Sprinklers Req'd for Wood Shop Training Facility?

9/15/2020

7 Comments

 
Working with a 10,500 square foot building that is primarily a wood shop (as the AHJ, fire official). In this building they basically saw cut raw lumber on a large gasoline powered (vented) saw mill inside of the building (this is an issue I question as well). This is a two-part question, at the least!

The occupants claim they are a E occupancy (based on the 2012 IBC/IFC) and that they fall under the 12,000 square feet for automatic fire sprinkler requirements in chapter 9.

I look at this as a woodworking facility over 2,500 square feet per 903.2.4.1, that would require automatic fire sprinklers.

The organization is not a school, but rather consider themselves as a vocational school that serves students working on their G.E.D. along with troubled students needing extra guidance, and they pay these students. They teach life/work skills and help with job placement.

I feel this would either fall under a B-Occupancy for training and skill development not within a school or academic program, or an F-1.

Thoughts on this part?

Next, even if we would call this an E-Occupancy, would sprinklers be required since it is under the 12,000 square feet? I would think yes because of section 903.2.4.1, however the organization says no because they believe they are an E.

​I know where I am leaning on this issue, but would welcome any other input. ​I am all about helping this organization out, but also need to take safety and property preservation into account. This place keeps me up at night with all of the students and hazards present.

​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Henry
9/15/2020 10:11:16 am

B occupancy for vocational (such as a community college)...never received any money for going to an actual school (E occupancy) so I would not classify it as that...wood working operation as well would require a sprinkler.

Reply
Bill
9/15/2020 10:54:03 am

903.2.4.1 would only apply if it is classified at an F-1, and the 2500 sq ft is not the entire building area. It would only apply to the wood-working portion where finely divided combustible waste or materials are used. If you classify it as a "B" or an "E", there would be no sprinkler requirements.

Reply
John
9/15/2020 12:55:24 pm

In my opinion the occupancy classification should be F1 based on highest hazard use of occupancy, or at least a Mixed Occupancy Classification. F1 and B.

903.2.4.1 would apply then as Bill stated above.

Reply
Tony
9/16/2020 08:58:02 am

It is not an E occupancy. IBC 305.1 is clear that E occupancys only apply to students up to the 12 grade. Based on your description, the occupants in this facility are legal adults and over the age of 18.

Generally, I do not care about the intentions of a space when it comes to classifying the occupancy, just because they are teaching students to wood work, the fire hazard is the same as professionals wood working. The fact that the students are being paid even further confirms my opinion that this should be an F-1.

I could see an argument for classifying this as a skill development, but the examples that the IBC gives are low hazard areas such as tutoring, gymnastics, and martial arts.

If this is an E occupancy, sprinklers would not be required, your entire building is is less than 12,000 square feet. So your fire area must be less than that (assuming you have no horizontal projections).

If this is an F occupancy, which I believe it is, sprinklers would be required per 903.2.4.1. That code requirement is under the 903.2.4 section so it only applies to F-1 occupancys. The sprinkler system must be throughout the fire area. So it would be the entire building or the area within the fire barriers (if that building has any).

Reply
Bill
9/16/2020 05:52:42 pm

To determine if it is a B or an F1, more information is needed. The exchange of money does not determine occupancy type. There are many vocational training programs that compensate the participants. If there is a scheduled training program, especially if there is a certification, this is most likely a B occupancy, as this would be an educational occupancy for students above 12th grade or training or skill development.

If you determine this to be an F1, sprinklers would only be required if the area dedicated to woodworking operations exceed 2500 sq ft., regardless of fire area.

Reply
Oscar Anderson
6/23/2022 08:01:38 am

What ICC Occupancy Use Group is a sawmill ? Thank you in advance.

Reply
Garen
10/7/2022 08:09:08 am

I See this is old but does the 2500 sqft mean total area or can it divided by a wall. I am looking at adding on and the way I understood it when I built my building originally is that I could build 2500sqft and have another 2500 sqft if separated by a door. I am also in the country where I have no access to municipal water supply. I have heard people using tanks for stored water and also people getting exemptions from needing a sprinkler system. Also how do they classify dry storage? Can it be over 2500sqft if not doing any machining or any generation of dust in the area other then dry storage.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT