Store Exposed Group A in Lowest Rack Only?

4/29/2024

10 Comments

 
Consider a high-piled rack storage area with 30 ft roof height and the following arrangements:
 
(A) Class I through IV and cartoned nonexpanded Group A plastic up to full rack height
(B) Exposed nonexpanded Group A plastics, only up to five feet
 
NFPA 13 Table 23.3.1 prescribes protection criteria for (A) as pendent K25.2 at 15 psi starting pressure; however, it does not provide protection criteria for exposed nonexpanded Group A plastics using K25.2 sprinklers where ceiling height is ≤ 30 ft. NFPA 13 Table 4.3.1.7.1.1 prescribes protection criteria for (B) as Ordinary Hazard Group 2.
 
The owner will have exposed nonexpanded Group A plastics. They have agreed in writing to maintain exposed nonexpanded Group A plastic to the bottom five feet of the racks.
 
Would storing exposed nonexpanded Group A plastics only in the lowest five feet of the rack, with Class I-IV above to the full rack height, be permissible?
 
If so, the overhead sprinkler design under NFPA 13-2022 § 20.4.13.2 would only require the more-demanding of the two criteria (which is A), correct?
 
Some have suggested that the presence of the exposed nonexpanded Group A plastic within the (A) criteria mixes with the (B) criteria to form a more hazardous condition than posed by either individual commodity / arrangement. However, NFPA 13 § 20.4.13.1 and 20.4.13.2 seem to require each commodity / arrangement to be considered independently and not to hypothesize protection requirements based on commodity / arrangement mixes. 

Long one, but thanks in advance. 

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
4/29/2024 07:03:25 am

Check out NFPA 13 (2022 edition) Table 4.3.1.7.1.1

Specifically check out Exposed Unexpanded plastics in rack protection on that chart.

If the top of the group a nonexpanded exposed storage is less than or equal to 5'-0" in elevation, that is equivalent to an OH2 design curve on Figure 19.2.3.1.1 (1500 square feet at 0.2 density).

Which is not going to be your final demand, as your esfr calculation is significantly more demanding and would prove out this requirement and your OH2 area is covered as per your 23.3.1 design as per 23.1.1(3).

CONCERNS: If you have solid shelf racks and this exceeds the requirements of "Miscellaneous Storage" and is in "Low-Piled Storage", in rack sprinkler protection is still required (4.3.1.7.2.6)

Reply
Glenn Berger
4/29/2024 08:08:43 am

Administrative control of storage arrangement / commodity is commonplace. Failure to comply with this approved administrative control is also commonplace.

Reply
NK
4/29/2024 08:18:00 am

You cannot store a higher commodity below a lower commodity in racks without solid horizontal barriers. NFPA 13, 2016 §5.6.1.2 "Mixed Commodities" and §5.6.1.2.4 "Mixed Commodity Segregation" provide guidance on when you can and cannot mix commodities. Generally speaking, you can't mix commodities without using solid barriers and in-rack sprinklers. The handbook right below 5.6.1.2.4 specifically states that FM Global testing found that placing Group A plastics below class III commodities resulted in the need for Group A plastic protection.

There are alternate in-rack design schemes in NFPA 13, 2016 + 2019 + 2022 for segregating high hazard storage in specific areas of racks, otherwise the roof needs to be designed to protect the highest level of commodity being stored.

Reply
Franck
4/29/2024 09:17:24 am

As indicated by Glenn, it is nice to have rules, but most of the time, rules are not considered on the long term.

In addition to that, NK is right.

It is not fine to have group A plastic at the bottom and another commodity above and considering that the protection is fine at the ceiling because it is fine for both taken individually.
Because they are not stored individually.

The plastic commodity needs to be considered as a plastic commodity for the entire rack and the best you can do is to provide in-racks above this storage as indicated by NK.
Then you have 2 solutions:
1- to provide solid barriers above and you only need one level of in-racks.
2. Not to provide solid barriers and consider the entire rack as plastic (with the necessary requirements in term of in-racks and density at ceiling).

Reply
David Kalinec link
4/29/2024 09:18:56 am

Unfortunately, the proposed scenario is not compliant without horizontal barriers, in-rack sprinklers as mentioned in other replies, or some other engineered solution. Assuming this is under the 2021 International Fire Code, §3204 and §3206.3 prevent this arrangement. The way I explain it to my clients is to consider the plastics on bottom as the burner underneath their stovetop grate. The plastics turn the dial to high-heat instead of medium heat. It is added fuel that otherwise would not be there.

Reply
Streeter
4/29/2024 10:07:43 am

We have done some storage arrangements similar to this and have found that is this scenario, the use of ESFRs is almost always going to be a hydraulically less demanding system than an OH2 system.
Going through the tables mentioned above will give you a more direct answer but only having to calculate the 12 most demanding heads is often a lot better hydraulics wise than 1500SF of OH2.
The layout is a bit more involved due to the 8’-10’ min/max spacing requirements, and the requirements for obstructions, and the soon to be added requirements for distance of heads from ceiling to added in 2025.

Reply
Jon
4/29/2024 01:22:17 pm

Glenn's comments are spot on. As a former AHJ with 37 years of experience as a fire marshal, I have rarely seen compliance with "promises". "I promise not to let more than 49 people into my business with one exit - until I have a sale." "I promise not to store more than 12 feet high so it is not high-piled storage - until I figure out that I have a large volume of space that I could use." "I promise not to use my large assembly venue for concerts - until I find that I can make a lot of money even though I chose not to sprinkler it."

Go to almost any big-box retail store and you will see in-aisle or end-cap displays that were never contemplated in the sprinkler design. Unless there is a way to ensure compliance with the "promise", I was not interested in it. We had a facility put up chain link and chicken wire fence above the level of adequate sprinkler protection to avoid in-racks so that the forklift operators couldn't stack materials to the roof deck.

I never considered myself to be an unreasonable fire marshal and was often told that I was reasonable to deal with. Experience has shown me that Murphy's Law can happen (and often does with fire). As a fire marshal in the neighboring town used to say: "Why don't people just design in compliance with the code rather than trying to design around it?".

Reply
Brandon Wilkerson
4/29/2024 01:59:05 pm

To those stating that this is not allowed because higher hazard commodities cannot be stored within a rack without designing to the high hazard commodity, regardless of the storage arrangement:

I submit for your consideration NFPA 13 (2022) 20.4.13.2 which states "Unless the requirements of 20.4.13.3 or 20.4.13.4 are met, mixed commodity storage shall be protected by the requirements for the highest classified commodity AND storage arrangement."

Emphasis on "highest classified commodity AND storage arrangement."

In my opinion, 5 feet of exposed nonexpanded Group A plastic is a LOWER hazard commodity/arrangement than ~30 ft of cartoned nonexpanded Group A plastic. As evidence, I submit the low-piled storage criteria in § 4.3.1.7.2 which defines 5 ft of exposed nonexpanded Group A as OH2. If this is true, then the sprinkler system must only be designed to protect the higher hazard commodity/arrangement (in this case, clearly the ESFR system).

Further, NFPA 13 (2022) § 20.4.13.1 explicitly states that design must not be based on the overall commodity mix.

So, just from an NFPA 13 perspective, it seems that one must compare all of the various commodities *at their planned arrangement*, and design to the most restrictive. Struggling to find NFPA 13 rules which dictate otherwise.

Great discussion, thank you all!

Reply
NK
4/30/2024 08:11:04 am

"highest classified commodity AND storage arrangement" refers to the most demanding commodity and the most demanding arrangement. For example, if you have class IV commodities and cartoned expanded group a plastics in a rack then you would protect the rack for the cartoned expanded group a plastics since it is more demanding. Like wise, if you have a warehouse with single-row racks and multiple-row racks you would protect the warehouse for multiple-row racks since it is more demanding.

Reply
Pete D.
4/30/2024 08:27:10 pm

This kind of goes along with what others were saying regarding mixes commodities and rack barriers. When you get into NFPA 13 sections /tables on ceiling-only protection of group A plastics in racks, it gives a 0.6 density, but it also comes with a 10 ft maximum clearance between the storage and roof. That is if youre storing 15 ft in a 30 ft building, you must protect as though you're atoeing at 20 ft. This is echoed in the General Storage requirements (used to be Ch. 12), and it's all throughout FM's design criteria, NFPA 13 tire storage, etc. I've installed a single line of in-rack sprinklers with a horizontal barrier in the past to protect class III combustible liquid IBCs in the lowest tier. Think of the horizontal barrier as a way of bringing the ceiling to the storage instead of vice versa.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT