Life Expectancy of Wet and Dry Sprinkler System?

9/22/2020

8 Comments

 
What is the average life expectancy of a wet and dry fire sprinkler system?

​​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Casey Milhorn
9/22/2020 10:14:24 am

That is a tough one to answer. We've seen wet and dry systems begin to have major corrosion issues as soon as 5 years, and have seen others close to 100 years old that are still in operation. Some of the variables are schedule of pipe used (schedule 40 is going to better than schedule 10 of course, because of the thickness), proper pitch for dry system and avoidance of trapped water wherever possible, installation and design to avoid trapped pockets of air in wet systems, installation of air relief valves where wet systems are installed with pipe at pitched ceilings/roofs, installation of a nitrogen system when applicable, installation of galvanized pipe when exposed to exterior or corrosive elements (sometimes galvanized pipe can be a bad call in certain situations unless a nitrogen filled system is provided), and just overall proper maintenance will extend the life of a system many many years.

Reply
Richard OLeary link
12/10/2021 08:33:50 am

Corrosion and bacteria can destroy fire sprinkler pipes in as little
as 5 years. Understanding the internal environment of a fire sprinkler system can determine the useful life of the steel pipes
that make up these systems. Bacteria (odor) Corrosion (black magnetic water). We protect ALL water applications with treatment programs to protect against this issue. Clean & treat and protect
with U.L.Listed products. Create a cleaner and healthy work environment. www.huguenotlabs.com

Reply
Jim McHugh link
9/22/2020 10:15:39 am

There are many factors which can effect longevity but an often cited study by German testing authority VDS stated "... found that 73 percent of dry systems have significant corrosion issues at 12.5 years old and 35 percent of wet systems have significant corrosion issues at 25 years after installation. For that reason, VdS guidelines specify that wet systems be thoroughly inspected after 25 years and dry systems after 12.5 years, adding that the inspections include an internal examination with an endoscope and a check of the residual wall thickness with ultrasonic measurement. That’s more relaxed than the NFPA recommendation of inspections every five years.

Reply
Joe
3/11/2021 06:12:09 pm

Our inspector told us we have to replace all dry sprinkler heads in our condos - garages and balconies - because it's more then 10 years old. About 70 total. True?
Is there such regulation? This is in GA. Thank you!

Reply
Brian Richard Cook
4/17/2021 10:12:34 am

Yes after 10 year Dry pendants or sidewall heads either need to be sent out for UL testing or change them out that is NFPA 25 Inspection and Testing

Reply
Joe
4/17/2021 10:38:20 am

I read somewhere that on-site testing is a possibility?
That you need to test one out of the same group and if it passes, it's OK for all of them.

Kit
8/4/2023 09:04:48 pm

I live in a condo with a wet residential system and it is a nightmare. After being there 15 years the problems started. Frequent leaks and even sprinkler heads going off for no reason. I am currently painting a bathroom and bedroom and replacing the flooring due to a sprinkler malfunction. Thecwater remediation experience was horrible. One building had all sprinklers replaced and they are still having problems. The real kicker is there was a unit that actually had a fire and no sprinkler activated! Once I am done with the repairs from this thing I am selling and leaving this place. You can be sure I will move somewhere without fire sprinklers.

Reply
Kord Fire link
10/9/2025 04:18:40 pm

We’ve seen similar results in the field. Corrosion and MIC can drastically shorten system life if untreated. Regular internal inspections and water testing go a long way, especially when combined with proper treatment programs to control corrosion and bacteria. That’s the best way to extend both wet and dry system lifespan.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT