Does a trash chute sprinkler riser have to have its own control valve and flow switch?
I've only seen ones with a control valve (ball valve) only. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
2/29/2024 07:15:20 am
I've never seen that come pre-installed. I wouldn't add the cost for it either. Usually trash rooms (where the chute empties out to) has a floor drain for washdowns that should be able to handle any errant sprinkler activation. So, if the concern is that you won't know which sprinkler head is flowing or that there will be flooding while the fire department and maintenance go looking I wouldn't worry about flood damage.
Reply
Franck
2/29/2024 08:08:53 am
As indicated by Anthony, this is not a requirement.
Reply
J GOLDEN
2/29/2024 08:24:25 am
ASK THE AHJ,
Reply
Jesse
2/29/2024 08:38:19 am
I tend to avoid an autonomous riser for trash chute sprinklers and instead, feed them from the adjoining floor system. I can see the value in a isolation valve, but that adds expense and needs to be supervised. Some AHJs may require flow switches on trash chute sprinklers, but again that adds expense. Check with your AHJ.
Reply
Glenn Berger
2/29/2024 08:50:20 am
I have not seen a requirement requiring isolation valves or a dedicated flow switch for this application. Remember to have to the protective shielding installed.
Reply
In 20 years of inspecting fire alarm systems, I've seen many dozens of dedicated control valves for trash chute sprinklers. Most of them are tampered. (However, when I inspected a fire alarm system, any valve that affects a suppression system is either tampered, or it is written up on that fire alarm inspection.)
Reply
Pete H
2/29/2024 10:52:01 am
Gonna lean on all the "AHJ may vary" comment J Golden put on.
Reply
Dan Wilder
2/29/2024 12:14:40 pm
Based solely on your wording of "Trash chute sprinkler riser", which I am taking it as a dedicated riser for the trash chute, yes and no* for a flow switch/control valve. Need to know what the applicable IBC/IFC edition is. Unless there is some other requirement that I'm not seeing in the IFC, NFPA 13 or 82, it's not a requirement to be dedicated per chute.
Reply
Jack G
2/29/2024 03:58:50 pm
Please revisit “ Meyer fire “ 10-13-2021
Reply
Jack G
2/29/2024 04:42:44 pm
Also: ( see above)
Reply