We have an original 17,000 sqft building built during the 1970's which has a masonry deck on OSB boards on steel structure. The original building had a continuous gypsum board ceiling at the bottom of the trusses, and no sprinkler system. Lay-in ACT ceilings have been added over the years and a lot of the gypsum board has been damaged or removed.
Due to the exposed OSB boards, we've listed the structure as Type V-B. As part of the new project in the building, we will be adding a sprinkler system. Is there a code-compliant way to avoid sprinkler protection above the ceilings? Perhaps a post-factor spray-on fire retardant? Thank you for your input. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
7/24/2023 08:08:13 am
This is a discussion point with the AHJ and others having interest in the building.
Reply
Dan Wilder
7/24/2023 08:42:30 am
This will likely be an AHJ call so I'm speaking on what would likely happen in my neck of the woods...it's going to be sprinklered above and below. If the deck was fire-treated, those chemicals are not forever and I would hardly call an entire roof deck "limited" or "minimal". The space is deeper than 6". The access needed for hanging also presents an issue as the will need to be access holes for the field to install the hangers to the structure. The costs would be better spent for all installing trades to have clear access to the structure by demo of the lower gyp board in lieu or access & repair.
Reply
Jon N
7/24/2023 10:03:04 am
By definition in the codes, fire-retardant treatments for (fire-retardant-treated - FRT) lumber can only occur during the manufacturing process of the lumber. To the best of my knowledge, there is no after-market spray, brush, or roller-applied products that will make ordinary lumber into FRT lumber.
Reply
AL
7/27/2023 04:51:46 pm
What about NFPA 13-2019 omission allowances:
Reply
Todd E Wyatt
8/1/2023 08:43:10 am
You are correct ... NFPA 13 permits ommissions of an automatic sprinkler system (ASPS) including "concealed spaces."
Reply
Todd E Wyatt
8/1/2023 08:43:57 am
REFERENCES
Todd E Wyatt
8/1/2023 08:45:00 am