NFPA 22, 2018 Edition regarding filling requirement and duration -
Section 4.2.1.4. states "The water supply shall be capable of filling the minimum required fire protection volume within the tank in a maximum of 8 hours" and at the same time Section 14.4.3 states "The tank shall be kept filled, and the water level shall never be more than 4 in. (102 mm) below the designated fire service level." If I understand correctly, as soon as the water goes below 4-inches from the normal filled level in the tank (HHL), the makeup water supply should be starting to replenish and the pipe sizes should be provided in such a way that the tank can be filled within 8-hours. In a fire, as the water is going down, the tank will always start full. What is the case where the tank would be emptied out (except maintenance) and need to be refilled within 8-hours? What if we store water in two tanks to allow maintenance - would we not need to meet this 8-hour requirement? I'm unsure of how these two requirements work together. Appreciate any feedback. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Peter
9/21/2020 10:11:34 am
The idea behind a water storage tank in most cases is that the water supply is not capable of meeting the system demand for the required duration. So as a default, over time, the tank will empty because the system demand will out last the tank supply. In some instances you can calculate a water supply to refill the tank to shrink the size of the tank so it meets system demand. However, sometimes that is not possible such as in a rural application where there is no water supply that is really capable. I have seen, in this instance, that the refill of the tank is nothing more than an irrigation pump pulling water some a small lake or a well. The 8 hour requirement is to make sure that that water supply (irrigation pump from a well, lake, or other) is capable of refilling the tank within 8 hours so that the fire protection system can be restored.
Reply
Martin Etcheverry
7/17/2024 11:01:58 pm
Break Tanks, with them you can dramatically reduce the volume of water Stored to comply with the system demand, as you can have a smaller unit (Tank) that is REPLENISHED with a flow that is capable to garanty a certain duration.
Reply
Franck
9/21/2020 11:41:16 am
And as always with requirements for duration, the limit is set arbitrarily.
Reply
Bruce Verhei
9/21/2020 02:12:15 pm
The tank has infrequent requirement to be emptied for ITM.
Reply
GC
9/23/2020 01:33:17 pm
If the water tank is not "full" then you have an impaired water supply. NFPA 25-15.5.2(4) will allow a preplanned impairment of up to 10 hours before the big-ticket mitigations like evacuations or fire watches come into play. An 8-hour fill time keeps it under the 10-hour impairment.
Reply
Morteza
4/14/2024 10:47:24 am
Thanks for your informative discussion.
Reply
8/19/2024 02:26:33 am
In Spain, according the standard UNE23500 time to refill the total volume ofthe tank is 36 hours, regardless that if the filling is auntomatic or by an external source. Here in Europe the break tanks are according the codes (there are llimits in the minimum capacity depending the hazard category).
Reply