MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does a Pendent (Horizontal) Meet NFPA 409?

1/11/2024

8 Comments

 
We have a steel aircraft storage hanger Group 1. It's approximately 50-ft high with exposed steel columns requiring a fire rating per NFPA 409-2022 Edition.

The steel will not be fireproofed but will be protected with sprinklers in accordance with NFPA 409 5.6.3.4.

Can pendent sprinklers, installed sideways, be used to satisfy NFPA 409 for column protection?

In the past we have protected the columns with sidewall sprinklers spaced according to 409 and on alternating sides of the column. Then the sidewalls were changed to pendent sprinklers installed horizontally to provide better spray distribution on the columns as the sidewall spray tended to (in theory at least) bounce the spray back in stead of vertically.

This approach has been accepted by EOR and AHJs alike.

NFPA 409 states that "wetting of the lower sprinkler should be considered" although multiple level sprinklers were never used. I'm not sure how this plays in.

I recall reading that pendents installed horizontally could be used for column protection due to better spray distribution, however, I cannot find that in code.

The client is not open to fireproofing or intumescent paint; column sprinkler protection is in the bit and is going to be used.

All is appreciated!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
1/11/2024 07:54:48 am

There are several sections within NFPA that state "Sidewall" specifically, others just reference nozzles or open-head sprinklers along with the GPM requirements based on area of coverage. I'm not seeing a 409- 5.6.3.4? You did not specify if the sprinkler protection was a closed or open sprinkler design. IMO, if closed, stick with a sidewall, if open, allowable in any orientation. If the EOR/AHJ has bought off on the AMM approach, document appropriately and pipe-on!

13-22'
20.14.2.2.4.1 - indicates sidewall
20.15.2.1 - indicates sidewall


409-22' - Only indicates "discharge devices" within 7.7.3 (and subsections) but requires the 10' vertical distance AND the 0.25 GPM/FT² wetted area. The intent is wetting in a downward direction hence the 10' max vertical requirement and I'm not onboard with providing coverage "upwards" from a pendent installed sideways or what benefit that has unless there are obstructions internal to the webbing (stiffeners) that are trying to be accounted for.

There is reference to NFPA 15 (22') where 7.4.3.4 applies and you have described within the question for protection.

The advantage of a sidewall would be the nearly 180° coverage at the top of the boss fitting allowing the sprinkler to essentially be buried within the flanges of the column and still available to provide the 100% wetting (pipe outlet right to a sprinkler instead of addition pipe/fittings for positioning). A pendent would need to be further out to provide the same 100% wetting coverage within an "I-Beam" configuration due to the conical distribution pattern.

Reply
Kimberly Olivas
1/11/2024 09:37:52 am

So, would a horizontal sidewall with the deflector to the side be the best, then you get the 180 degree spray going up and down on the column, is that you were envisioning?

Reply
Dan Wilder
1/11/2024 01:22:17 pm

No, but I can see that inference.

The HSW would be installed normal with the water spray in a horizontal direction into the webbing. Let gravity handle the rest.

The only function of this is to make sure the steel stays at a reasonable temperature via the cooling effect of the water thus keeping its integrity.

When installing these in the past, we used a vertical pipe attached to 3¼" unistrut that sandwiched the beam. The outlet faced into the webbing and the HSW was installed directly onto the pipe outlet...protected the sprinkler and was a quick install.

Chris Leaver
1/9/2025 03:55:10 pm

Wondering if anyone has specific guidance or reference to how far from the top or ceiling to start the applicable spacing for protecting columns. Depending on the what is driving the protection, standards or FMDS state 10 ft. or 12 ft. spacing and opposite sides (so 20 ft. or 24 ft. on spacing on the same side), but no specific guidance on how close to the top/ceiling you need to be.

Have a design were the side wall sprinklers are protecting 30 ft high and sprinklers are spaced vertical from the bottom at 12 ft and 24 ft (opposite sides), is a third sprinkler required to properly cover the 30 ft.?

Reply
Fred Walker
1/11/2024 08:41:08 am

NFPA 409 is open on this, leaving compliance to NFPA 13 with the limited guidance in Chapter 7. Don’t read more into 409 than is there, if the column protection complies with NFPA 13 and the limited requirements of NFPA 409 Chapter 7 then 409 is satisfied.
From there it engineering judgement and AHJ approval.

Reply
Jesse
1/11/2024 09:31:31 am

Agree with everything here thus far. Its easy to read too much into standards.

Personally, I'd go with the sidewall.

Reply
O.P.
1/11/2024 11:10:53 am

As I originally posed the question, I was more inclined to go with the pendent in the horizontal position, due to anticipated "bounce back" from a horizontal discharge, However, as Dan stated, " The intent is wetting in a downward direction".

With that in mind, I feel that using a sidewall now is the better option as the water will certainly wet the column web

A few items inadvertently omitted in my original post.
1- Overhead Wet system to be installed ( No foam)
2- Column sprinklers located in between flanges on opposite sides, spaced 10 ft vertically.

The answer as to whether the pendent could be used horizontally can be found in NFPA #13 (2016) 8.2.1.2

Thanks for the insight everyone - very informative.

Reply
Patrick Drumm
1/11/2024 01:09:57 pm

O.P. I appreciate your original question because although you observed something in the field that had been previously installed (swapping of sidewall to pendents in horizontal position), you still want the code back-up to perform that type of installation in the future. I sometimes find others simply see things in the field and assume they were done properly and that is a dangerous game to play.

In regards to your requested code-path. I start in Chapter 5 of NFPA 409 at Section 5.6.3. In the appendix it states that "Additional guidance pertaining to fixed water spray systems can be found in NFPA 15" as well as stating that "The design of such protection should take into account factors such as the shape of the column, wetting of lower sprinklers, obstructions, and type of discharge device." Obviously, the last item being the most important to us.

I think the code section your looking for to get the buy in from AHJ's would be NFPA 15 Section 6.2.1.4. - "Where approved, sprinklers shall be permitted to be used in water spray systems and installed in positions other than anticipated by their listing to achieve specific results where special situations require." The text of this section is very similar to NFPA 13 Section 8.3.1.2.

I agree with your follow-up post though. I like horizontal sidewalls installed per their listing at 10 feet max intervals. It's a similar installation to what is required in storage occupancies where column protection is needed - See NFPA 13 Sections 16.1.4 & 17.1.4.

NFPA 13 & NFPA 409 References are 2016 Editions.
NFPA 409 References are 2017 Edition.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT