Replace Existing ESFR K14.0 in Existing 40' Deck?

9/23/2021

16 Comments

 
I was asked to evaluate a warehouse that was built in 1996 for a new racking permit.

The original fire sprinkler system was designed with ESFR sprinklers with a K factor of 14.0. During the evaluation I found that the building peak was 40'-0" tall. Knowing that NFPA 13 no longer allows K-14 ESFR sprinklers in a building over 32'-0", I informed the building owner that the existing sprinklers need to be replaced with a larger-orifice ESFR sprinkler.

The building tenant has tried everything they can to find away around this and does not understand why the building is not grandfathered.

I am just curious if anyone else has encountered this situation and what the outcome was.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Dan Wilder
9/23/2021 07:57:30 am

The area of the new racking would need to be upgraded but areas outside of that scope should be excluded...however, in many cases (justifiably in most of them) this provides the AHJ the means to require building upgrades. Has the AHJ adopted the newer NFPA that removed the allowance (I'm assuming so but it's an argument if not)

The 2018 IFC (what I have available) gives the AHJ the power to require the upgrade within due to the new work being performed:
-Sections 101, 102
--102.1 Construction and design provisions
--102.3 Change of use or occupancy
--102.4 Application of building code
-Section 901.2 Construction Documents
-Section 901.4 Installation

In the case of a large financial impact, we have been successful in having the owner make the upgrades in increments over a specified timeframe and documented in a signed letter from the owner. Seeing how the ESFR's are up for or beyond testing anyway (NFPA 25 - 20 years for fast response), are they passing that testing where replacement may be needed regardless of new scope?

Reply
Glenn Berger
9/23/2021 08:09:29 am

Situation is always ugly. Good Luck

Reply
matt
9/23/2021 08:30:32 am

I have found on occasion that swapping out k14's for k16.8 ESFR heads will still function hydraulically and also will provide updated coverage criteria. That has been a less-expensive route for upgrades. That or in-racks for the revised storage plan.

Reply
matt
9/23/2021 08:33:14 am

...also, it is technically grandfathered right now since they are using the facility under outdated design criteria with their current permit. If they need a new racking permit, then it is a new use. You can't "grandfather" a new use. (generally)

Reply
Alex
9/23/2021 05:12:46 pm

My thoughts exactly ^

Reply
NK
9/23/2021 08:34:14 am

We run into this often. 14K ESFR heads were really popular in our area in the early 2000's which is terrible when tenants change. If new racks are being added or modified to an existing warehouse we usually don't have problems matching the existing design criteria, but new use and occupancy typically requires the system to be brought up to the currently adopted NFPA 13 standard. Most of these buildings have fire pumps so there are multiple things you can do to upgrade the existing system without significant modifications. Consider in-rack options if you don't have a fire pump. Talking to the local AHJ first is usually a good place to start.

Reply
M
9/23/2021 08:38:58 am

Could you consult with the AHJ to allow the use of FMDS 8-9?
Table 8: Class I-IV and CUP allows K14 ESFRs under a 40' roof.

Reply
Jesse
9/23/2021 09:00:31 am

I strongly dislike the "grandfather" concept. We've always operated under the "fire doesn't care about your grandfather" mode.

Its a difficult situation, I get it. K=14 in that building height were pretty common 15-20 years ago. Since then, we've had some experience and seen testing data indicating K=14 wasn't the best approach, which is precipitated the standard change.

FM still allows this in storage applications for up to unexpanded Group A / cartoned. Maybe the AHJ will allow this as an alternative method of compliance.

But their insurer may not.

Reply
Franck
9/23/2021 12:27:19 pm

Fully agree with Jesse regarding the "grandfather" concept.

If there is a change, there is normally a good reason and the path between an adequately controlled fire and a disaster is very narrow with storage arrangement. And the higher the storage and the height of the building, the less flexibility you have.
Not to speak about the change of commodity.
There is a huge number of fire losses because of inadequately protected storage warehouses or change in occupancy.

Reply
Matt
9/23/2021 09:06:50 am

be sure to review the specifics in the FM data sheets before trying to use those criteria. The FM discharge requirements can be much higher than NFPA.

It is possible that attempting to use the same piping/head layout to meet an FM design could be more costly than in-racks or a head change. if it is even possible.

Reply
Bob
9/23/2021 11:15:10 am

Upgrading or changing out racking is different than a change of use and does not necessarly mean an increased hazard. We have hit similar situations related to smoke venting and tenant changes in existing warehouses.

Discussion wise, there does not appears to be any dispute about the current requirements nor about the validity of the original design using K14 heads. However, in general from a design standpoint almost ALL warehouse fire protection designs from 20+ years ago are not as robust as they are now, but if the hazard has not increased you should not have to do major reworks every time a tenant moves out or just wants to upgrade racking.

If this was originally permitted and used as high piled storage in the past and the new racking does not create a higher hazard than as originally permitted, then many AHJ's would go along with the existing system.

From an Owners perspective, one would hope that the design professionals engaged would sort through all of the "gray area factors" and provide an accurate view of the changed risk factors and not just apply “current code” blindly in this type of situation. From the limited perspective garnered from your initial question (and not knowing the AHJ involved), it appears your facts are correct, but there may be some pragmatic nuances to consider here also.

Reply
Joshua Freedman
9/23/2021 04:41:57 pm

As a property consultant for an insurance company, I often have to tell building owners that we honestly don't care if the City says they are grandfathered in for one thing or another, the City isn't going to pay for the damages caused by a fire. If I have to rate a sprinkler system as inadequate, they can see their insurance rates double which can be quite a lot of money and puts the investment of a few sprinkler heads into a different perspective. Also, the cost of doing the upgrade now while you are out there and have the engineering and permitting going on is going to be a lot less that if they have to do the update down the road and start from scratch. Just from a cost/business perspective, it would probably be in their best interest to upgrade.

Reply
BOB
9/24/2021 09:11:39 am

I think Joshua makes a very valid point from about the insurance issue and I have heard it often "in the field".

However, as a general contractor working with some very large national companies and limiting this discussion to warehousing only (Note: on the production and manufacturing side the "loss production" risk factors do seem to motivate change) this insurance rate increase concern centered around grandfathered items has seldom seemed to be a factor for their decision to upgrade or not.

For our clients this is seldom an initial cost issue and their decisions seem to be made based more on long term return on investment. I know this branches into things like "marginal cost of production" to replace losses, etc.

Does anyone have some additional insight on this insurance aspect?





Reply
Brian Gerdwagen FPE
9/24/2021 08:54:43 am

To make a real quick point:

K14 ESFR's were not "popular" in the late 1990's and early 2000's. They were all we had, unless you wanted to use a Specific Application storage sprinkler.

Reply
Stef
11/12/2022 04:19:43 am

Is it technically easy to remove current K14 heads by bigger orifice ones (K17 or even bigger) considering threadings are different... ?
What does that involve?

Reply
Andrew Valente
4/27/2023 09:55:08 am

k14 and k17 (16.8 actually) are almost always 3/4-inch thread.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT