Get Quick System Volumes: Free Calculator

2/28/2018

 
Last week I explored when volumes of a system or portion of a system become important. Principally, volume in fire sprinkler or standpipe systems becomes important in overall capacity limitations of dry and pre-action systems and in draining portions of wet, dry, and pre-action systems. See the full article here.

This week I've created a basic quick-and-dirty volume calculator based on the length of pipe in a system (don't see the calculator below? View in your browser here): 
Picture
Download this Tool


​​Simply select the type of pipe used and enter the approximate length of pipe for each pipe size in the system or portion of a system you're evaluating.

I created this when looking at whether I break the 5-gallon volume threshold for portions of wet sprinkler systems, bottom legs of standpipes, or overall dry and pre-action system capacities. Email suggestions or tips for improvement to me at [email protected].

Want to see more like this? Subscribe to these free weekly articles here.

Quick Announcement & A Favor

2/27/2018

 
I'll be posting the weekly article tomorrow but before then I have a question and a favor.

Over the past two years I've been working on a long-awaited resource involving literally hundreds of hours of research and development, but before I wrap up the project I have just one question that will help create a better resource: Learn more and provide input with my quick one-question survey here.

When are fire sprinkler volumes important?

2/19/2018

 
It does not necessarily come up often, but the volume of a fire sprinkler system does carry several requirements.

​Dry and Preaction systems carry water delivery requirements, while all systems carry requirements for drainage. Today I'm summarizing requirements related to when volumes of fire sprinkler systems are important to consider.

Dry System Capacity

Systems under 500 gallons (1900 L):
  • Not required to meet any water delivery time to inspector's test connection (NFPA 13 2002 A.7.2.3.1, 2007-2016 7.2.3.3).

Systems between 500 and 750 gallons (1900 - 2850 L):
  • Not required to meet any water delivery time when a quick-opening device is provided (NFPA 13 2002 A.7.2.3.1, 2007-2016 Section 7.2.3.4).

Systems over 750 gallons (2850 L):
  • Subject to water delivery times (NFPA 13 2002 11.2.3.9, 2007-2016 Table 7.2.3.6.1, below):
Hazard      No. of Remote Sprinklers Initially Open        Max. Time of Water Delivery
Dwelling Units                       1 sprinkler                                                                           15 seconds
Light                                          1 sprinkler                                                                          60 seconds
Ordinary I                                2 sprinklers                                                                        50 seconds
Ordinary II                               2 sprinklers                                                                        50 seconds
Extra I                                       4 sprinklers                                                                        45 seconds
Extra II                                      4 sprinklers                                                                        45 seconds
High Piled                               4 sprinklers                                                                         40 seconds
​
Note for Dwelling Units:
​
Dry systems must discharge water in 15 seconds, regardless of system size (NFPA 13 2002 11.2.3.9.1, 2007-2016 7.2.3.1).
​

Picture
Inspector's Tests are used to test water delivery times for dry systems when water delivery time test is required. See this article for details and components on inspector's test and drains.
Pre-Action System Capacity

Single-Interlock and Non-Interlock Systems:
  • Must serve no more than 1,000 sprinklers (NFPA 13 2002 7.3.2.2.1, 2007-2016 7.3.2.2)

Double-Interlock Systems of 500 gallons or less (1900 L):
  • Not required to meet any water delivery time to inspector's test connection (NFPA 13 2016 7.3.2.3.1.1).

Double-Interlock Systems over 500 gallons (1900 L):
  • Subject to water delivery times (NFPA 13 2002 7.3.2.2.3, 2007-2016 7.3.2.3.1 and Table 7.2.3.6.1, above)
  • System size based on calculating water delivery (NFPA 13 2007-2016 7.3.2.3.1.4)
  • listed quick-opening devices are permitted to help meet trip-time requirements (NFPA 13 2007-2016 7.3.2.3.2)
  • Note: NFPA 13-2002 Edition only requires water delivery times for systems 750 gallons or greater (NFPA 13 2002 7.3.2.2.2 and 7.3.2.2.3) 
Dry and Pre-Action System Drainage

Auxiliary Drain Location:
  • must be accessible where located in areas subject to freezing (NFPA 13 2007-2016 8.16.2.5.3.1)
  • where maintained at freezing temperatures, must be minimum 1-inch and accessible with plug or nipple and cap (NFPA 13 2010-2016 8.16.2.5.3.2)
  • locations and number of drains must be identified at the dry pipe or preaction valve (NFPA 13 2007 8.166.2.5.3.6, 2010-2016 8.16.2.5.3.7)

Trapped Sections less than 5 gallons (20 L):
  • minimum 1/2-inch valve with a plug or a nipple and cap (NFPA 13 2002 8.15.2.5.3.1, 2007-2016 8.16.2.5.3.2)

Trapped Sections more than 5 gallons (20 L):
  • provide auxiliary drain with drum drip leg in accessible location, see figure above (NFPA 13 2002 8.15.2.5.3.3, 2007-2016 8.16.2.5.3.5)
  • where multiple trapped branch pipe occurs, minimum 1-inch tie-in drains shall be provided and sloped at 1/2-inch per 10-feet (NFPA 13 2002 8.15.2.5.3.4, 2007 8.16.2.5.3.5, 2010-2016 8.16.2.5.3.6)
Wet System Drainage

Trapped sections of pipe less than 5 gallons (20 L):
One of the following is required (NFPA 13 2002 8.15.2.5.2.3, 2007-2016 8.16.2.5.2.3.):
  • auxiliary drain with nipple and cap or plug not less than 1/2 inch in size
  • removal of a single pendent sprinkler allows for drainage of the trapped section of pipe
  • an auxiliary drain with flexible coupling or other easily separated connection

Trapped Sections between 5 and 50 gallons (20 - 200 L):
  • Minimum 3/4-inch auxiliary drain with valve and plug or nipple and cap (NFPA 13 2002 8.15.2.5.2.2, 2007-2016 8.16.2.5.2.2). 

Trapped Sections 50 gallons (200 L) or more:
  • Minimum 1-inch auxiliary drain pipe to accessible location (NFPA 13 2002 8.15.2.5.2.1, 2007-2016 8.16.2.5.2.1).
  • Annex material notes that a typical accessible location would be a valve located 7 feet above floor level to which a hose could be connected to discharge water (NFPA 13 2002 A.8.15.2.5.2.1, 2007-2016 A.8.16.2.5.2.1).

Subscribe & Share
Want more like this? Subscribe to our free weekly articles here. 
Already subscribed? Send to a friend or share on LinkedIn.

Are Fire Sprinklers Required for a Canopy?

2/15/2018

 
“Does this canopy need sprinklers?” “Are sprinklers required below the porte-cochere?” “I have a residential balcony; does it need sprinklers?”

​It's one of the most common design questions in commercial buildings with fire sprinkler systems; you’ve undoubtedly encountered it yourself.

The decision isn’t something that is taken lightly, either. In climates where freezing occurs, dry-sidewall sprinklers are often used for shorter-length projections. With new antifreeze systems are not an option (antifreeze must be a listed, pre-mixed solution which is not currently available), larger exterior projections could require dry sprinkler systems with increased cost, maintenance, and greater susceptibility to corrosion.
​
Picture
Non-combustible overhangs without combustible storage beneath typically don't require sprinklers, but the process to determine whether sprinklers are required is not always clear-cut.
​

Good Design Judgement 

Before diving in on whether sprinklers are required or not, remember that good design judgement is always important. Just because certain code verbiage or annex material exists does not mean you, as a designer, engineer, or review authority, should forfeit good judgment or common sense. These are life safety systems and you were blessed with the ability to think analytically for good reason.

Soapbox aside; canopies, overhangs, and porte-cocheres provide a unique challenge in that they can compromise a building by (1) subjecting the building to trapped convective heat, (2) radiate heat down to the base of the fire and encourage further growth, (3) provide a continuous fuel path to the building.

NFPA 13 addresses exterior projections in Chapter 8 (2002 Edition: Section 8.14.7, 2007-2016 Editions: Section 8.15.7, 2019 Edition: 9.2.3.1 and 9.3.19.1). There are five paragraphs in this section, and while they appear straightforward there are two critical words that tend to throw a figurative wrench into every situation.
Two Words that Complicate Everything: “Combustible Storage”

NFPA 13 8.15.7.5 (2016): Sprinklers shall be installed under exterior projections greater than 2 ft (0.6 m) wide over areas where combustibles are stored.
​

What constitutes combustible storage? Storage of any item that can burn? What about temporary placement or handling of items – would they not burn in the same fashion that long-term storage would?

While not enforceable unless specifically adopted by a jurisdiction, annex material within NFPA 13 offers guidance in interpreting what is considered “combustible storage”.

Temporary or short-term items, such as parked vehicles or delivered packages, while combustible, would not be considered ‘storage’ (NFPA 13 2007-2016 Annex A.8.15.7.2 and A.8.15.7.5, 2019 A.9.2.3.2). 

Minor amounts of combustibles may also not justify sprinklers, such as planters, newspaper machines, or combustible furniture on balconies for occupant use (NFPA 13 2002 Annex A.8.14.7.4, 2007-2016 Annex A.8.15.7.5, 2019 A.9.3.19.2). 
​
Picture
Temporary loading and unloading of vehicles, according to the Annex material in NFPA 13, doesn't necessarily justify sprinklers. However, good judgement is critical especially when protecting high-priority facilities like hospitals.
​

Justified Situations

Conversely, an exterior loading dock is designed to accept incoming shipments which inevitably end up residing below canopies while loading and unloading occurs, even if only temporary. While long-term storage might not occur, it could be reasonably argued that enough shipping items, pallets, boxes, or other items could collect to be considered “combustible storage”. 

Projections above the only means of egress or exterior ceilings where the building is occupied above is also suggested to require sprinklers (NFPA 13 2007-2016 Annex A.8.15.7.2, 2019 A.9.2.3.2). Either of these arrangements, if not protected, could reasonably compromise the egress ability or occupied areas above and could be justification for providing sprinklers.

Parking areas that are not used for pickup and drop-off are another example of combustibles that would be present long-term, which the annex does not exclude.
​
Picture
Loading docks are used for transitioning shipments to the building, so collection of combustibles underneath an overhang could be a common occurrence.
​
Judgement by the Designer and Authority Having Jurisdiction (AHJ)

If so much of the guidance is provided in the unenforceable annex material and the body of NFPA 13 is vague about combustible storage, how do we determine when sprinkler protection is required? Ultimately, the determination of whether a situation requires sprinklers due to the amount of combustible storage is up to the Authority Having Jurisdiction. It is a judgement call that is based on the amount of combustibles and length of time where combustibles would be present. 
​
An Exterior Projection Cheatsheet

While the judgement of amount of combustible storage resides with the AHJ, here is an updated and expanded flowchart based on the body and annex material of NFPA 13 to help guide the decision process (original published by the National Fire Sprinkler Association in a TechNotes in May 2007):

Canopy, Overhangs, and Projections Sprinkler Flow Chart
Get this free, printable PDF quick-guide to Canopy, Overhang & Exterior Projection Requirements here:
Download Free PDF Guide

Design Challenge #1 Winner

2/15/2018

 
Congratulations to Mike, our first ever design challenge winner. 

Last week Mike's submitted "Design A" was voted the top design running away with 64% of the submitted votes. Congratulations Mike; he climbs to the top of our new leaderboard and earns a $40 gift card towards the online store.

See the submitted designs, the challenge, and follow-up discussion about them here.
MeyerFire ​Design Challenge Leaderboard
Designer
Mike
​FireManStan
Points
2
​1
Notes
Challenge #1 Winner
​Challenge #1 Runner-up

Have a design challenge you'd like to propose? Send it to us at [email protected].

Vote Now: Design Challenge #1

2/7/2018

 
Which of the following designs do you prefer? 

We have two chosen finalists for this Design Challenge. Review, vote, and discuss below.

Original Design Parameters:
Codes: 2012 International Building and Fire Code
Standard: NFPA 13 - 2010 Edition
System Type: Wet Pipe System, Fully-Sprinklered
Seismic: Occupancy II, Design Category B
Construction Type: V-B (combustible)
Structure: Solid Engineered Joists
Pipe Type: CPVC or Black Steel
Surroundings: Unit door runs to the common corridor; additional units reside on each side of these units

​Design A:
[View PDFs]
​
Picture
Picture
Picture

​Design B:
​
[View PDFs]
​
Picture
Picture
Picture

Material Comparison:
​
Picture
Picture

​Vote
Vote

​What works and what doesn't? Discuss your take in the comments section on the website.

​Top designers with highest voted submissions earn a spot on our leaderboard.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT