When Can Pipe Just be "Similar Size" to Existing?

12/15/2023

7 Comments

 
Does NFPA 13 address the ability to size sprinkler pipe simply by being "sized by similarity"?

For instance, I have a small room that has (4) 1/2" pendent sprinklers to be located in it. I cannot determine any pipe routing from above due to an old ceiling but can verify the lines are 1-1/2" schedule 40.

I've heard of this method being used but do not find it in NFPA 13 so I'm hesitant to use this method.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
12/15/2023 07:58:22 am

Are you trying to not provide calculations for a project? Typically, when we provide TI services, the existing piping schedule, piping method, and sprinkler K-Factor gets followed or we provide calc's to prove something new (like adding flex hoses vs hard pipe).

If the rooms are like for like along with the sprinklers and piping methods are like for like, none of my AHJ's require calcs. If we need to double up sprinklers in an area or add a branch line to avoid loading up a branch line, depending on its location to the riser and what the calc plate indicates for calc area and hazard, it is a case by case basis.

Reply
Glenn Berger
12/15/2023 08:12:36 am

In small applications, the replace in kind method tends to be acceptable as long as the contents/room being protected is "Light Hazard."

I do feel your pain when trying to retrofitting small portions of old facilities.

Reply
Jesse
12/15/2023 08:50:14 am

I feel ya. Seems this is Light Hazard and I'm guessing by the age and Sch 40 pipe, this may be a Light Hazard Pipe Schedule. In that event, yep.

The requirement to prove hydraulic efficacy rests with the AHJ, and all of our respective AHJs differ. I do have one or two AHJs that would require calcs for this, but most of them are ok with it.

Reply
Casey Milhorn
12/15/2023 08:56:45 am

There are millions of different scenarios that NFPA 13 just cannot cover, especially when it comes to remodels, upfits, etc... Not that 13 does a bad job, it just isn't practical for it to cover everything. Many AHJs have their own rules on this. One of my favorites is not needing drawings for 10 heads or less being relocated, and not needed calculations for 10 or less new sprinklers (when matching existing pipe schedule). Of course even this can be abused, but it's a good starting point. But to answer your question, it's going to be AHJ specific. I've found most AHJs just want some type of common sense reasoning on why you are doing what you are doing, and if they trust you and know you are ethical and knowledgeable, they will typically show a lot of grace.
Now, that being said, there are some AHJs that really just don't understand or are mistrustful of everyone. If you look at the stats, specifically in light hazard occupancies, the vast majority of the time one sprinkler controls or extinguishes the fire. I've actually had a small restaurant under construction, with only test water on it, where the sprinkler extinguished the fire (some paint rags ignited in a plastic bucket). I think AHJs, and even us sprinkler designers/engineers, get carried away sometimes on being ultra obsessed with the details. Being in this industry for some time now, leaving a head out of a calc area, adding one too many sprinkler heads from 1", etc.... doesn't keep me up at night. Unsprinklered buildings, unknown valves in the yard being shut off, whole sections of buildings unsprinklered because of bootleg construction, 30' of group A plastic storage in an OH2 building, out of commission fire alarm systems, etc... is what keeps me up at night. Not that I think we can ignore the small details, but we as an industry can do better educating AHJs to the bigger issues. Major on the majors, minor on the minors.

Reply
Alex
12/15/2023 09:29:55 am

If the system is designed as pipe schedule, I can see it working but if its a hydraulically calculated deign, I don't see how you can justify simply matching pipe sizes since you will be adding fittings and additional sections of pipe.

Reply
Jack G
12/15/2023 12:02:41 pm

When we calculate a system it is “the hydraulically most remote area “.
We then size similar branch lines like the remote area. In essence we ‘ve created a “ hydraulic pipe schedule “ for the remainder of the system.
Areas that are not piped like the remote, but are closer to the source,need a “ check area calculation” in my opinion, which I include with my submitted.
So if your area is pretty similar to the remote, modifications I feel can be made per the systems “ hydraulic pipe schedule”.

Reply
sean
12/31/2023 06:01:48 pm

I am a reviewer so i take these factors into account.
1 - does the information presented show how the existing system was feed.
2 - does the existing feed seem rational
3 - how extensive is this work? is it 1 head or 100 heads

So if i have a system that is made up of a tree with 1-1/2" branch lines I would not have an issue with a small additional branch line installed based of the existing hydraulic basis. If you need to do this for multiple lines I become wary.

There is really nothing in the code to back it up more than you are just backing up the original design. Same way with a relocate how do we know the arm over and drop wont be an issue most of the time? experience.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT