MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Floor vs. Intermediate-Level for Standpipes

9/24/2025

 
By Joe Meyer, PE | Fire Protection Engineer / Founder of MeyerFire 

One of the traditionally-tricky nuances of standpipe design was when we had standpipes within exit stairs - does the standpipe hose connection go on the floor-level stair landing, or the intermediate-level stair landing?

Since the IBC was first developed, there have been mixed results, depending on the year, as to whether the IBC and NFPA 14 suggested the same location.

​Today I'm updating a previous dive on the topic with the latest NFPA 14 and IBC alignment taken into account.

STANDPIPE READS
If you haven't read already, here are a few good reads on standpipes we have:

   An Introduction to Standpipes
   Addressing Egress & Clearances for Standpipe Hose Connections
​
   Standpipes: Floor vs. Intermediate-Level Landings (← The key read for this topic)

CHEATSHEET
​Here is a printable cheatsheet for standpipe hose connections and stairway landing locations - correlating the different editions of the IBC (2000-2024) and NFPA 14 (1996-2024).

If you find these helpful, you have to join MeyerFire University. This is just one of over a hundred printable PDF resources we have on the site alongside our online courses and virtual simulations. You get access to all of them within 2 minutes of signing up:
Picture
What's notable for the 2024 IBC and 2024 NFPA 14, is that they now correlate well.

LATEST CHANGES
For a period of time, the default location for standpipe hose connections different between the two (Intermediate-Floor Level for IBC 2012 and 2015, and Main Floor Landing for NFPA 14 2010 and 2013).

That's no longer the case in both the IBC and NFPA 14 now defaulting to the Main Floor Landing unless approved otherwise by the AHJ. That part hasn't changed.

What has been clarified is that standpipe hose connections are required for all required interior and exterior exit stairs. The IBC and NFPA 14 didn't explicitly include exterior exit stairways, though it would have been reasonable to include standpipe hose connections for required exterior exit stairs because of the verbiage in NFPA 14 of "Exit Stairways" in Sections 7.3.2 and 7.3.2.1 of the 2010-2019 editions. 

Today, in the latest available editions at the time of this writing, IBC 905.4 and NFPA 14-2024 Section 9.5.2.1 directs us to standpipe hose connections in "required interior and exterior exit stairs," which clarifies and puts the matter to rest.

WANT MORE?
If you enjoyed this topic, don't forget to check out the greater breakout article in Standpipes: Floor vs. Intermediate-Level Landings. And if you enjoy the resources, consider joining MeyerFire University. It's exploding in learner growth (amount of NICET and ICC continuing education credit hours), in the amount of organizations (now over 550 companies and organizations), and in new content (42 new courses added since 2023). Great time to join.

Thanks for reading and being part of our community! Have a great rest of your week.

- Joe

Introduction to Grooved Pipe & Fittings

5/24/2022

 
We previously have introduced different types and combinations of threaded fittings - which have been around for more than a century.

Here we're introducing another common way to join pipe; using grooved fittings. 
Picture
An attic sprinkler system using a grooved elbow with couplings. 
Use of "mechanical" couplings that could allow faster joining of pipe came to life in 1919 by Lieutenant Ernest Tribe. Just a few years later the Victory Pipe Joint Company renamed itself to Victaulic (a combination of "victory" and "hydraulic"), and grew to expand the technology worldwide. 

Today, Victaulic and other manufacturing leaders provide grooved fittings that are often used for pipes in fire sprinkler systems. It is not uncommon for both mains and branch lines to be grooved today.

What are common grooved fittings, and how do they work? Let's introduce them. 
Picture
An in-rack sprinkler with a branch line using (starting with the sprinkler) a groove x thread reducing elbow
​with a grooved coupling, a grooved piece of pipe, and a grooved tee (connection not shown).
PIPE
Let's start with the pipe. In order to give grooved fittings an opportunity to "grip" the pipe and remain in place, they need an opportunity to resist the pressure of the water that is trying to "pull away" the pipe from the fittings which join them together.
Picture
A grooved coupling about to connect two grooved-end pipes. Note the loose nut and bolt on the right-hand side, allowing the coupling to be expanded and "slip" over the pipe on the left.
In order to create a groove in the pipe, steel can either be "roll groove" or "cut groove". Roll groove pipe involves pressing an indentation into the pipe near the end of the pipe. This allows a grooved fitting to slip over the end of the pipe and fit into the groove. Roll groove pipe has the advantage of not reducing the pipe thickness, so it can have more tolerance for corrosion than thinner pipe, similar pipe with threads, or pipe with cut grooves.

Pipe which is cut groove involves cutting into the pipe rather than pressing it. This cutting removes a portion of the pipe wall, making a thinner but smooth interior pipe wall. This thinner wall makes it more susceptible to corrosion, however, for pipe systems with a minor slope, the smooth inside of the pipe does not create a ridge where water can sit and corrode the pipe.
Picture
Roll Grooved Pipe (top) and Cut Grooved Pipe (bottom). Note the ridge on the inside of the pipe wall for roll groove pipe, and the thinner pipe wall along the cut groove pipe.
Picture
A tape measure with a "go" or "no-go" measurement to determine if the groove is within manufacturer tolerances.
ELBOWS & TEES
Let's start with the basics. Elbows allow bends of 90-degrees (most common), 45-degrees, 22-1/2 degrees, and 11-1/4 degrees.

Why not every possible angle? What if I need to have a 60-degree bend because of my building?

First, it wouldn't be economical to make a fitting of every bend. Second, is that using just two 90-degree elbows back-to-back we're able to create a "swing joint" and make any angle we could want, just by changing the elevation of the pipe that's being joined.
Picture
Picture
Picture
Victaulic "FireLock" Grooved Fittings; 
90-Degree Elbow #001 (left), 45-Degree Elbow #003 (center), and Standard Tee #002 (right)
One notable specialty with the grooved elbow is a "Drain Elbow", which has the elbow except it includes a drain outlet at the bend of the elbow. This is used all the time with fire department connections which come down a wall and need to be capable of being drained (to avoid having water-charged pipe freeze and burst). This is also called a "Drain-El" or is a Victaulic #10-DR.
Fire Department Connection
A wall-mounted fire department connection that is away from the riser, here showing the "Drain Elbow" with a ball drip below. The portion upstream of the check valve is intended to be dry unless the FDC is actively being used in order to avoid freezing water inside.
COUPLINGS
Nice sketches, Joe, but that's not how things look in the field!

That's because unlike threaded fittings, the actual pipe joining is by a grooved coupling. The coupling has malleable iron bumps that grip the indent of one groove (pipe/fitting) and connect it to the second groove (the other pipe/fitting). 
Picture
A grooved coupling (here a Victaulic #009N shown).
OTHER FITTINGS
There are a host of other fitting types. Grooved Reducing Tees? Yep. Less common. Less common can equate to more expensive, or at least that's what I hear from contractors familiar with all the pricing nuances.

What other grooved fittings do I often see? 

Reducing fittings, which is a concentric, single-cast piece of metal that has a large groove on one end and tapers down to a smaller groove on another end. One note of caution is using these in the vertical orientation; I've heard it is much better, more stable, and stronger to use a reducing-fitting as opposed to a reducing-coupling when in a vertical orientation. One of my clients goes so far to say to not use reducing couplings at all (where the coupling itself has two different groove sizes). I wouldn't have the expertise to gauge that myself.
Picture
Picture
A flange x groove reducer (left) and a grooved cap (right).
There are also reducing adapters, than can accept a flange connection and convert it to a reduced groove connection. 

Crosses are also available, as are caps (like the Victaulic #006 shown above on the right) which can terminate the end of a branch line. These caps even have 1-inch threaded opening options for easy auxiliary drains. 
Picture
Many manufacturers have equipment and components with grooved ends that can readily attach to pipe and fittings.

If you're looking to explore the extend of all available grooved fittings, I'd invite you to check out manufacturer's catalogs or do a simple google search for grooved sprinkler pipe fittings. The manufacturer's product data can do a whole lot of good in clarifying what's been created and listed for use in sprinkler systems.

Have tips, tricks, or things to consider about grooved fittings? Comment below.

​That's all for this week - hope you have a great rest of yours.

Requirements for Drains in Fire Sprinkler Systems

6/10/2021

 
Drainage from a fire sprinkler system can often be overlooked as it does not directly fight the fire. However, those involved in inspections & testing of sprinkler systems know all too much about how poor drain design for a sprinkler system can negatively impact how tests are conducted, how long it takes a system to drain, and what messes building owners have to deal with.

​Here are various components for drains on a sprinkler system, and some of the common requirements that pair with them.
Fire Sprinkler Drain
For best viewing of the table below, click here: requirements-for-drains-in-fire-sprinkler-systems.html
Component
Notes / Description
Purpose
​Properly sized and arranged drains help minimize the amount of time a system is out of service. For pre-action and dry systems, drains also help minimize the amount of time water is prone to freezing temperatures. Some drains also help verify the water supply. 
[NFPA 13 2002 §8.15.2, 2007-16 §8.16.2, 2019 16.10]
Approval / Listing
Approval / Listing: Drains are not required to be listed but must be approved. 
[NFPA 13 2002 §6.1.1, 2007-10 6.7.3, 2013-16 §6.1.1.5, 6.6.3, 2019 §7.1.1.5, 16.9.1.1]
Discharge Location
Drains must discharge to the outside or to drain capable of handling drain flow.
[NFPA 13 2002 §8.15.2.4.4, 2007-16 §8.16.2.4.4, 2019 §16.10.4.4]

Drains cannot discharge in blind spaces under a building.
[NFPA 13 2002 §8.15.2.6.4, 2007-16 §8.16.2.6.4, 2019 §16.10.6.4]

Cannot direct connect to sewer and must conform to health/water dept. regulations.
[NFPA 13 2002 §8.15.2.6, 2007-16 §8.16.2.6, 2019 §16.10.6]
Floor Drain Capacities
The following are approximate plumbing floor drain intake capacities, according to Standard Detail P-33 from Plumbing Engineer. In many cases, floor drains are not acceptable to handle flow from main drains, PRV discharge, or inspector's tests.
2” Floor Drain = 7 gpm             5” Floor Drain = 78 gpm
3” Floor Drain = 10 gpm           6” Floor Drain = 126 gpm
4” Floor Drain = 43 gpm          8” Floor Drain = 272 gpm
Signage
Clear permanent signage of weatherproof metal or rigid plastic is required to identify a drain valve, secured with corrosion-resistant chain or wire or other approved means. [NFPA 13 2002-13 §6.7.4.1, 2016 §6.6.4.1, 2019 §16.9.12.1]
​
​
For dry or pre-action systems with auxiliary or low-point drains, signage is required at the riser indicating quantity and location of each individual drain.
[NFPA 13 2007-16 §8.16.2.5.3.7, 2019 §16.10.5.3.7]
Size of Main Drain
Serving risers and mains, size according to riser/main size.
[NFPA 13 2002 Table 8.15.2.4.2, 2007-16 Table 8.16.2.4.2, 2019 Table 16.10.4.2]
Riser Size                        Drain Size
1” to 2”                       ¾” or Larger
2-1/2” to 3”                 1-1/4” or Larger
4” or More                      2” or Larger
​
Serving pressure-reducing valves, sized to allow flow of greatest demand of PRV.
[NFPA 13 2002 §8.15.2.4.5, 2007-16 §8.16.2.4.5, 2019 §16.10.4.5]
Size of Drain Riser
​Drain risers acting as a common riser for multiple floor control valves must be piped one-size larger than any drain connection typing into it.
[NFPA 13 2002 §8.15.2.4.7, 2007-13 §8.16.2.4.7, 2016 §8.16.2.4.8, 2019 §16.10.4.8]
​Where Required
  • Antifreeze Pendents: Water must be drained from entire system after hydrostatic test if completed with water.
    [NFPA 13 2007-16 §7.6.1.3, 2019 §8.6.1.3]
  • Antifreeze Riser/Backflow: Must be capable of draining antifreeze system.
    [NFPA 13 2002 §7.5, 2007-16 §7.6,  2019 §8.6]
  • Antifreeze Remote Point: At the most remote portion of the system (with test).
    [NFPA 13 2007 §7.6.3.5, 2010-16 §7.6.3.6, 2019 §8.6.3.6]
  • Exposure Protection System Riser: Except for top-fed, open systems.  
    [NFPA 13 2002 §7.7.4.1, 2007-13 §7.8.4.1, 2016 §7.7.4.1, 2019 §8.7.4.1]
  • Fire Department Connection: Pipe between check valve and outside connection in areas subject to freezing must have an automatic drain valve, that is approved and in an area that permits inspection & testing. Where trapped, auxiliary drain is required.
    [NFPA 13 2002 §8.16.2.6, 2007-16 §8.17.2.6, 2019 §16.12.7]
  • Floor Control Assemblies: At floor control valve assembly for buildings over two stories in height, except on top-level if sprinklers are fed from level below.
    [NFPA 13 2013 §8.16.1.5.1, 2016 §8.2.4.1, 2019 §16.9.11.1]
  • System Valve (Main Drain): Each system must be capable of being drained.
    [NFPA 13 2002 §8.15.2.1, 2007-16 §8.16.2.1, 2019 §16.10.1]
  • Trapped Pipe (Wet or Non-Freezing Pre-Action): Where trapped section of pipe:
    - contains less than 5 gallons, auxiliary drain, single pendent sprinklers capable of draining section, or flexible coupling must be provided,
    - contains 5 gallons or more, minimum ¾” auxiliary drain must be provided
    - contains 50 gallons or more, minimum 1” auxiliary drain must be provided.
    [NFPA 13 2002 §8.15.2.5.2, 2007-16 §8.16.2.5.2,  2019 §16.10.5.2]
  • Trapped Pipe (Dry or Pre-Action): Where system is trapped:
    - containing less than 5 gallons, min. ½” auxiliary drain valve with plug or nipple/cap
    - tie-in drains required for multiple adjacent trapped branch pipes.
    ​[NFPA 13 2002 §8.15.2.5.3, 2007-16 §8.16.2.5.3, 2019 §16.10.5.3]

A Practical (Read-World) Design-Spec Checklist

1/22/2020

 
Design-specifications have had a tradition and sometimes contemptuous past in the world of fire protection design.
Sometimes called “design-build spec”, “performance-specification”, “delegated design”, “deferred submittal documents”, “scope drawings”, or “design-spec”, these all mean relatively the same thing; the engineer is not providing a working submittal of how a fire suppression system should end up in the field.

Back in 2008 advocacy groups from the Society of Fire Protection Engineers (SFPE), National Society of Professional Engineers (NSPE), and National Institute for Certification of Engineering Technologies (NICET) adopted a joint position on the role of the Engineer and the Engineering Technician as they relate to fire protection systems. A summary and full-length document are here.

The position statement does a good job of identifying the relationship between engineering documents and a working shop drawing submittal. It maintains that the role of the Engineer is to support the proper protection of the public’s health and safety. A licensed Engineer is required to understand a broad sense of fire protection beyond just suppression, and also has specific state requirements for licensing and authorization.

While the position statement does a good job of identifying roles and defining the relationship between an engineer and a technician, real-world experience says that many “design-build specifications” fall short on good practice.

I’ll save my frustrations on the lack of quality engineering documents for another day (it is not a regional issue). There is a ton to explore on that topic.

I will however offer up what I like to use as a practical checklist for design-build specifications. Not all owners want to pay consultants to flush out all the details of a system. I get it. But if an owner is paying for anything at all, then the documents should address basic requirements and cost-impacting elements of design.
Picture
GET THE PDF CHECKLIST
If a set of plans just outlines an area and says “per NFPA 13”, then someone isn’t doing it right.

This cheatsheet is a collection of the items I’m looking for when I help contractors bid jobs. It’s a shortcut to all of the items that have a design and cost-impact to a job.

If you, as a consulting engineer, address every single one of these items clearly and within code, then pat yourself on the back my friend, you are a gift.

If your documents don’t address each of these items (yes, including flow test information), consider making it a part of your regular practice. None of the items on this list are major time consumers, but by accounting for them you’ll allow better bidding from contractors and much less contention after bids are due.

Please, please: don’t loft up vague project requirements to contractors and hope for the best. Invest in being a knowledgeable and quality practitioner of this great industry. It'll more than pay itself back to you. 

What are your thoughts? What type of bid documents are you used to seeing? Join the conversation and comment here.

The Top 10 MeyerFire Articles & Tools of 2019

12/26/2019

 
This time of year is just the best. 

I feel extremely fortunate to have three young kiddos at home, a supportive and all-around great family, and an extremely rewarding career in fire protection and doing what I do here at MeyerFire.com. Whether you subscribe, dabble occasionally on the forum, or just stop in to use tools here and there, THANK YOU for a really wonderful 2019.

One of the tasks of wrapping up a year is revisiting what resonated the most in 2019 of all the content here. If you just joined in this year or know someone who would benefit from this content, please consider sending a link.
​
Picture
#10 | Trouble Orienting the 2019 Edition of NFPA 13?
NFPA 13's 2019 Edition brought in huge changes - this tool helps translate sections between the 2016 and 2019 edition.
Picture
#9 | An Introduction to Standpipes
This article lays an overview of common challenges and requirements associated with standpipes for fire protection.
Picture
#8 | Calculate the Quick-Response Area Reduction
This calculator quickly adjusts remote area size based on the use of quick-response sprinklers in low-ceiling areas. 
Picture
#7 | Fire Sprinklers and Overhead Doors: A Love Story
Disclaimer: this is not a love story - rather an overview of requirements and misconceptions associated with protecting above and below overhead doors.
Picture
#6 | A Fire Department Connection Cheatsheet
Need a quick-reference for everything related to FDC (fire department connection) requirements? This PDF guide is made for you.
Picture
#5 | When Are Sprinklers Omitted in Electrical Rooms?
You might get this question a lot if you're in sprinkler design. This article explores when sprinklers are allowed to be omitted in electrical rooms with code references.
Picture
#4 | Is a Post-Indicator Valve Required for My Project?
This article explores code requirements for indicating valves (post and wall) and when they are required for projects.
Picture
#3 | How to Determine Fire Flow (IFC Method)
This Fire Flow Calculator simplifies fire flow requirements using the International Fire Code's Appendix B method.
Picture
#2 | Components of Basic Wet-Pipe Riser Assemblies
This breakout of wet system risers breaks out requirements and components for riser assemblies.
Picture
#1 | Window Sprinklers & Fire Ratings
​This article uncovers popular misconceptions and the actual code paths for use of sprinklers with rated fire barriers.

While we're at it, here are the Top Ten Tools & Articles of 2018 and the Top Ten Tools & Articles of 2017.

Hope you have a relaxing and rewarding holiday week wherever you call home!

New Beta Test for Water Storage Tank Sizer

12/11/2019

 
This week I'm pulling back the curtain a little bit and showing a tool that is very much still under development. It's a water-storage tank sizer that incorporates a handful of decisions that go into water storage tank sizing.

I'd like to get it in front of you this week as I'm looking for feedback on how to improve this tool. There's not a lot of great documentation on how to size water storage tanks, but there are plenty of variables that impact proper water storage tank sizing.

With that said, check out the tool as part of our Toolkit package here:​
[If you don't see the tool below, click here]
SEE THE WATER STORAGE CALCULATOR

If you're in the water storage tank space and have tips or feedback, please email me at [email protected] or comment here. I'd be very much interested in ways to improve this one (or any tool for that matter).

On a side note, this and many other recent tools are going to be included with a major MeyerFire Toolkit update here in the next few weeks. We've been working quite a bit on improving the activation/subscription process which has been no small task. When that gets cleaned up I'll be happy to send out the major update for the Toolkit.

​Hope you have a great rest of your week!

A New Fire Sprinkler Max Drain Flow Calculator

11/6/2019

 
I was asked recently for a specific project how much flow the owner should anticipate coming from a building's main drain. 

There are just a few factors that play into exactly how much water to expect. Is the drain serving as the main drain for a system? Is it only serving an inspector's test? Is the drain off a 1-inch pipe or 2-inch pipe? How much pressure is on the system?

These are relatively easy to answer if you're familiar with the job, but each answer plays a role in determining how much water will come out of an open orifice.

This week, I simplified a few of these parameters to create a quick inspector's test and drain calculator for fire sprinkler systems.

This tool estimates the maximum amount of flow that could come from an inspector's test or main drain. It does not represent the actual amount of flow from a main drain or inspector's test. Read more about this challenge here.

With it, you can estimate the amount of flow that will come from an inspector's test (use the k-factor option) or from a drain (diameter option), for the purposes of figuring out drain solutions from these outlets.

​For our international audience I have incorporated real units from the get-go this time. It's a free tool that's now live on the site, here.

Give it a spin and let me know what you think in the comments here. 
​
READ "THE TROUBLE WITH ESTIMATING MAIN DRAIN FLOW"

Know others that might find this helpful? Send them a link or tell them to subscribe here. 

Thanks & have a great week!

A Fire Department Connection Cheatsheet

8/21/2019

 
There’s no real way around it: I love cheatsheets.

In a design course in college we received 5x7 index cards to include any handwritten notes we wanted for an upcoming final. I wrote so much on that card with handwriting that was effectively size-4 font that it could have been displayed as a work of art. 

Nearly an entire semester summarized to a 5x7 card. It was a thing of beauty. 

While I no longer have a need to write so small, I still enjoy having information organized so that it is extremely easy to access. 

If you haven’t seen these before, here are a couple cheatsheets I’ve created so far:
Summary of Differences of NFPA 13, 13R, and 13D
Sprinklers & Passive Fire Protection Options

Fire Department Connection
GET FDC PDF CHEATSHEET

​Last week I covered important considerations surrounding fire department connections from a design perspective, which was a joint-effort with QRFS covering the topic.

At some point I’ll compile the best blog posts and resources into a hardcover reference book. For this week, however, here’s a cheatsheet on requirements surrounding fire department connections across NFPA 13R, NFPA 13, and NFPA 14:
Value
NFPA 13R
NFPA 13
NFPA 14
Purpose
​To supplement pressure (not based on system demand)
[same as NFPA 13]
To supplement pressure (not based on system demand)
[NFPA 13 2019 A.16.12.4]
To provide primary (manual) or secondary (automatic) supply to standpipes
[NFPA 14 2019 3.3.4.1.2]
When Required
All buildings except:
- single story buildings not exceeding 2,000 sqft (185 m2)
[NFPA 13R 2002 6.6.4.1, 2007 6.7.4.1, 2010-19 6.11.1]​
All buildings except:
- Remote areas inaccessible for fire department support
- large-capacity deluge systems exceeding pump capacity of F.D.
- single story buildings not exceeding 2,000 sqft (185 m2)
[NFPA 13 2002 8.16.2.2, 2007-16 8.17.2.2, 2019 16.12.2]
​Always required.
[NFPA 14 2000 2.8, 2003-19 4.8]
Caps
No requirement.
Approved plugs or caps, secured, with easy removal by fire department.
 [NFPA 13 2002 6.8.4, 2007-13 6.8.2, 2016 6.7.2, 2019 16.12.3.2]
Approved plugs or caps, secured, with easy removal by fire department.
[NFPA 14 2000 2-8.2, 2003 4.8.2.1, 2007-13 4.7.3, 2016 4.8.3, 2019 4.8.3]
Check Valve
​In accessible location with automatic drain valve where subject to freezing.
[NFPA 13R 2007 6.7.4.4, 2010-19 6.11.4]
In accessible location with automatic drain valve where subject to freezing.
[NFPA 13 2002 8.16.2.5 & .6, 2007-16 8.17.2.5 & .6, 2019 16.12.6 & .7]
Installed as close as possible to fire department connection inlets.
[NFPA 14 2000 4-3.2, 2003 6.3.2, 2007-13 6.4.2, 2016-19 6.4.2.1]
In accessible location with automatic drain valve where subject to freezing.
[NFPA 14 2000 4-3.4, 2003 6.3.4, 2007-2019 6.4.4]
Clearance
No specific guidance.
Such that “hose lines can be readily and conveniently attached without interference from nearby objects, including buildings, fences, posts, or other FDCs”
[NFPA 13 2002 8.16.2.4.6, 2007-16 8.17.2.1, 2019 16.12.1]
Such that “hose lines can be readily and conveniently attached without interference from nearby objects, including buildings, fences, posts, or other FDCs”
[NFPA 14 2000 4-3.5.1, 2003 6.3.5.1, 2007-19 6.4.5.1.1]
Distance to Nearest Hydrant
No specific guidance.​
​No requirement.
Not more than 100 feet (30.5 m) from nearest fire hydrant, unless approved otherwise
[NFPA 14 2019 6.4.5.4, 6.4.5.4.1]
Height of FDC
No specific guidance.
1.5 – 4 ft above grade
(500 mm – 1.2 m)
[NFPA 13 2002 A.8.16.2, 2007-16 A.8.17.2, 2019 A.16.12]
1.5 – 4 ft above grade
(457 mm – 1219 mm)
[NFPA 14 2000 4-3.6, 2003 6.3.6, 2007-19 6.4.6]
Location of FDC
​No specific guidance.
At nearest point of fire department apparatus accessibility, or at a location approved by the AHJ.
[NFPA 13 2002 8.16.2.4.6, 2007-16 8.17.2.4.6, 2019 16.12.5.7]
Located within 50 ft (15.2 m) of street or nearest fire department access.
[NFPA 14 2019 7.12.2.3]
Visible and recognizable from street or nearest fire department access, or on street side of buildings.
[NFPA 14 2000 4-3.5.1, 2003 6.3.5.1, 2007-19 6.4.5.1]
Number of FDCs
At least one.
[NFPA 13R 2002 6.6.4.1, 2007 6.7.4.1, 2010-19 6.11.1]
​At least one.
[NFPA 13 2002-13 6.8.1, 2016 6.7.1, 2019 16.12.3.1]
One for each zone of Class I or III standpipes, unless fire department cannot supply high-zone.
[NFPA 14 2000 5-12.1, 2003 7.13.1, 2007-19 7.12.2.1]
Two (physically separated) for each zone, for high-rise buildings or multiple attached buildings exceeding 900 ft perimeter distance.
[NFPA 14 2000 5-12.2, 2003 7.13.2, 2007-16 7.12.2, 2019 7.12.2.2]
Size of FDC
At least 1-1/2” (38 mm)
[NFPA 13R 2002 6.6.4.2, 2007 6.7.4.2, 2010-19 6.11.2]
Riser 3” or smaller: Single 2.5” outlet
Riser larger than 3”: Two 2.5” outlets
[NFPA 13 2007-13 6.8.1.3, 2016 6.7.1.3, 2019 16.12.3.1.3]
One 2-1/2” (65 mm) inlet for every 250 gpm (946 L/min) standpipe demand, or approved large-diameter connection
[NFPA 14 2007-19 7.12.3]
Size of Feed to FDC
Pipe with diameter at least as large as the riser.
[NFPA 13R 2010-19 A.6.11]
Fire Engine, Pipe Schedule: 4-inch (100 mm)
Fire Engine, Hydraulically-Calculated: Size of largest riser
Fire Boat: 6-inch
[NFPA 13 2002 8.16.2.3, 2007-16 8.17.2.3, 2019 16.12.4]
Must be determined by hydraulically calculated.
[NFPA 14 2007-19 8.2.1]
Type of FDC
No specific guidance.
(2) 2-1/2” threaded unless fire department does not conform to NFPA 1963. Must be approved regardless.
[NFPA 13 2002 6.8.2 & 6.8.5, 2007-13 6.8.1.1 & 6.8.3, 2016 6.7.1.1 & 6.7.3, 2019 16.12.3.1.1, 16.12.3.3]
(2) 2-1/2” threaded unless fire department does not conform to NFPA 1963. Must be approved regardless.
[NFPA 14 2000 2-7, 2003-16 4.8.2 & 4.8.2.2, 2019 4.8.2, 4.8.4]
Where attached to system?
​See NFPA 13R.
[NFPA 13R 2002 6.6.4, 2007 6.7.4, 2010-19 6.11]
See NFPA 13;
not on suction side of fire pump.
[NFPA 13 2002 8.16.2.4, 2007-16 8.17.2.4, 2019 16.12.5]
​See NFPA 14;
not on suction side of fire pump.
[NFPA 14 2000 4-3.3, 2003 6.3.3, 2007-19 6.4.3]
Find this helpful? Consider subscribing to free resources like this here.

Have a great week!

An Engineer's Perspective on FDCs (Part I)

8/14/2019

 
​Why are fire department connections (FDCs) so important to a suppression system?

They are the link between initial response and supplemental help.

Despite appearances, sprinkler systems are not intended to discharge forever. Their goal is to suppress long-enough that firefighters can take over and finish the job.

Standpipe systems exist to extend the reach of the fire department in tall, wide or complex buildings. Manual standpipes depend upon pressure and flow from the fire department. What single piece of equipment is relied upon to make the transfer? The FDC.

This week's article is an overview of fire department connections from an engineer’s perspective. It is one part of a two-part series covering fire department connections. Read more from a supplier’s perspective at Quick Response Fire Supply here.

Authority Intervention Needed
Fire department connections are a unique piece of a suppression system in that they’re not just governed by the designer and code. NFPA 13 and 14 require that fire department connection type and location is coordinated with the Authority Having Jurisdiction.

Early in design, prior to bid, I’ll call the local fire marshal and coordinate each of the following big-picture elements:

Coordination Item 1: Type of Fire Department Connection
The most popular types of FDCs? Siamese (2 x 2-1/2" threaded connection) and Storz (4" or 5" with or without 30-degree elbow).

In my very unscientific study of jurisdictions I call (nearly half are local to my area), I've found the following; 73% use Siamese-type 2-1/2” fire department connections, 11% use 4” Storz connections, and the remaining 16% use 5” Storz connections.

Of these, 13% have special requirements such as Knox Locking caps, 30-degree elbows, or irregular threading.

There’s no right or wrong answer here – I just want to be sure what I’m calling for or showing on plans match what the jurisdiction uses.
Fire Department Connection
Large diameter Storz-type fire department connections have become more common for their ability
​to quick-connect a single hose and flow large amounts of water.
 
Coordination Item 2: Location of Fire Department Connection
The most obvious coordination during design is the location of the fire department connection.
 
My design preference, driven by installation effort and cost, is typically in the following order:
 
1. Wall-mounted FDC, adjacent to the sprinkler riser
2. Wall-mounted FDC, remote from the riser (such as the front of the building)
3. Freestanding FDC, downstream of a site backflow pit or hotbox
4. Freestanding FDC, connected underground into the sprinkler riser room
 
The first couple options are not always workable and depend on the building.
 
Sometimes the water supply and riser room are in the back of a building inaccessible to the fire department. This would be a bad place for an FDC.
 
Sometimes the front face of a building is "grand view" with large glazed curtain walls and no room to mount a fire department connection. This comes up with large offices or modern schools.
 
Sometimes a building-mounted FDC doesn’t make sense with major hazards; why risk firefighter safety in these cases? High-rises, for instance, require multiple FDCs due to the potential for falling glass that could injure firefighters or sever hoses. If there's potential for wall-collapse (think high-hazard warehouse wall) then a wall-mounted FDC also may not make sense. Freestanding FDCs can make a lot of sense for projects like these.
 
Considering most of my work is two stories or less and light commercial, it may not be surprising that roughly 85% of projects include building-mounted FDCs. The remaining 15% have necessitated freestanding FDCs.
 
Freestanding Fire Department Connection
Some jurisdictions require freestanding fire department connections, but it typically
​depends on the type of building and hazard presented.
 
Coordination Item 3: Distance of FDC to Nearest Hydrant
As a designer it would be great if I could operate in the dark. Send me all the information I need to do a design, I do it, and everyone’s happy.
 
If it were that simple, though, we’d probably already have machines design and do it without downing two bags of Doritos and a half hour of facebook each day.
 
Back to the topic: FDC-to-hydrant distance has an impact on the tactical approach in firefighting.
 
Many designers & installers in our field are current or former firefighters. They could readily speak to this. I’m not one of them, but I can imagine that having to shut down a major roadway or cross a parking lot with hundreds of feet of hose quickly during an emergency is not exactly the easiest thing to accomplish.
 
As a result I like to ask AHJs what distance the FDC should be to the nearest hydrant.
 
Of my highly unscientific and locally-biases results, 41% of jurisdictions require a hydrant to be within 100 feet of the FDC or less, 47% require a hydrant to be within 150 feet, and only 16% of jurisdictions require a hydrant within 200 feet or more of the FDC.
 
These three elements are a part of my code calls. Next week I'll distribute my FDC Cheatsheet that outlines requirements for FDCs across NFPA 13, 13R and NFPA 14. If you haven't already subscribed, consider doing so here.
 
What do you look to coordinate with the AHJ? Discuss your experience here.

​Want more coverage on fire department connections? See the other half of our two-part series on fire department connections here: Quick Response Fire Supply.

Post-Indicator Valve: Required for My Project?

7/24/2019

 
One project question I very commonly receive from civil engineers is whether a post-indicator valve (PIV) is required.

In short, there are options. I'm exploring PIVs in more detail in this week's article. If you want to get more like this, subscribe for free here.

Purpose of Post-Indicator Valves
Post-indicator valves have long been used to stop the flow of water into a building during developed stages of a fire. Exterior wall collapse of a burning building poses a threat to break water supply mains as well as create many openings to the water supply. Without a valve to stop supply to these areas, firefighters and their efforts could be compromised by the loss of pressure and outflow of water to areas of a site that don't need water.

With the recognized effectiveness of sprinkler systems and cost pressures, the requirement for post-indicating valves have become more relaxed in the last decade. Code references to account for building collapse, for instance, now appear only indirectly in location requirements for hydrants and post-indicator valves to be sufficiently away from a building.

Components of Post-Indicator Valves
The post-indicator valve has several important features - first is the ability to quickly shut the valve with use of the post indicator valve handle. The second is to quickly see whether the system is in the 'open' or 'shut' condition in a protected enclosure. It can sometimes be difficult to see after years of dirt on the glass, but not impossible.

The valve itself is along the water main below frost depth such that only the stem is subject to freezing conditions. It's a simple concept that's carefully crafted to protect the valve and stem in a reliable fashion.


Post Indicating Valve
One example of a post-indicating valve - a Mueller Company Vertical Adjustable Post Indicator Valve (see https://www.muellercompany.com/fire-protection/ulfm-indicator-posts/)

History of the PIV Requirement
So is a post-indicator valve required or not? This used to be an easier question to answer.

While not a referenced standard from the International Building Code, the International Fire Code requires that all private fire service mains be installed in accordance with NFPA 24 (IFC 2000-06 Section 508.2.1, 2009-18 507.2.1). NFPA 24, the Standard for the Installation of Private Fire Service Mains and Their Appurtenances, governs system requirements between a water supply main and a building's service entry. 

Up until the 2010 Edition, NFPA 24 required a listed post indicator valve on every connection from a private fire service main to a building unless special criteria were met (NFPA 24 Section 6.3). The special criteria included the use of a non-indicating underground gate valve with a roadway box and T-wrench or locating an inciating valve in a pit. Either special case required approval of the AHJ.

Current Valve Options within NFPA 24
Since the 2010 Edition, NFPA 24 gives a series of options for isolating a building's system and does not mandate that a post-indicator valve be used. These options (from 2010-13 6.2.11, 2016-19 6.2.9) include:
  • A post-indicator valve at least 40 feet (12 m) from the building.*
  • A wall post-indicating valve
  • An indicating valve in a pit
  • A backflow preventer with an indicating valve at least 40 ft (12 m) from the building.*
  • A non-indicating valve, such as an underground gate valve in an approved roadway box with T-wrench at least 40 ft (12 m) from the building*
  • Control valve in a fire-rated room accessible from the exterior
  • Control valve in a fire-rated stair enclosure accessible from the exterior as permitted by the AHJ.
*Where the building is less than 40 feet tall, the valve can be less than 40 feet from the building but not closer than the height of the wall.

wall post indicating valve
While still considered an "indicating" type valve, wall indicating valves are generally less preferred than post-indicating valves as they are more susceptible to a building collapse than post-indicating valves.

​Post-Indicator Requirements of NFPA 14
NFPA 14, the Standard for the Installation of Standpipe and Hose Systems, also weighs in on post-indicator valve requirements. 

NFPA 14 requires that each water supply (except for an FDC) shall be provided with a listed indicating valve in an approved location (NFPA 14 2000 4-2.6.1, 2003-07 6.2.6.1, 2010-19 6.3.6.1.1). 

The prescriptive way to accomplish this is through the use of a post-indicating valve. Annex material within NFPA 14 goes further, stating a list of preferences for outside control valves:
  1. listed indicating valve at each connection into the building at least 40 feet (12.2 m) from the building where space permits.
  2. Control valves in a cutoff stair tower or valve room accessible from the outside.
  3. Valves located in risers with indicating posts arranged for outside operation.
  4. Key-operated valves in each connection into the building.

NFPA 14 does give exceptions (as is almost always the case in fire protection), but they require AHJ-approval. Wall-point-indicating valves, or underground valve with roadway box and T-wrench, are alternative options that require AHJ approval (NFPA 14 2000 4-2.6, 2003-07 6.2.6, 2010-19 6.3.6).

Post-Indicator Requirements of NFPA 13
So where does NPFA 13 stand on post-indicator valves? In short, it doesn't. NFPA 13 only states that where post-indicator valves are used, the top of the post must be 32-40 inches above grade, and they must be protected against mechanical damage (NFPA 13 2002 8.15.1.3, 2007-16 8.16.1.3, 2019 16.9.9).

AHJ & Insurer Inputs
Authorities Having Jurisdiction may also want to weigh in on requirements for post-indicating valves. Some municipalities write code amendments to require PIVs, while others may request PIVs be installed for certain building types.

Insurers, such as FM Global, may also want input. FM Global for instance, recommends that each system has a control valve a minimum of 40 feet from the building (with less preferred options also recommended in Data Sheet 2-0 2.6.2).

Best Practice
What's the best course of action for your project? First, check for local or state code amendments that may affect post-indicating valves. If you have a standpipe system within the building, plan to provide a PIV. Last, check with your AHJ for any nuanced requirements you may be missing or to coordinate a location with the AHJ.


Want More?
Not already getting these free weekly articles? Subscribe here. Found this helpful? Share on LinkedIn.com or send to a friend. MeyerFire is all about helping you do great work in fire protection with tools, tips and resources.
<<Previous
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT