|
We're working on a one-story school. The AHJ (Fire Marshal) is requiring inside 2 1/2-inch hose valves at the exit locations.
These hose valves are fed directly off the wet sprinkler system main - not fed from a dedicated standpipe main. 1. I'm having trouble finding code regarding feeding hose valves off of the wet system main. 2. I'm trying to determine if the pipe, off the main, to these hose valves, needs a control valve installed. Appreciate the tips and insight. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
David Kendrick
9/20/2023 08:18:38 am
This may be a local requirement memorialized in addition to the building standards.
Reply
Todd E Wyatt
9/20/2023 08:37:41 am
It is permissible to request the AHJ provide the section of the adopted Code and/or Standard for this "requirement."
Reply
Casey Milhorn
9/20/2023 08:59:39 am
I think what they are asking for are hose connections from the A/S system, not a full hose valve and standpipe system. Below is from NFPA 13, 2016 ed.
Reply
Dan Wilder
9/20/2023 11:21:52 am
What is the intent of the Fire Department for use of the hose valves? Are they being used for secondary, ancillary cleanup or direct fire fighter operations?
Reply
Jesse
9/20/2023 11:42:15 am
We see this a lot with large footprint buildings and it has to do with distance from the fire apparatus lane. We handle with just a 2.5" drop from the AS main to a hose valve.
Reply
Sharon
9/21/2023 09:57:10 am
We have been required to provide these on schools lately because they are bringing in the "Mall" criteria. This has been allowing the architect a bit more flexibility with building locations, etc.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed
