Clearance Req'd Between Steel & Sprinkler Pipe?

2/22/2024

8 Comments

 
Is there a minimum clearance requirement in NFPA 13 between structural steel and steel sprinkler pipe?

Area is not subject to earthquakes and the structural engineer want to strap the pipe directly to the steel like CPVC is strapped to wood.

I've always been of the understanding that steel pipe must be hung, strapped to Unistrut attached to the structure, or supported on a trapeze, but I can't find where in 13 (if it exists) that says I can't use a strap.

​Obviously the fittings/couplings will prevent the pipe itself from contacting the steel. Trying to get the pipes as tight as possible to the sloped structural members and even using 1-5/8" unistrut with pipe clamps is getting pushback.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
2/22/2024 07:41:37 am

No required clearance as far as I know between steel and sprinkler pipe.

Don't drill through steel without talking to a structural engineer.

There are required clearances between sprinkler deflectors and steel. Those depend on construction type and sprinkler head.

Could be entirely wrong, I did not look into this.

Reply
Dan Wilder
2/22/2024 08:02:22 am

If there are no seismic considerations, technically no.

Not sure I have heard of an approved hanger (strap) for this application...I've used "Mutt & Jeff", "U", and wrap around "U" hangers for wood applications (Tolco 120, 120MJ, 120W) along with the more standard "U-Bolt" hanger (Tolco B3188) with top beam clamps to attach to I-Beams.

Reply
James Art, FPE
2/28/2024 11:53:59 am

Mutt and Jeff means a couple of things:
For U hooks, it can be where the lengths of the 'arms' are different,
such as hanging from wood on a slope.
But for tieing togther a pipe like around a Vic Groovelock,
or equivalent,
It can mean two all thread rods tieing to two "riser clamps", one long rod and one short rod to only one of the clamps each, so the clamps bind.
Does anyone have a good picture of this?
THANKS!

Jim

Reply
Glenn Berger
2/22/2024 08:13:12 am

Clearances between sprinklers and obstructions are covered in NFPA 13. Clearances between piping and structural members are not specifically stated.

Reply
Anthony
2/22/2024 08:15:20 am

there is no requirement. I've designed systems that require the pipe to be "strapped" to the bottom of beams for spacing concerns.

I'd also add you can core through the center of an I beam and rest the pipe there as a hanging point. note you'll need structural approval.

Reply
Michael
2/26/2024 11:12:41 am

In this case I would recommend some type of neoprene pad or similar between the pipe and steel.

Reply
Dave
2/22/2024 11:32:48 am

Clearance requirements are partly based on whether or not the piping will move independently from the structure. For horizontal piping, NFPA 13 requires 2 inches clearance from structural members which are "not penetrated or used, collectively or independently, to support the piping"
(18.4.9 in the 2019 Edition)

Reply
RYAN HINSON
2/22/2024 01:01:39 pm

It should be noted that NFPA 13 (2019) Section 18.4.9 only applies where seismic protection is required. The original post indicates that this is not the case.

I would note that common sense should direct one to provide sufficient clear space all around piping for pipe wrench- or coupling dis/assembly.

If strapped directly to beams, minimum bolting component sizing must be met or the assembly "...has been tested and listed by a testing laboratory and installed within the limits of pipe sizes expressed in individual listings" per Section 17.2.

Additionally, spacing between such supports must still adhere to Section 17.4.2.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top April '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    NFPA 415
    NFPA 45
    NFPA 495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT