm wondering what might happen if the water storage gets down to ~25% of the design level, or lower, and the potential need to shutdown the pump before it runs dry. 

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

How to Include Suction Tank in Hydraulic Calc?

7/1/2022

5 Comments

 
We are bidding a job that may possibly need a 1,250 gpm rated fire pump due to not enough flow from the city. Our test was 43 psi static, 35 psi residual at 872 gpm. We will need to include a ground suction tank.

How do I correctly include or simulate a ground suction tank in my hydraulic calculations?

We use the Sigma Hydraulic Calculation program.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Typical Suppression Water Storage Tank Type?

3/31/2022

9 Comments

 
​We're looking at a fire protection system, Ordinary Hazard Group 2, that requires primary fire protection water from a storage tank.

We are looking at three options, (1) above ground insulated with a heater, (2) underground concrete and (3) underground fiberglass.

I am curious what the community here sees around the industry as being the most common choice here?

The job site already has substantial excavation going on and the job is located in the north east so freezing is a concern. There will be no private hydrant so we don't see the need to carry hose allowance in our tanks sizing.

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Pool for High-Rise Secondary Water Supply?

12/28/2021

6 Comments

 
Can a commercial pool be used as the required secondary water supply to a high-rise sprinkler system?

The 2019 IBC/CBC Section 403.3.3 requires an automatic secondary water supply in certain seismic design categories. This is typically met by installing a dedicated tank that meets the minimum demand for 30 minutes.

I have a developer asking if they can run a feed line to their 100k +/- gallon commercial pool so it can serve this purpose.

Outside of the engineering challenges and value engineering their team must address, I'm wondering if this arrangement is even allowed. I cannot find anything in IBC/CBC, NFPA 24, NFPA 13, etc. that wouldn't allow this. Any help is appreciated.

​
6 Comments

Does Tank Meet Secondary Supply in IBC?

11/29/2021

14 Comments

 
Section 903.3.5.2 (IBC 2012)/Section 403.3.3 (IBC 2015) requires and automatic secondary water supply. I am an FPE and I work in a jurisdiction (Hawaii) that has never required this secondary water supply due to local code amendments to IBC. Recent code revisions now require this secondary supply, and I now have my first project subject to this requirement. I'm planning to meet this requirement as as follows;
  • Secondary Water Supply: Provide an underground storage tank capable of supplying the sprinkler system + Hose Stream demand for 30-minutues per IBC requirement (min. 12,000 gallons). A vertical turbine fire pump will sit on top of the tank and pull water from below. Pump will be sized to supply full sprinkler system and standpipe system pressure demand (750 gpm @ 250 psi).
  • Primary Water Supply: The city water main will flow directly into the water storage tank at a rate equal to the standpipe system demand. The tank will serve as a "break tank" as long as the city water supply is viable. Although the city water supply will fill the tank at an equal rate to the system demand, the minimum break tank size will be 750 gpm x 1.5 x 15 min = 16,875 gallons.

Am I on the right track here? Is this primary/secondary supply arrangement viable? Does anyone foresee any code or other issues that may be a problem with this arrangement?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

How to Find A Leak in a Water Storage Tank?

11/11/2021

9 Comments

 
We have a water storage tank that is leaking but cannot find the leak.

They have scoped the pipes, used dye to try to track with no luck.

Does anyone know if ground penetrating radar or some other thing that we can try to locate this leak?

Any help is appreciated!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

How to Size Tank for Surge Suppression?

9/10/2021

6 Comments

 
We design fire protection systems for large industrial plants with a large area network running in the kilometers.

In such case there could be chances of surge due do sudden closure of a deluge valve, check valve, or fire pump. We do not have time/expertise to carry on surge analysis on software.

I have heard about using tanks for surge.

How would we go about sizing an anti-surge tank?

Is there any basic guidelines based on fire water flow rate/pump discharge pressure to get first cut sizing of a surge  protection tank?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Height of Fire Pump Pressure Relief into Tank?

9/2/2021

5 Comments

 
We have a water storage tank and a diesel fire pump on our project.

Is there any requirement for the pressure relief valve discharge pipe, when connected to a supply tank, to be extended below the lowest possible water level?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Tank Size, Options for Sprinkler System Supply?

8/3/2021

12 Comments

 
We have a fire sprinkler system with a 550 gpm total sprinkler demand (including hose allowances). The supply duration is 60 minutes. There is no city water supply and we are only utilizing a storage tank.

Is the tank required to have a minimum capacity of 33,000 gallons?

Or, could we rely on fire department response, potentially reduce the tank size, and have a manual fire department connection for tank refill?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Larger Water Storage Tank In Lieu of 8-hr Refill?

3/19/2021

4 Comments

 
We have a project with a limited water supply that makes it impossible to automatically replace the required fire water in 8-hours. 

Could a larger (1.5 x the required fire flow) water storage tank be an option?

​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Add Second Water Storage Tank In Lieu of Larger?

3/3/2021

4 Comments

 
Our fire water demand capacity is 60,000 gallons, but our current water tank storage capacity is 30,000 gallons. We don't have any space near our current fire water storage tank. 

Is it possible to make another (second) tank with a capacity of 30,000 gallons and connect it to the old tank through pipe?

​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Swimming Pool as Fire Protection Water Supply?

1/28/2021

24 Comments

 
​I am currently working on an existing high rise building that requires a fully automatic sprinkler system to be added and the AHJ is requiring a water tank to be added on the property to serve as a secondary supply.

There is no room for a secondary supply.

Can a pool be used to substitute a water storage tank that will supply the building through fire pumps?

What codes could back up this option?

​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
24 Comments

How to Prevent Algae Growth in FP Water Tank?

12/15/2020

5 Comments

 
How can we prevent the formation of algae or microorganisms in water storage tanks for fire protection due to the water being stagnant?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
5 Comments

When is a Storage Tank Req'd with a Fire Pump?

12/7/2020

10 Comments

 
I'm putting together design-build requirements for a new single-story construction building. The flow test pressure is borderline in my opinion so I'll be calling for a fire pump.

When is a water storage tank required with a pump?

I don't think the system needs one, but I just want to be sure.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

Refill Considered When Sizing Fire Water Tank?

11/17/2020

10 Comments

 
Is it permissible to consider the refill supply for a water storage tank when sizing the tank?

The supply would come in above 20 psi. Thanks in advance.

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

Why Do Fire Storage Tanks Require 8-Hour Refill?

9/21/2020

7 Comments

 
NFPA 22, 2018 Edition regarding filling requirement and duration - 

Section 4.2.1.4. states "The water supply shall be capable of filling the minimum required fire protection volume within the tank in a maximum of 8 hours" and at the same time Section 14.4.3 states "The tank shall be kept filled, and the water level shall never be more than 4 in. (102 mm) below the designated fire service level."

If I understand correctly, as soon as the water goes below 4-inches from the normal filled level in the tank (HHL), the makeup water supply should be starting to replenish and the pipe sizes should be provided in such a way that the tank can be filled within 8-hours.

In a fire, as the water is going down, the tank will always start full.

What is the case where the tank would be emptied out (except maintenance) and need to be refilled within 8-hours?

What if we store water in two tanks to allow maintenance - would we not need to meet this 8-hour requirement?

I'm unsure of how these two requirements work together. Appreciate any feedback.

​​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Fire Pump Type with Underground Storage Tank?

7/20/2020

12 Comments

 
I’m working in the construction of 4-star hotel. The water storage tank is underground made from concrete and the pump room is located above the water tank. The designer specified the fire pumps to be vertical split-case type! In order to follow code, I proposed to install vertical turbine pumps instead of the specified vertical-split case.

The supervisor Engineer is insisting to follow the specification of the fire pump and pushing me to create an underground pump room in order to install the specified pump set.

Any recommendations to avoid this directive?

I have a bad flooding experiences with this this type of subgrade pump rooms.

​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
Forward>>
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Dec '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT