Combine Trapeze Hanger and Seismic Brace?

7/8/2022

8 Comments

 
I am planning a sprinkler system for a warehouse which is in a seismic area.

Because of the ceiling structure, we need to use trapeze hangers, and possibly combine it with the seismic bracing.

We are planning to use steel angles attached to concrete purlins, based on the sketch below, and put the seismic bracing to this steel angle (like we usually would do with a trapeze hanger).
Picture
Is something like this allowed?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
7/8/2022 07:45:45 am

This would be a question only a structural engineer can answer. The lateral & lower shearing/twisting forces hitting that lower purlin are a big question along with sizing of both the angle iron and the attachment hardware to/through to the purlins to the adjacent secondary structure.

Reply
Glenn Berger
7/8/2022 08:11:33 am

My gut reaction is that this would not be allowed.

Reply
David Kendrick
7/8/2022 08:31:11 am

NFPA 13 is published with the engineering using best available technology and consensus of the industry for product application.

When you step away from what is printed you have the privilege of pursuing your own engineered product and application.

There is a huge responsibility to interpret without the proper credentials and appropriate liability insurance.

Difficult as it may seem using the listed products and standards available is the cleanest approach.

Reply
James Phifer
7/8/2022 08:41:28 am

I believe NFPA 13: 9.3.5.1.4 (2016 ed) addresses this but you would need to prove the angle iron is capable of meeting your seismic needs.

Reply
David Pitts
7/8/2022 08:47:53 am

Looks like you would be better off attaching the seismic bracing directly to the concrete tee with a Hilti Kwik Bolt. Like Dan Wilder said this would be a question for the structural engineer.

Reply
Cliff Schulze
7/8/2022 08:58:29 am

I would be concerned about drilling through the bottom of a concrete joist like that. I've worked on projects where they wouldn't let us connect to the bottom third of a concrete joist because that's where they have rebar installed.

Reply
Ryan Hinson
7/8/2022 09:33:50 am

While your approach would appear to be feasible, as previously stated, you are now in the structural engineering realm. I would also wonder the following:
- Why not use the trapeze for its prescriptive sole purpose of supporting the weight of the water-filled pipe?
- Why not use the allowed designer-chosen L/R up to 300 on the sway braces used for their intended purpose to resist lateral loading by extending the bracing to the top of the concrete tee?
- What is the depth of the depth of the tee/purlin?
- Are you intending for only lateral braces off this configuration or longitudinal as well? Note that the required longer leg being vertical for the trapeze member is good for vertical loading but is less conducive to a longitudinal brace where the loading is directed across the member in the orientation where the section modulus is reduced.
- Would you be planning on bracing multiple mains off the same trapeze member? If so the accumulative loading of the trapeze member would have to be verified both in a vertical load for each water-filled pipe AND in horizontal loading from each pipe braced in this trapeze section.

Without a structural engineer's buyoff, I would recommend using the prescriptive methods already in existence separately and move on.

Reply
Anthony
7/11/2022 08:56:28 am

Per NFPA 13-16 9.1.1.3.1 and 9.3.5.1.4 you can in fact use the same support for both sway bracing and gravity load support.

However, as most have mentioned above this is a bad idea from a liability standpoint.


Some thoughts on the proposed hanger detail:

1) You're placing the pipe through the T in what appears to be a lower third. That's where the T experiences the highest tension forces (If I can remember back 14 years to statics.) So you're putting a hole where structural forces are high with out know how the building was designed to carry the load.

2) You're asking a pipe to hold the load in shear on its side. So your using the thinnest and weakest part of the pipe to hold the load. There will also be a bending moment on that pipe and I'm assuming ATR also? ATR is designed to hold a load axially in the vertical through tension not horizontally in bending.

I agree with David Pitts that several Kwik bolts would be better for this application. I'd avoid putting holes the the concrete purlins If you can. If you have to use the tee get the buildings structural engineer signing off on any proposed drilling.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT