MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Gang All Main Drains Together? Any Downsides?

12/20/2023

10 Comments

 
Can all main drains can be joined in one pipe?

If they can, does this pipe need to be capable of handling all flow at the same time?

Are there any downsides to ganging them together?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Daniel Arnold
12/20/2023 08:10:08 am

If I understand your question, in my view ganged drains should not be installed on a dry system as it /they may functionally create a semi gridded system that could cause delay valve opening and delivery times.

Reply
Daniel Arnold
12/20/2023 08:12:25 am

Are you only asking about wp main drains? If so, I see no problem with that.

Reply
Jesse
12/20/2023 08:17:50 am

I think the OP is referring to main drains. I don't see a problem with ganging multiple main drains from wet-systems

Reply
Andrew M.
12/20/2023 08:43:19 am

In NFPA 13 2016, - Table 8.16.2.4.2 will size the drain based off of Riser Size. When Drains are joined into one pipe (Drain Riser) the drain size must be one size larger than any drain tying into it per 8.16.2.4.8

Reply
Dan Wilder
12/20/2023 09:43:24 am

Truly depends on what is being drained.

If it is individual floors, the one size larger is not an issue from connection to the final discharge point as the chance that multiple systems are being drained down at the same time are slim.

If you are using the gang drains for PRV hose valve testing, I would highly suggest increasing the size pipe as the additional standpipe drains are combined. We had this scenario on a previous 50 story with a center pressure zone and PRV's on the high end (no ability to drain to a roof). Trying to push 1000 GPM through a 3" pipe was....problematic. Unfortunately, with the size increase (we ended up with a 4" gang drain at the basement), the AHJ required bracing.

Be very careful with any dry or preaction systems located along that same gang drain that do not have an additional check valve in the piping prior to the gang drain as these will just become a water feature at the wrong time.

Also, make sure that any of your riser pressure relief valves are not trimmed in anything but stainless steel flex or hard pipe (water feature again), the pressure from some of these tests will blow off or split those plastic hoses and friction clamps. Also, a nice thing to have is a 1/2" spring check valve and a globe valve at the top of the drain that can be opened for testing to avoid a huge negative pressure situation within the drain piping.

Reply
Alex
12/20/2023 11:43:11 am

I have no issue with tying in multiple drains. Confirm piping sizing as Andrew mentioned.

Reply
Glenn Berger
12/20/2023 12:37:20 pm

Main drains can be tied together and sized for one system being drained at a time. Aux drains on wet systems can be tied together. Aux drains on dry or preaction systems needs to be reviewed to ensure a grid is not being introduced into the system.

Reply
Anthony
12/21/2023 07:10:23 am

I concur with Glen, Andrew and Alex here.

Reply
sean
12/31/2023 06:09:05 pm

Yes.

keep in mind that draining down the system is now significantly more dirfficult

Reply
Streeter
1/8/2026 11:58:41 am

I am going to put this here for future reference if anyone comes back to this thread, specifically for dry systems.

Where there are multiple adjacent trapped branch pipes in a dry system tie-in drains shall be provided, and be limited to 1". (Per the commentary they should be avoided if possible, but we know that's not always going to be the case.)
​
[NFPA 13 2002 §8.15.2.5.3, 2007-16 §8.16.2.5.3, 2019 §16.10.5.3, 2022-25 §16.10.5.3.6]

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT