One of the things I feared most when I had my first real job was that I was going to be exposed as a complete fraud. Yes, I had a degree. That degree had a grand total of 9 credit hours specifically to fire protection, which statistically is more than roughly 90% of our industry starts out with. But, see, the problem was… that I knew nothing. I knew this. But my fear was that when I made my first phone call to someone on the other line, they’d quickly know this too. And that all came in the form of my first ‘code call.’ THE CODE CALL We used the term code call, I don’t know what you might call it, but it’s just a touchpoint check in with the AHJ to be sure that (1) we’re on the right track with applicable codes and standards, and (2) that we coordinate jurisdictional needs. What good is a set of engineering bid plans, if we halfhazardly threw an FDC in the wrong spot? Or the fire alarm control panel? If we referenced the wrong codes? If we stipulated too low of a hydraulic safety factor? If we located the hose connections on the wrong landings? The answer is no good at all. If we’re not helping clarify and coordinate the needs of the project with the jurisdiction, then we, as consultants, are simply getting in the way and making things more difficult than they need to be. IMPOSTER SYNDROME Back to that phone call. How long would it take for the person on the other line to realize that I knew very nearly absolutely nothing about fire protection? That if they asked one clarifying question, it would call my bluff and I’d have no escape? Ten seconds? Twenty seconds? It wasn’t an irrational fear, nor was it overwhelming. I made that call. And more after it. And I did make a fool of myself. I once asked “do you require duct detectors to be located on the supply side, return side, or per code?” The response: “Why would it be anything other than per code?” Ope. Game’s up. I have no idea. Time to pack the bags and find a new career. All drama aside, I survived. Sometimes failed. I learned. I slowly grew to understand the purpose behind our list of questions. Who were these people I was calling? That’s half the game. Sometimes it’s a Fire Marshal. Sometimes it’s a plan review as part of the building department. Or fire department. Sometimes it’s the volunteer combination of Fire Chief/Marshal/Inspector/Reviewer. Sometimes they were the nicest people I’ve ever met. Sometimes hostile. Just goes with the territory. I’ve had jurisdictions that wouldn’t pick up the phone unless I called from a local area code. And I’ve had others apologize because they wouldn’t be able to run a flow test for me until Monday morning. (I had called on a Friday. At 4:45pm). Diatribe aside, I’d like to share the list of questions that I ask – (1) – so you can critique and help us all improve upon the list of questions – and (2) – so that future generations of inexperienced callers might not have to suffer the imposter syndrome that I did with those first few calls. WHO IS THIS FOR? Here is my developed list of questions that I would ask today for a code call. This is very specifically used for consultants to coordinate requirements with AHJs before a bid set is issued. Why isn't this used for contractors? Would I ask this when doing shop drawings? No; I might coordinate FDC types and locations. Coordinate standpipes. Coordinate some fire alarm or waterflow questions. However, a designer at the shop drawing stage is not the person to determine the scope. They can and should coordinate, but not determine scope. A consultant's role is to determine the scope, so principally these questions are supposed to happen before bids ever take place. These do have cost impacts. MY LIST OF QUESTIONS (AND NOTES) Below it is a very short context for why I ask the question. Code basis can wait for now. This is long enough as is. What I ask from you is what you would tweak? If you’re an AHJ, how can I better ask the question? How can I better clarify the intent of the question? OPEN-RESOURCE FOR CODE CALLS We’re actively working on an open and free tool just for code calls. Some time ago we tried a spinoff code call database, but the enthusiasm for jurisdictions to volunteer information wasn’t something that we could get to scale. So I’d like to try this from a different angle. My hope is that, if we construct this open tool right, and educate around the process in the open, it could be a tremendous resource for both designers and AHJs to meet in the middle and have coordinated projects that meet the needs of each jurisdiction. Easier and better results, every time. A new code call resource for designers and AHJs to better coordinate local requirements is in the works. So, here’s the list of questions that I would ask today, almost like a script.
My own personal notes are italicized below each question. BRIEF INTRO Thanks for taking my call. I’m Joe Meyer, designing the [project] at [address]. It’s going to have [fire alarm/sprinkler/standpipe system(s)], and I’d like to ask you a few questions to make sure we’re coordinated with your department. Should take about five minutes. Is that OK? → Note: If the time isn’t good, or they’d prefer an email, I’d go that route instead. APPLICABLE CODES & STANDARDS 1. Great. Your website says you’ve adopted the [2012/2015/2018/2021/2024 IBC or NFPA 101], is that correct? → Note: Doing the research ahead of time is key. Without it, it makes the listener feel like they’re doing the work. 2. Do you adopt any specific editions of NFPA standards like NFPA 13, 14, or 72, or just whichever edition is referenced by your building code? → Note: Many people don’t know this, but IBC Chapter 35 and NFPA 101 Appendix D or E will actually list which editions of NFPA standards are referenced. Some jurisdictions will adopt very specific editions, which is why I like to ask the question here. Following questions noted with an asterisk (*) are only asked if necessary. FIRE ALARM* 3. For fire alarm, we intend to locate the main control panel in [front entry/main electrical room/a back of house area]. If we do so, do you require an annunciator panel at the building’s front entry? → Note: For small buildings with one main entry where the FACU is located near the entry, no annunciator is usually needed. For larger or more complex buildings, when we might not want the FACU at the front entry, having an annunciator at the front is a very reasonable need. 4. Does the fire alarm monitoring require a listed Central Station Service, or is standard code-required monitoring, like a supervising station, acceptable? → Note: Jurisdictions that require a listed Central Station service usually know what it is, and will recognize that it’s required. It’s more expensive and carries more stringent requirements than a normal supervising station, which is a code-minimum requirement. DUCT DETECTION* 5. When duct detectors are needed, do you simply require locations to be per [the IMC/NFPA 90A], or do you require duct detectors to be located in specific locations, like the supply or return side of units in the ductwork? → Note: This is a question I could use help with. A simple ‘per code’ answer is wanted here, but some jurisdictions have insisted on locating duct detectors on the supply-side of units, or return-side, or both. If the jurisdiction has a specific requirement, I’d like to know that now rather than be surprised later, but most usually don’t, and as a result, it’s a lame question to ask in those cases. 6. Do you require duct detectors to initiate an alarm signal, or is it OK to have those report a supervisory signal to the fire alarm control panel? → Note: NFPA 72 allows duct detectors to initiate a supervisory signal, because they’re more prone to nuisance alarms than other devices. An alarm signal usually results in a truck rolling up to the building each time. Jurisdictions that are familiar with this topic are usually more than happy to have duct detectors on supervisory rather than alarm. 7. When a duct detector activates, can it shut down just that unit or do you require all units to be shutdown? → Note: To my understanding, this is just a preference. Not a huge deal either way unless we’re talking about a massive building or building complex where all units shutting down would be very uncomfortable and problematic. SECURITY / KNOX BOX 8. Do you require a Knox Box? → Note: There’s likely a code path for this, but it’s not something I’ve hunted down to date. Most jurisdictions can readily answer this. 9. Is the Knox Box required to tie to the fire alarm system? → Note: These can be monitored by the fire alarm system. Most jurisdictions don’t require them to be monitored, but some will in areas that have higher crime rates. FIRE SUPPRESSION - FIRE DEPARTMENT CONNECTION* 10. Do you mandate a maximum distance from a fire department connection to a nearest hydrant? → Note: Some jurisdictions care, others less so. There’s (to my knowledge) not a mandated distance, but some jurisdictions will require as close as 50 ft and others as far away as 400 ft. 11. Can the FDC be mounted on the building’s street-facing exterior wall, or does it have to be located remotely from the building? → Note: As a designer, my strong preference is to have the FDC on the building to save cost, protect the pipe from freezing, protect the pipe from mechanical damage, keep it clear from snow, and keep it easier to inspect, maintain, or repair. Operationally, depending on the building and the site, some departments are not going to want to send firefighters to the building face and would rather have a remote connection for some applications. 12. What type of FDC do you use [Dual-Inlet 2-1/2” / 4” Storz / 5” Storz]? 13. Do you require locking caps on the FDC? → Note: Some jurisdictions will have locking caps to prevent people from shoving debris, trash, or other ‘items’ into FDCs, and to prevent theft of the caps. Many areas have no need for locking caps. BACKFLOW* 14. What type of backflow preventer do you require [double check, double check detector, RPZ, or RPZ detector]? We [will/will not] have antifreeze or chemical additives in the system. → Note: Some jurisdictions, like fire departments, may not want to answer this because it’s under the building or water department. But most are familiar with the requirements anyways. Some places require RPZs for everything fire protection (like an Illinois state mandate). By code, RPZs are required if an antifreeze system is used, or if chemical additives are added to the system (such as corrosion inhibitors like Vapor Pipe Shield). 15. We intend to locate the backflow inside the building. Is this acceptable? → Note: This is a designer preference for longevity of the backflow, protection from damage and tampering, protection from freezing, service, maintenance, and cost. Some owners may want the floor space or jurisdictions might require it to be outside (though I don’t know why). 16. [If a double check is allowed, allowed to be inside, and there is only a single zone] We intend to use a backflow preventer that’s listed for a vertical orientation. Is it acceptable to install it vertically? → Note: RPZs have to be horizontal. If we have single-zone systems, designers generally prefer to use a ‘shotgun’ approach and save floor space. This is usually fine. HYDRAULICS* 17. Do you mandate a safety factor for fire sprinkler systems? → Note: This is a topic that is book-worthy. NFPA 13 has no mandate other than to account for seasonal and daily fluctuation. It could be argued that a safety factor is implicit within NFPA 13. But to save everyone’s time and scrutiny, a simple 5 PSI or 10% safety factor tends to be common practice. Too high a safety factor isn’t necessarily a good thing because it could lead to needing a fire pump that introduces many new points of failure or could add unnecessary cost to a system. 18. Does your department conduct flow tests, can we conduct a flow test, or are those done by the water department? → Note: This is just practice-based by jurisdiction. Some don’t allow flow tests at all and use water modeling (California). INSPECTOR'S TEST* 19. [If there are only wet systems] We usually locate the inspector’s test at the riser, which NFPA 13 allows for wet systems. Do you require it to be located remotely? → Note: If this is a dry or pre-action system, then the inspector’s test must be remote. If it’s wet, it’s allowed to be at the riser. That said, some jurisdictions have a preference which we’d want to accommodate here. WATERFLOW* 20. Do you want a horn/strobe, or electric bell on the outside of the building for waterflow? → Note: Just a jurisdictional preference. Either of these are easier to accommodate than a water motor gong which had been the tradition for some time. 21. Is exterior access required for the sprinkler riser room? → Note: These are usually on the outside of the building since the water service entry cannot go more than 10 ft underneath the building without open trenches, per NFPA 13, but sprinkler riser rooms don’t always have an exterior door. SITE 22. Just a few more questions. Do you require a post-indicating valve? There are no code mandates for one. → Note: Some jurisdictions want them, many don’t care. Just an opportunity to coordinate it early here. 23. Is Fire Flow ok to be determined using the International Fire Code Appendix B, or do you have some other method to calculate it? → Note: Fire Flow is wildly misunderstood and falls through the cracks of design scope. As a result, many jurisdictions don’t pay attention to it or aren’t familiar with it. If they don’t know or don’t care, Appendix B is a fine approach to use. FIRE PUMP* 24. We have a fire pump on this project. Do you consider the electric power supply to be Reliable or not? → Note: NFPA 70 has specifics on how power is considered to be reliable or not. There are formal definitions, but it’s up to the AHJ on whether they consider the power utility at the site to be reliable or not. If it’s a point of contention or needing clarification, it’s worth spending time here because the cost to go from an electric fire pump to a diesel or add a generator can be substantial. STANDPIPES* 25. We intend to have a [wet/dry manual/semi-automatic/automatic] standpipe system for this building, using [Class I 2½” / Class II / Class III] hose connections. → Note: In sticky projects using dry standpipes or high-rises, the type needs to be coordinated. In basic non-high-rise situations, a wet manual system is fairly straightforward, so it’s not a question as much as a coordination point. 26. We intend to locate hose connections on the floor level landings of stairs. Is that acceptable? → Note: The IBC and NFPA 14 have jogged back and forth on this, but they now correlate on the main-floor-level landings of stairways for hose connections. AHJs are permitted to require intermediate-level landings in both the IBC and NFPA 14, though, so it’s an important coordination point. Thank you SO much for your time. Any questions for me, or anything else you feel I should have asked? YOUR TURN Alright - it's all out there - what would you tweak? If you’re an AHJ, how can I better ask the question? How can I better clarify the intent of the question? What am I missing? Would absolutely love your commentary below. Your input can make this new collaborate tool much more helpful and hopefully impactful for the industry as we launch it and hopefully move things forward. See you in the comments ↓↓ - Joe Last week, we posted results on what sprinkler contractors need as part of a set of biddable construction documents. One of the top needs that sprinkler contractors expressed was whether the owner had any insurance-driven criteria that applied to the project. THE SURPRISE This likely isn't a surprise if you've encountered it on a job: a building is designed, bid specs are applied, bids are collected, the contract is awarded, sprinkler shop drawings are created and submitted, and then out of the blue [BOOM!], a review comes in from FM Global. FM Global? Did someone know that this was an FM Global job? No discredit to the FM Global team whatsoever - they do an excellent job in establishing a higher level of excellence and have propelled our industry for years - but shouldn't we all have known that FM would be a part of the project from the beginning? That answer, of course, is yes. CHALLENGES WITH INSURER-DRIVEN CRITERIA It can be tough to grapple with if you've been on a project where that's been a surprise. It can also put a building owner in a difficult position of mediating what their insurer wants them to provide against the increased cost of doing so via change order. As we've discussed, delegated design is one key area where a consultant provides tremendous value in coordinating and pre-planning these asks well before bid day, which would create a smoother project experience. Instead, missing or ignoring insurance criteria altogether can set the project back in schedule and cost. From the consultant's side - it's not always easy to get a straight answer from a building owner. VARIABILITY AMONG BUILDING OWNERS Big developers or large corporate clients are often very informed on their design standards; they may even have a complete set of standards themselves ready to distribute. Smaller or first-time building owners are often less likely to carry insurance criteria that stipulate much in terms of fire protection above code minimum. But what about the projects in between? What about the corporate client building in the area for the first time? The regional grocery chain? The distribution center? Mid to large retailers? Restaurants? Healthcare? Manufacturing? Hotels? Anything in this range could carry insurance that mandates a standard above NFPA 13 in certain areas, including critical ones like sprinkler design criteria. Just because an insurance company isn't FM Global doesn't mean that FM Global Standards don't apply; many other carriers could still follow FM Global criteria or even have a more comprehensive program like XL GAPs (or something similar). Insurance criteria and owner standards play a critical part in a set of fire protection bid documents and can be a costly surprise too late in a project. But what's the best way to get the answer from the right person?
BEST PRACTICES FOR GETTING THE INSURANCE QUESTION ANSWERED What I'm most curious about is what has been your most successful process for getting this information from a building owner. As a consultant, I had my best luck when we'd have a design meeting, and the owner or owner's representative was in the room, and I could ask directly about any insurance mandates above code minimum. The line I used often sounded like, "Do you carry any requirements or standards above code minimum, like FM Global?" If the owner or owner's representative was familiar with FM Global, there'd usually be a quick yes and they could confirm fairly quickly. Honestly, all other cases would get a blank stare. I'd explain that the insurance criteria above the code were not the norm but that we'd want to incorporate it if there were any that applied. In most cases, this was enough information to work from, but I never liked the inexact nature of going by a mostly uninformed answer. I found it to at least elicit a response, unlike emails, which tended to never get returned, but still - there's got to be a better way. THE BIGGER QUESTION: WHAT WORKS BEST FOR YOU? From last week, we know that insurance criteria are a major factor in determining what should be in the bid documents. So my question to the consultants here is: What have you found to be the best approach to getting this information from an owner? What method has worked to (1) actually get a response from the right person and (2) get a response that's usually accurate? Let us know in the comments here. I have my lame approach but I'd much rather collaborate and share ideas on what works so that, as a whole, we can do a better job of creating a quality set of bid documents. Thanks for continuing to advocate for the industry. Hope you have a great rest of your week! - Joe Perhaps the biggest elephant in the room of the fire sprinkler design industry is the problem of delegated design. It's not the concept, per se, but its execution that leaves so many projects in bad waters ripe with change orders. I'm looking specifically at projects where little to no effort was put into the fire protection bid documents, and as a result, the bidding contractors are worse off than if no fire protection bid documents had been provided at all. BAD DELEGATED DESIGN Bad delegated design (1) makes bidding and estimating far more difficult, (2) performing the work more difficult, (3) can create costly change orders for the owner, (4) can actually get in the way of code compliance, and (5) hurts bidders, building owners, and the practice of fire protection engineering overall. Fire Protection doesn't have to be a "necessary evil." It doesn't have to be the bane of every architect and building owner. We don't have to be the bad guys: this is an issue we can do something about. And make no mistake - I'm not immune to putting out sour projects. I can improve just as much as I like to soapbox. Personally, I think this should be the central focus for any fire protection engineering organization. It's the #1 issue I hear about from the construction side. Cleaning up the practice and improving the building owner's experience with a smooth, streamlined process with far less adversarial friction can put fire protection in a warmer "thanks-for-looking-out-for-us" light rather than what it is today for many. HOW TO FIX? I don't get the impression the issue has much of anything to do with those who are fire protection people - those inside the industry who learn, read, push themselves, get educated, engage online, ask questions, go to the fire protection conferences, get their CEUs in fire protection, or get credentialed in fire protection. I don't get the sense that the problem is from those who are plugged-in and are invested in fire protection. But, that doesn't mean we let it slide. This is a topic that we're not going to let go until it's far better than what it is today. If you want to read more on this, see these pieces: - The Delegated Design Problem - FP Engineering Documents: What Goes In? - A Practical (Real-World) Design-Spec Checklist - The "Lanes" of Fire Protection Pre-Bid Consulting - Why Isn't All Sprinkler Design Done Upfront? WHAT MATTERS IN A SET OF BID DOCUMENTS? We're working on material to help build up the consulting side - what we need help with today is identifying what it is that actually matters to sprinkler contractors in executing a project (estimating, bidding, managing, designing). IF YOU WORK IN SPRINKLER CONTRACTING, WE NEED YOUR OPINION HERE: Yes, this is a survey - it should take about 120 seconds - but it's one where we're looking for specific scoring data so that we can relate, score, and real, helpful give feedback to consultants on how they can create better documents. This is an opportunity to be heard and help us deliver something tangibly helpful in improving the industry. We'll follow up with the data we collect and give that back to you as a big thank you for your time and input. I hope, in time, to put together entry-level educational material on exactly these topics but have your voice in as part of that process. Plenty more to come on this topic. After you've had a chance to take the poll and score what matters to you, come back here and share your take in the comments below. Your take is always appreciated! Thanks as always for being part of this community, and have a great rest of your week! - Joe HOW DO WE FIX BAD SPECIFICATIONS?
Last week I touched on a concept of using large language models to instantly review a series of specifications. Thanks for the comments! I’ll write up the step-by-step and incorporate that in a how-to video for posting here and on YouTube. A special shout out to Kimberly Olivas, Brian Gerdwagen and Casey Milhorn on their comments in that thread – very helpful and insightful. The discussion brings me back to two questions I may have inadvertently skipped right over –
A PROBLEM WE CARE TO FIX? If part of a bidding contractor’s value proposition is using their expertise to sort through bad specifications and give an advantage; either in exclusions or clarifications, or change orders later in the process due to inaccuracies, scope not meeting code, or scope gaps. In other words, based on a bidding contractor’s position – there might not be any incentive for them to play their cards for competitors to see through the Pre-Bid RFI process other than a smoother project experience for the owner. A bidding contractor is not a representative of the owner; the consultant is. Ultimately the consultant is responsible for protecting and supporting the owner – which is why they were hired in the first place. Perhaps many contractors don’t look at it that bluntly – but I can understand the sentiment not to tip a hand at project issues when it could mean losing a bid. WHAT’S THE ANSWER? If Pre-Bid RFIs are not the cure-all in today’s pace of estimating – and contractors are not incentivized to be correcting consultant issues – then do we care to actually fix it? For estimators – are bad specifications purely an annoyance for you – or do they cause issues on your projects? Would you prefer that specifications actually be well written? I’m not being facetious – I’d love to know your take on this. ALTERNATIVE APPROACHES If better specifications (and plans) are something we deem better for the industry – and we collectively want better plans and specifications – what is the approach to get there? More specifically, how do we encourage those who don’t really care about fire protection to put a little more effort into their plans and specifications? This was last week’s idea:
Here are some alternative from-the-hip ideas that I’d love to kick around with you and see if you find any of these might be viable: IDEA #1: PUBLISH AN OPEN MICROSOFT WORD FILE BASIC FIRE PROTECTION SPECIFICATION
IDEA #2: CREATE AN AI TOOL FOR CONSULTANTS TO QC THEIR OWN SPECIFICATIONS
IDEA #3: PROMOTE OR CREATE A LOW-COST SPECIFICATION GENERATOR
IDEA #4: HAVE A FORMAL THIRD-PARTY REVIEW PROCESS (A GROUP) FOR SPECIFICATIONS
IDEA #5: PUBLIC HUMILIATION
IDEA #6: YOUR IDEAS
Do you (1) think this is a problem that should be fixed, and (2) what concepts do you think could make a difference? Comment below – would love to foster a deeper discussion on how we might solve this problem before skipping ahead and creating something that might not be impactful. How do we solve the systematic problem we have with fire protection bid documents? Some, if not much of the plans and specifications that go out for bid are generally helpful. A quality set of fire protection bid documents:
These types of bid sets do happen. But far, far too often, they don’t. It’s systematic, and makes every step of the design and installation process far more difficult and far more costly than it could be. NOT FAULTLESS I don’t even want to pretend I’m not at fault here. I’ve designed poor projects. I’ve slacked on coordination, and detailing. I’ve glossed over parts of a project that I shouldn’t have glossed over. It’s been painful. But this is something that we can change. WHAT CONTRACTORS SAY For some years now I’ve spoken with sprinkler contractors, architects, and consultants about this. If you’re a contractor, especially if you work in estimating - you could provide countless examples of terrible bid documents. Bid documents that actually get in the way of you doing code-compliant, efficient work. You could speak to this far better than I can. In these conversations, over and over, I’ve heard one key feature that I think many consultants in the MEP space miss. It is far better to have no fire protection bid documents, than to have bad fire protection bid documents. NO FIRE PROTECTION BID DOCUMENTS? That’s important, and counterintuitive. It is far easier for a sprinkler contractor to look at a project and define their own scope, and put a price to it, than it is to try and bid a set of documents that:
If that sounds too far, ask your closest estimator friend. They see this all the time. How many projects do we see underground feeds piped 20-ft before rising up? How many times do we see Star, Central, or Gem still specified today, in 2024? How many times do we see projects wanting a fixed-price bid yet have zero information about the water supply? How are those documents helpful to a bidder? They’re not. MY ANALOGY The analogy that I’ve had in my head and finally am able to bring to life a little is the road, showing the different tiers of fire protection bid documents: 1 - NO FIRE PROTECTION BID DOCUMENTS
There’s the sidewalk on the left, where we have no fire protection bid documents. Let’s say we have a single-family home with an NFPA 13D system. Scope is simple, perhaps we have no specific owner needs, and it’s unambiguous. That type of project probably warrants no upfront, pre-bid fire protection involvement. It wouldn’t have to just be a single-family home though. What about an add & relocate job for a small retail space. Or a small office building. Those can, and often do, work just fine without any upfront fire protection bid documentation. Design-build all the way. 2 - QUALITY "PERFORMANCE SPECIFICATIONS" Then we skip ahead to quality “performance specification” documents. These do all the things we’ve talked about. They don’t necessarily show pipe or sprinklers, but they clearly define the scope, they communicate clearly, they answer major scope questions, they address and alleviate major issues or coordination challenges upfront, and they make it easy to put a price to the job. That’s a quality set of “performance specifications”. 3 - QUALITY "FULL-DESIGN" For high-end jobs, or high-hazard jobs, or critical function or high-visibility or unique jobs – perhaps we’re looking at a full-upfront design prior to bid. Full-design isn’t free, nor quick, and isn’t necessarily the answer for every job. But, as we’ve talked on this topic before; if it’s done well, and thoroughly, then fully-detailed plans can be a tremendous asset to a project. They can eliminate ambiguity and really dial-in exactly what work needs to be done. AND... THE DANGER ZONE What about the DANGER ZONE? There’s a gap, and it’s in-between no bid documents and quality “performance specifications”. And that is the Danger Zone. This is the lane of bad bid documents. These are all the bad things. Inconsistent, boilerplate, confusing, inaccurate, unachievable, irrelevant, or not actually code-compliant. What happens when we live in that lane? We get hit by the proverbial bus. Change orders. Litigation. Or much worse – a fire happens with major loss. This is not the spot to be. WHY DO WE STAY IN THE DANGER ZONE? I’m fairly confident that those who live in that space don’t want to be there either. They feel compelled because the client asks for fire to be included. They feel pressure because competitors are offering to do fire protection. They feel they can’t spend enough time on fire because there is hardly any fee there. Honestly – these are all poor excuses. If there isn’t enough money in the job to put together a quality set of fire protection bid documents – then don’t do them at all. It is far better to have no fire protection bid documents, than to have bad fire protection bid documents. HALF-BAKED DOESN'T HELP Bad, sloppy, half-baked documents don’t help. They don’t solve anything. They get in the way. If you’re the MEP who finds yourself in this area, having that conversation with an owner or architect and there’s just not enough fee to do quality work – then just exclude it entirely. If an architect insists that it get thrown in or done on a microscopic budget, then just ask them to hire a fire protection consultant separately. Half-baking a set of documents is not worth the hassle or the liability. It also doesn’t actually help. When you do take it on, do it well. We all benefit from that. YOUR TAKE If you’re a sprinkler contractor or architect – I really want to hear from you. Where do you land on this? When projects have gone south or had major change orders – what happened? Would being in a different tier have changed the result? Comment below, would love to hear your take. And, thanks, as always, for reading and being a part of the community here. We will get this right. The majority of bid documents for fire sprinkler work is some form of delegated design. A consulting engineer frequently does not provide all of the detail about a system (pipe locations, size, hanging methods, hydraulic calculations, etc). Why is that? In other disciplines, the opposite is common. Mechanical Engineers regularly selects a system type and lays out ductwork in a one-line or two-line configuration on a plan before a contractor bids the system. Electrical Engineers commonly size up, calculate and provide power and lighting locations on plan with an overall one-line diagram. Even plumbing often has plans for domestic water feeds and sanitary waste. Why doesn’t that happen for fire protection? First, the biggest disclaimer today, I’m not advocating for all design to be upfront. Or even a majority of it. I do see many applications where a quality FPE consultant can provide a tremendous amount of value to a project. I explored this a bit with The Delegated Design Problem and in A Practical Design Spec Checklist. But I would like to start the conversation and get your ideas on why we are where we are today with why designs are not done upfront. Here is why I think all sprinkler design is not completed upfront, before bid time. #1 WE DON’T WANT EVERYTHING UPFRONT
Overwhelmingly, the sentiment I hear from sprinkler contractors about ‘full-design’ fire sprinkler drawings is that they wouldn’t want upfront designs for all projects. Why? Because in some (or many) cases, sprinkler contractors feel that upfront design either limits their flexibility or is of very poor quality, or both. A design that doesn’t coordinate with other systems, or ‘leaves coordination’ for the sprinkler contractor, is problematic. It’s difficult to bid and difficult to work with after a project has been awarded. How much needs to be ‘coordinated later’? How ‘real’ is the design? Is it less efficient than the contractor could have laid it out? Many who have designed on the contracting side feel that real-world “fit” and doing the sprinkler layout are one in the same. You can’t ‘rough-in’ a layout without thinking about conflicts and making it actually work in the real world. As an extreme example, I think most could agree that a basic NFPA 13D layout does not need upfront involvement by a consultant. Could they help? Perhaps. Could they provide value? Perhaps. But it does not need a high level of involvement. Now there’s a big counterpoint to this. Just because we don’t want upfront design on all projects doesn’t mean it wouldn’t be beneficial on some projects. Projects that have very specific needs, unique needs, high-visibility challenges, coordination challenges, or that require a specialized set of expertise could very much benefit from upfront involvement. Maybe it’s a retrofit in a high profile historic museum. Maybe it’s suppression for an automated storage retrieval system. Maybe it’s a unique storage configuration that is outside the bounds of NFPA 13. In these types of situations, involvement from a quality FPE consultant can address code concerns and clearly define the scope. It can help mitigate a lot of risk for contractors by doing so and help everyone bid apples-to-apples instead of a wide-open, ill-defined scope. #2 INADEQUATE WORKFORCE (INDIVIDUALS AND COMPANIES) Perhaps the alternative reason is the lack of expertise in the workforce. We simply don’t have enough people, nor expertise, to take on every project. Even if we wanted upfront involvement to a high-level of detail, we as an industry couldn’t pull it off. We don’t have enough bodies, nor enough qualified expertise. Is it an issue? Absolutely. Does the lack of people affect how well we advocate for fire protection itself? Absolutely. Could the construction experience for architects and owners and contractors actually benefit from more and better individuals working upfront on project? Absolutely. But until we catch up on the quantity of our own workforce, we simply can’t take on more involved work. #3 LOCATION OF THE EXPERTISE Another reason we don’t perform highly-detailed layout work upfront is the location of where expertise for layout technicians often falls – and that’s in contracting. Anecdotally I know far more layout technicians in contracting than I do in consulting. In our survey of nearly 500 industry professionals in 2022, of those who had roles as a designer or layout technician, 68% of them worked for contractors (another 4% were self-employed). That’s different than other disciplines where there is plenty of design and layout expertise embedded in consulting. #4 DOWNSIDES: COST, INFLEXIBILITY, & SCHEDULE Involving expertise upfront isn’t free. There’s a cost associated with it. We mentioned it before and stipulating a full layout upfront also set some parameters in place that can limit the creativity and efficiency of a contractor-provided layout. Lastly, there’s time needed to do that work upfront. Having a high-degree of involvement may not be a positive impact to overall project schedule. SO CAN WE KILL-OFF UPFRONT INVOLVEMENT? It sure feels like I’ve put out a hit piece on any upfront involvement in fire sprinkler design. The question is – does all design need to be done upfront? By an engineer or consultant, or someone other than a contractor? That answer is no. All design doesn’t need to be upfront. We couldn’t pull it off anyways, but it could also be costly and obstructive for many small or simple project applications. Is there value to having upfront involvement? Absolutely - when it’s done well. Consultants provide tremendous value, all-around, when:
Do consultants need to be doing fully-detailed layouts to accomplish this? Often no, though sometimes it could help. HOW DO WE RESHAPE THE WORK? In an SFPE Magazine Article in 2022, Thomas Gardner wrote “There is a happy medium between no delegation and full delegation of the fire protection system.” Count me in that camp. Many times when the subject of “Delegated Design” gets brought up, we instantly jump to extremes. Either all design should be by the EOR, or no design should ever be by the EOR. On one hand we have many military projects that specify the Qualified Fire Protection Engineer (QFPE) to be in direct charge of the layout upfront, if they don’t perform it themselves. On the other hand, we have an ever-growing amount of residential projects in North America that have no FPE or consulting involvement whatsoever. Both of these situations are not necessarily at odds. We can strike the balance between the two, and we can do “Delegated Design” better than what’s being done today. We can improve the quality of upfront documentation that defines scope and goes out for bid, and at the same time, still provide flexibility for the contractor and an overall lean project delivery. Part of solving that puzzle is looking realistically about what different approaches mean – how they look – seeing good and bad examples – and moving forward to introduce, educate and advocate on what better “Delegated Design” means in the future. For literally the past two decades there has been growing momentum to bring light to the issue. We’re not far from having more resources to define what “better” looks like and how we can easily get there. WHAT'S YOUR TAKE? We had a great dialogue about the problem of Delegated Design before, that's here. But what's your take on why work isn't provided upfront? Is it just tradition? Just the way things always have been? Is it any of the reasons I've cited? Why is our delivery method so different from Mechanical, Electrical, Plumbing or Structural? What separates us from other disciplines? Comment below - would be happy to hear your take. Last week I wrote on the Delegated Design Problem we have in the fire protection industry. The big ugly elephant that looms over us all. And wow – what a response! It’s a good thing (I guess) that so many others are as agitated as I am with the state of delegated design as I am. GOOD DELEGATED DESIGN ≠ FULL-LAYOUT One big and important point I’d like to make about the issues with what I’m calling delegated design; the answer is not full layout drawings by engineers. Some fire protection engineering firms can, and do, excellent detailed layout drawings for fire suppression systems. In some cases (unique, high-risk, location-sensitive clients), full-layout fire sprinkler documents can help convey exactly what the owner needs to all bidding contractors. It can be well done. But that’s not what we’re talking about when we’re talking about good delegated design. A set of engineering documents go by plenty of names:
I’m simply calling them “Engineering Documents” and that process being “Delegated Design”. A good set of high-quality of Engineering Documents is helpful to contractors, helpful for pricing, helpful to define and communicate the scope, and helpful to the owner as it conveys what the owner wants. In my opinion, that doesn’t have to mean a full-layout. In most contractors’ opinions (we’ll get data on this later), my guess is the far majority don’t believe that quality engineering documents means a full layout. If done poorly, they’re actually worse for a project. WHAT SHOULD ENGINEER DOCUMENTS INCLUDE? So what criteria exists today? We wrote on this a few years ago with a checklist for things to consider in a set of Engineering Documents. That’s our go-to on what to include. But what does everyone else say? Ten different leading organizations in the industry addressed just that. In a joint position statement originally created by SFPE and endorsed by everyone else (ABET, AFAA, AFSA, ASCET, FSSA, NCEES, NFSA, NICET, NSPE, SFPE), the paper identifies what it is that Engineering Documents should include. A link to the position statement is here: https://www.nspe.org/resources/issues-and-advocacy/professional-policies-and-position-statements/sfpenspenicetascetncees This is an important piece of information that (just my opinion) seems to be met by those who care about fire protection, and completely ignored by those who don’t. I would go so far as to think that most of the players who don’t meet the recommendations of the white paper probably don’t know it exists. There’s a major disconnect there. STATE MANDATES In some states, much of this same criteria is formally adopted into state law. Three that I’m personally familiar with (Florida, Illinois, and South Carolina) overlap much of what the joint position recommends. These state mandates have teeth. If an AHJ has installation drawings without upfront engineer involvement, they have the authority to reject and require upfront involvement (Illinois is slightly different in that the specific requirements are less defined). Other states have mandates too. If you have a tip you’d want us to add to this, comment below here. SO, WHAT IS REQUIRED FOR ENGINEERING DOCUMENTS? Below is a table to compare the main elements of the joint position paper and a sample of state mandates. Now, fire protection is not just fire suppression, but I wanted to start on the fire suppression side and look at this in detail since it’s the suppression side of delegated design that seems to be the most pervasive issue today. A comparison of the joint-position statement (ABET, AFAA, AFSA, ASCET, FSSA, NCEES, NFSA, NICET, NSPE, SFPE) and several state statues for minimum requirements of fire protection engineering documents. In this list we find a lot of should-be-obvious things. Identifying the scope of work. Ask your favorite contractor – how many drawings have you seen for a renovation or an addition that doesn’t cleanly identify what work is actually supposed to be done? Are we scrapping everything? Are we going in all-new? Are we just add and relocating sprinklers? Hazard Classifications & Design Criteria. This one is the hammer to the head. It’s the most-important decision for the design of a suppression system. What is the hazard? What design criteria do we need to protect it properly? Again going back to your favorite contractor – how many times have you had projects where hazard classifications weren’t even identified? Or, the only place it is addressed is with a paragraph about Light Hazard and Ordinary Hazard in the specification while completely ignoring the huge storage area that’s part of the project? Water Supply. Every state and the position statement all agree that water supply is an upfront, engineering document responsibility. Ask your contractor – how often do they see it? ASK YOUR FAVORITE CONTRACTOR As an industry – as a collective – we’re failing right now. And I don’t want to pretend that I’m above scrutiny. Ask someone who’s looked at my documentation. It’s not perfect. I’ve failed to meet this mark. But I can be better – we all can. This has to improve, and I think we can build up the support and resources around this topic to make it happen. YOUR TAKE This is the first look at simply “what should be in a set of fire protection engineering documents”. What should they be? If you have input – tips, comments, thoughts – join the discussion below. If you work in other areas – Louisiana, Arizona, wherever – that have state-level mandates for fire protection engineering documents – let us know below! Having a representative summary helps everyone. Thanks for reading – hope the research we’ve compiled this week helps you think about how we as a whole can improve the way we practice. |