MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Zone Control Allowed Downstream of Another?

8/1/2023

20 Comments

 
Can a zone control valve assembly be installed downstream of another zone control valve assembly?

If there is a fire in Zone A (the primary zone), Zone A's flow switch would activate.

If there is a fire in Zone B (the secondary zone), Zone A and B's flow switches would activate.

Not sure whether this is permitted under NFPA 13 or 72. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Pete H
8/1/2023 06:50:57 am

My personal take based on nothing:

as long as zone a and zone b's total square footage is less than the maximum area for a single system as per NFPA 13 requirements (as zone b still would count as part of zone a for this), I take no issue with additional control within a system. I could see it as specifically good for buildings with "wings" or long dead end hallways.

Reply
CARLOS
8/2/2023 04:48:35 pm

But when you have to work on zone A, wouldn't that also shut off zone B? Shutting both systems down? I'm sorry but I don't agree with that set up. I believe 13 might say something against it and 25 too.

Reply
Anthony
8/1/2023 07:20:13 am

Adding to what Pete said: This happens all the time with smaller dry systems and pre-action systems off a wet system. I like to have a small butterball valve flow switch and test and drain for elevators. Kind of a mini system to keep everything isolated.

Reply
Chad
8/1/2023 07:21:34 am

As long as the controls and flows are supervised (and in the flow calcs if necessary) I cannot imagine why it would not be permitted.

Reply
Dan Wilder
8/1/2023 07:45:12 am

We do this often for individual levels of mezzanines in larger building footprints (13-22' 4.4.2, but this changes based on applicable year) and only when the primary system is wet.

It is also allowed within NFPA 13-22' Section 8.1.3.

In both cases, area limitations (as the math allows) are not exceeded.

Reply
Casey Milhorn
8/1/2023 08:18:01 am

I agree with everyone else and I don't know of anything not allowing it, other than than sqft limitation of NFPA 13 and your calculations. I've done it, and it has it's time and place, but as a rule I'm a fan of as few valves as possible to avoid the possibility of a closed valve (even when tampered, they get ignored sometimes). BUT, when you have trapped sections, a section prone to maintenance issues, etc, it has it's place. You just have to explain very clearly to the fire alarm guy that a signal in A means A, and a signal in A and B means just B... and program accordingly.

Reply
Glenn Berger
8/1/2023 08:24:44 am

The installation of flow series in series happens often in facilities. Easy examples are flow switches associated with elevator / elevator machine rooms and more recently with battery rooms.

Reply
Alex
8/1/2023 09:56:52 am

To echo others, yes, I believe its compliant and have done so myself before in the past.

Reply
Jesse
8/1/2023 10:21:27 am

Yep, we do this quite often. As long as both control valves are supervised and accounted for in the calculations (if relevant to the calcs), its shouldn't be a problem.

Reply
Franck
8/1/2023 02:37:03 pm

Yes, it is possible
And even recommended in the examples above or if you have an interlock on a machine to stop it when the sprinkler system operates (could be a rolling mill, broke pit for a paper machine, paint spray booth…) and you don’t want to stop the machine if the sprinkler on the main system is activated quite far away…
In addition, it could be wise to isolate the sprinkler system that has operated on this limited area (broke pit of a paper machine, for example) and keep the remaining of the building under active sprinkler protection.
Don’t forget to properly supervise these additional subdivision valves.

(note that this may normally not be allowed in some other countries standard, such as some European countries…).

Reply
James Evans
8/2/2023 08:36:30 am

I agree with what has been said for the most part. I do not agree with the area limitation stated in the 1st response. I believe that the area limitation is per system. If you look at this situation you have two separate systems. In this case you would have the first system acting as a bulk run for the second system. It is no different than the manifold supplying multiple risers.

The only difference between the manifold and this scenario is that both flow switches would activate.

If you have a light hazard wet system that covers 52,000 sq. ft. and then you have a dry system that drops off the end of that system that is ordinary hazard covering 40,000 sq. ft. you do not add those 2 areas together and say the system is covering 92,000 sq. ft.. Each system is considered as seperate.

I believe the area limitation is per riser or flow device.

Reply
Wes
8/2/2023 08:42:59 am

Oh that's a really good question. I had thought the area limitation was based upon the risk associated with having so much square footage tied to one point of failure (one valve).

NFPA 13 - 4.4.1 (2022): The maximum floor area on any one floor to be protected by sprinklers supplied by any one sprinkler system riser or combined system riser shall be as follows... 52,000 sqft for Light Hazard, etc.

A System Riser (defined term in 3.3.225) "contains a control valve, pressure gauge, drain, and waterflow alarm device".

So one riser cannot serve both a wet system (52,000 sqft) and a dry system (40,000 sqft) at the same time.

Now if the wet system is 32,000 sqft and the dry system is 20,000 sqft, I think that's fine, because it'd still be under the 52,000 sqft limitation.

Reply
James Evans
8/2/2023 09:36:21 am

I guess we need to know what they are defining as a "combined system riser" as you can see the term is singular not plural. I am not sure if one riser downstream of another riser is considered "combined" or is it considered 2 individual risers?

Wes
8/2/2023 09:47:32 am

That's a good question James. I've been so resolute on this for so long - but I'm not entirely sure.

It seems like that one upstream riser is 'serving' all 92,000 sqft because that much area is downstream of it - but is it considered two individual risers, or a combined riser?

Any loss prevention folks weigh in here? I had thought the system area limitations were mostly based upon risk tolerance for single points of failure/reliability.

Casey Milhorn
8/2/2023 10:28:16 am

So the area limitation conversation is always fun and lots of opinions about it. From what I understand, the sqft limitation was based on the old pipe scheduling method. The NFPA 13 Committee knew that some type of limitation was good for obvious reasons, and also practical as not to have ridiculously large pipe once you got back closer to the riser. So nothing very scientific about the limitations. I know there has been discussion about revisiting the system area limitations but I guess never a consensus on changing it, or what to change it to. I personally think keep it simple and limit it to 100,000 sqft per system no matter the hazard/occupancy type. That would equate to a lot of savings in bulk feed main, risers, and labor. NFPA 13 is still based on one fire event at a time, not multiple. I can't really think of any practical reason to limit size, other than the rare occasion of a system being down for maintenance. Of course you still have to hydraulically prove the systems and meet water delivery times on dry systems. It's definitely an interesting conversation.

Mark Harris
8/2/2023 03:10:43 pm

I agree with the comments about a single riser or control valve and the 52,000 (or less) max floor area. As NFPA 13 is written could see an issue with the added a 40,000 SF dry system since both would be out with the wet valve riser shut. But Casey brings up interesting point about the connection with old pipe schedules. Thanks for sharing that insight and may be time to up those floor area amounts.

Paint booth would be another scenario similar to special equipment comment from Franck.

But then with backflow preventers or underground valves with multiple risers we already have scenario where one valve shuts off multiple systems.

Reply
James Evans
8/2/2023 03:39:34 pm

I still believe that each riser (or riser manifold) can start an additional 52,000sq.ft. or 40,000 sq.ft. depending on the hazard. we always have systems where a single valve turns off multiple systems or a single riser controls multiple systems since we tend to drop off dry systems and per-action systems from wet systems. No where in NFPA 13 does it state that if you do this, then you are limited to a certain square footage. We have done many maxed out wet systems with large wet systems that drop off the end of the front grid main and then goes out to a large dry system covering an exterior dock. In this scenario nothing says that the two systems must be added together and not exceed a certain area. As long as the calculations show that it works it should be allowed.

As far as a single valve controlling a large area, just think of the main control valve on a standpipe system, or a backflow for an entire building, or the valve after a fire pump.

We are doing nothing different by chaining systems together. The only difference is that the alarm may show multiple flow switches activating.

Please if adding the systems areas is required by NFPA 13 please show me where it is stated.

Reply
James Art, FPE, Pleasanton, Ca
8/2/2023 04:32:37 pm

Wes 8/2/2023 08:42:59 am agrees with me, so he's obviously correct! (-:

The code gives a Maximum area subject to a single impairment,
so you CANNOT then add a 2nd area to that, and have more area, like 92K affected.
A 2nd INDEPENDENT source to feed another riser is called for.

Too many valves are generally a bad thing, more to go wrong.

But one common scene is the strip mall, or even a regular mall where it would allow tenant improvements for each tenant without affecting others,
if there was, say, a valve from a main to serve individual areas.

Often a good C16 will ask and add such a valve, so he can work on and test without affecting other tenants.
Needs valve supervision, add to plans and/or a sign at riser.
But often the original installer used a grid, so there is no such main.

Sometimes similar layout in office buildings or hospitals, esp,
when a main down a hall supplies different areas, tenants or departments.

A huge fire at the Roseville Galleria mall, in Northern Ca with $55 Million loss in 2010, was party due to having turned off a large area while remodeling a small area. And also turning off other systems too soon.
See
https://en.wikipedia.org/wiki/Westfield_Galleria_at_Roseville
But sorry, does not get much into the fire and why it was so large. old news?
----------------------------------------------------------
Soldiers' Complaint*: Nowadays the news shows the big fire, but we rarely find out the why, or what went wrong.
Few will tell at first, as there are too many lawyers, and later no one is very interested?

* a Soldier cab always complain, but it doesn't do any good!

Reply
James Evans
8/2/2023 05:07:02 pm

All of this conversation is good but no one has been able to show in the code where it states that if one system such as a dry system or even another wet system drops of a primary system, that those 2 areas have to be added together and not exceed the maximum area of a single system.

I have never seen an informal interpretation of this and as far as I know as long as those areas have their own risers and control valves and drains, they are considered their own system. We have never in the past added the areas of these systems together to indicate the overall area. Each has always been considered separately having their own system area.

Again if it is in the code I would like to know where. Everybodies opinions are great but there is no indication in the code as far as I can tell.

Reply
WES
8/2/2023 05:31:01 pm

Did some digging on this - I wasn't 100% sure myself. The questions you're asking are really good. Sorry to be bearer of bad news.

Here's what I found -

NFSA May 2013 under NFPA 13-2013, question:
" Can a dry pipe system for an ordinary hazard occupancy covering 10,000 sqft at the remote end of a building from the water supply be connected to a wet pipe system covering the rest of the building (also ordinary hazard), which is 45,000 sqft? "

Response: "No. The purpose of section 8.2.1 is to limit the amount of area that would be unprotected when a single valve is closed. For ordinary hazard occupancies, the intent is to make sure that when a single valve is closed, no more than 52,000 sqft of area per floor is taken out of service. In the situation that you have described, when the single valve on the wet pipe system is closed, it would take 55,000 sqft
of area out of service on a single floor, which would violate section 8.2.1.

One way to solve the problem would be to run a separate pipe out to the dry pipe system from the water supply entrance. That would be a significant amount of extra pipe, but it would satisfy the standard.

Another way to solve the problem would be to connect a dry-pipe system to a wet system, as long as the total area downstream of the wet system does not exceed 52,000 sqft. You could do this and save a great deal of pipe by splitting the portion of the building covered by the wet piping into two systems.
This would cause you to install an extra set of wet system equipment (check valve, control valve, alarm and drain) but would save on pipe. No physical barrier or wall would be required between the two portions of the wet system. "

Their online archives go to 2017 https://nfsa.org/tag/expert-of-the-day/, but the handbook has more - https://nfsa.org/eodhandbook/

They answered a similar question on the size restrictions - which came from Ordinary Hazard Pipe Schedule of 130 sqft per sprinkler, generally limited to 400 sprinklers, which is generally "cited as the basis of the maximum system size of 52,000 sqft". It was apparently carried over as a practical limit from the OH pipe schedule days.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT