Number of Sprinklers to Include in Calculation?

11/12/2020

4 Comments

 
A couple recently submitted questions relate to the same topic: 

(1) Extra hazard, grid pipe layout of approximately 1,800 sprinklers. What is the criteria that drives the specific number of sprinklers that will be operating together?

(2) What's the best way to determine the design area and number of sprinklers within a calculation for a parking garage?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
James
11/12/2020 07:29:21 am

If you're in an NFPA 13 system, NFPA 13 Chapter 23 annex can help with determining the remote area shape once you have your remote area size from the code itself. Some criteria that is not design/area driven will stipulate a specific number of sprinklers in a calculation.

If you're using a different design standard, such as FM Global, then there is typically also guidance on either a remote area size or number of sprinklers to include in the calculation.

If you're looking for a full-length explanation on how to determine remote area size and shape, I would recommend NFSA's book Design and Layout of Fire Sprinkler Systems, or Fire Protection Hydraulics and Water Supply Analysis by Pat Brock.

Reply
franck
11/12/2020 11:53:41 am

Once you have your design density/area of application, you take the number of sprinkler to cover this area.
As an example, if your design is over 2500 sq ft and your area covered by sprinkler is 100 sq ft, you need 25 heads.
The area of application is not related to the total number of sprinklers installed. It would be the same with a system with 40 sprinklers or with 200 sprinklers.

Note that with 1 800 sprinklers you may have several different sprinkler systems (there is a maximum floor area per system depending on the occupancy) and as many most remote area calculations. If different hazards on a same system, you may also have different calculations for each hazard.

As indicated above, NFPA 13 will give guidance to determine the correct shape for the calculation

In all cases, I hope the designer and/or the sprinkler contractor knows how to proceed

Reply
Franck
11/12/2020 12:40:18 pm

Regarding your question for parking structures, you can have a look to NFPA 88A Standard for parking structure.

Note that according to this standard, there is no need for sprinkler protection in open parking structures.
An open parking structure is when you have have uniformly distributed openings on two or more sides (see § 5.5 for more details on openings size and distribution)

The sprinkler protection, according to NFPA 13, is Ordinary Hazard group 1 for parking garages.

Unfortunately, this may be revised in the future as car composition has greatly evolves over the time and the behavior of cars involved in a fire is not the same nowadays compared to former times.
There are several reasons, among which:
- the extensive use of electronic equipment (more combustible load inside the car)
- the extensive use of plastic components where metal was used in the past (example, front and back side of the car - bumpers)
- the use of plastic tank for the fuel, where it was metal in older time. In case of fire, the flammable fuel will be released immediately and contribute to a spill fire)

Future design may be more Extra Hazard that OH.

See an excellent article in the NFPA magazine (March-April 2019):

https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2019/March-April-2019/Features/Protecting-Parking-Garages#:~:text=NFPA%2013%20classifies%20a%20parking,not%20a%20very%20big%20one%2C%E2%80%9D

There is a recent history of a very bad event that happened in a parking structure in the UK (Liverpool on December 31, 2017) where hundreds of vehicles burnt (not a sprinklered garage) - see :

https://www.bbc.com/news/uk-england-merseyside-46290095

One good news with the design, you don't need to consider the 18 in. (450 mm) clearance between the sprinkler and the top of the car for vehicles in concrete parking structures.




Reply
Benedic R. Mejorada
10/25/2022 04:17:54 pm

interested in calculation software

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT