CMDA, CMSA for 12-ft of Storage with 25-ft Roof?

9/29/2023

9 Comments

 
We have storage of Class I-IV commodity, in racks, with maximum distance from floor to top of storage of 12-ft with 10-ft aisles and roof deck at 25-ft.

The AHJ correctly asserts that this storage is not incidental to the occupancy and therefore cannot be considered as "miscellaneous storage".

Is there a way that these racks can be suppressed with roof-only sprinklers, preferably CMDA or CMSA?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Alex
9/29/2023 07:14:07 am

Yes, you can get away with ceiling only protection using CMDA - NFPA 13 (2013) Table 16.2.1.3.2

Reply
Pete H
9/29/2023 07:28:21 am

It's not miscellaneous storage.

But it's not high-piled storage either.

It is "Low Piled Storage" ... a term rarely used and frequently confused with Miscellaneous storage. And a term that applies to all the storage configurations found in NFPA 13 (2016) Table 13.2.1 "Discharge criteria for miscellaneous storage" (but still applies to your low-piled storage as per Section 16.2.1.2.1.)

Anyway, you can do ceiling only protection with cmda sprinklers for this.

And if you convince them to limit their class iv commodity to less than 10'-0" from the floor (so make these bottom shelf items), you can even do OH2.

Reply
Glenn Berger
9/29/2023 08:08:23 am

I concur with the opinion that opinion that you do not have miscellaneous storage.

Based on the condition stated you most likely can use ceiling-only sprinklers. You need to go through the many tables concerning storage and pick the most suitable condition that is applicable. Make sure that you are giving the owner some leeway to modify the initial storage configuration.

Reply
Casey Milhorn
9/29/2023 09:58:40 am

I agree with everyone. You probably have low piled storage and will follow those guidelines. You will have to go through the different options to compare CMDA, CMSA, ESFR, etc. Keep any group A plastics below 5', Class IV below 10', and you will be at a very reasonable demand.

Reply
Randy rathert
9/29/2023 10:24:51 am

Im still learning here, so can you explain what OH2,EH2,and EH1 are?

Reply
Joe Meyer
9/29/2023 10:44:08 am

Hi Randy -

These are Ordinary Hazard Group 2 (OH2), Extra Hazard Group 1 (EH1) and Extra Hazard Group 2 (EH2).

Based on the question I would highly encourage you to get into some fundamental resources, like NFSA's Layout Book (https://nfsa.org/layoutbook/) or get into some fundamentals training as this is a very important and very fundamental topic.

All the best!

Reply
Jesse
9/29/2023 12:35:03 pm

Absolutely you can protect with CMDA ceiling only. Just pick a point on the design curve for protection of C-IV without IRAS

Reply
AB link
10/2/2023 08:30:37 am

I agree with the points made earlier.

To delve deeper into your fire protection strategy, here's a business-savvy approach:

You can opt for ceiling-only protection by employing CMDA (Control Mode Density Area) sprinklers for this storage configuration, aligning it perfectly with your specific fire protection requirements.

Adding to this, consider this strategic perspective: If you can successfully advocate for the Class IV commodities to be kept below 10 feet from the floor, essentially positioning them as bottom-shelf items, you open up the possibility of implementing OH2 protection.

Reply
Quentin M Maver
10/4/2023 10:52:07 am

HIGH-PILED COMBUSTIBLE STORAGE. Storage of
combustible materials in closely packed piles or combustible
materials on pallets, in racks or on shelves where the top of
storage is greater than 12 feet (3658 mm) in height. Where
required by the fire code official, high-piled combustible storage
also includes certain high-hazard commodities, such as
rubber tires, Group A plastics, flammable liquids, idle pallets
and similar commodities, where the top of storage is greater
than 6 feet (1829 mm) in height.

From NC IFC

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top May '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    NFPA 415
    NFPA 45
    NFPA 495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT