Commodity Classification of Wood Chips, Mulch?

7/28/2023

7 Comments

 
What is the most appropriate Commodity Classification for wood chips (used for grilling) and wood mulch (used for pet bedding)?

The packaging consists of sealed paper bags that are palletized and secured with stretch wrap (plastic film) to stabilize the load onto the pallet. 

My initial thoughts would be a Class III Commodity, but NFPA 13 2019 Table A20.4(b) mentions "wood patterns" as being Class IV.  I'm not certain of the definition of "wood patterns". 

Your input and wisdom is much appreciated.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
7/28/2023 08:14:10 am

An argument can be made for various different type of commodities. Be careful of the plastic film wrapping in the analysis of storage material.

Also consider what else is being stored here and how much flexibility do you want to give to the building owner in terms of locking them down to specific storage type and configuration.

The question posed does not supply information on maximum proposed storage height or size of storage facility.

Reply
Dan Wilder
7/28/2023 08:39:51 am

Wood (lumber), wood chips, charcoal (basic)... all fall into Class III (13-22' - 20.4.3 + Annex)
The individual paper bagging keeps it at Class III along with minimal packaging described. If it gets placed into a double or triple ply cardboard box with multiple layers of separation, this will affect classification (NFPA 13-22 A.20.3 has a decent chart for this).
You did not indicate pallet style & type, that may increase the classification 1 or 2 levels (13-22 - 20.3.2)

Encapsulation will just change the density and in-rack requirements along with the storage arrangement considerations (solid pile, shelf, rack, depth, flue space..)

My thought on "Wood Pattern" is the base products used for laminate wood or the wood pattern sheets that are described below that under "Wood Products".

Reply
Craig Hanson link
7/28/2023 08:44:28 am

20.4.3.1
A Class III commodity shall be defined as a product fashioned from wood, paper, natural fibers, or Group C plastics with or without cartons, boxes, or crates and with or without pallets.

20.4.3.2
A Class III commodity shall be permitted to contain a limited amount (5 percent or less by weight of nonexpanded plastic or 5 percent or less by volume of expanded plastic) of Group A or Group B plastics.

Reply
Anthony
7/28/2023 08:45:33 am

Sounds like palletized, class 3, encapsulated.



Per NFPA 13-16 Table A.5.6.3:

Wood products (e.g., toothpicks, clothespins and hangers) -- Class III

Per FM 8-1

2.2.4 Class 3
2.2.4.1 Classify stored materials that meet the following criteria as Class 3 commodities:
A. Cellulosic materials, such as wood, paper, or natural textiles, on wood or FM Approved pallets. Products may or may not be stored in corrugated cardboard cartons.

B. Classes 1, 2, and 3 materials containing no more than 5% plastic (unexpanded, expanded, or a combination of the two) by either weight or volume.


PER NFPA 13-16:

3.9.1.11* Encapsulation. A method of packaging that ether consists of a plastic sheet completely enclosing the sides and top of a pallet load containing a combustible commodity, a combustible package, or a group of combustible commodities or combustible packages, or consists of combustible commodities individually wrapped in plastic sheeting and stored exposed in a pallet load.


When I'm iffy on an NFPA definition I like to cross check with FM data sheets. I think in this case per FM's clarification you're in class 3.

Reply
Pete H
7/28/2023 09:08:49 am

I'd go class III.

Wood Products (E.g. fiberboard, lumber, particle board, plywood, pressboard with smooth ends and edges); unbundled or non-solid blocks)

Or Wood Products (e.g. toothpicks, clothespins, and hangers).

Not too worried about wood patterns. Pretty sure that refers to things like woodworking kits (think like those little signs that say "home sweet home" or those entirely wood built toy cars). Like dress patterns, but wood.

Reply
Dave
7/28/2023 11:34:12 am

I have always assumed "wood patterns" were the library of wood master pattarns used in creating the sand molds in the foundry industry..

Reply
Franck
7/28/2023 12:01:08 pm

I would go to class III (and then possibly add penalties for packaging. pallets as indicated above).
I won't be too conservative with considering it as encapsulated just because the chips are in plastic bags. Encpsulated is for the entire pallet, covering homogeneously the top, which is probably not the case here. And the plastic film will melt very easily if involved in the fire.
The good news is that it is free flowing and easily wetted, so less problematic than wood planks (free flowing products tend to self extinguish by suffocation of the flame).
The bad news is that you may have deep seated fire where the sprinkler will not impregnate. So all good as long as the fire is from the outside. And need adequate manual firefighting, just in case...

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT