What would a proper hazard classification be for a casino gaming floor area?
The project is under NFPA 13, no known insurance requirements. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete
7/15/2021 06:57:15 am
It's not in 13's code directly.
Reply
Glenn Berger
7/15/2021 08:34:39 am
I agree with Pete's assessment above. I do note that your question did not say the casino was in Nevada. Given the various finishes, exposed surfaces, and the high density of machinery - OH2 per Factory Mutual and NFPA 13 would be applicable.
Reply
Dan Wilder
7/15/2021 08:36:44 am
From working in Clark County, they had some very specific language for the design requirements for Casinos. OH 2, 11.2K@30PSI minimum QR Sprinklers, Ceiling height vs Design Area requirements (ceiling height x 100 for remote area size), ceilings over 50' require design analysis....we had some very large pipe size systems.
Reply
Franck
7/15/2021 10:46:34 am
Fully agree with the above comments.
Reply
10/6/2026 01:45:53 am
Interesting and informative look at how casino gaming floors are classified from a fire-safety perspective.
Reply