Standpipes for Fire Suppression: An Introduction

6/6/2019

 
Hope your week is going very well.

This week I'd like to open a short series on standpipes. Today's article is a basic overview of some basic requirements associated with standpipes used for fire suppression.

Fire Standpipe
Basic components of a standpipe for fire suppression.
Purpose
Standpipes are used to support manual firefighting efforts by delivering water to hard-to-reach areas of a building. The intent of a standpipe system is to avoid having to distribute and connect hundreds of feet of hose for a single interior attack by firefighters.

Hard-to-reach areas of a building aren't confined to one direction. Buildings which are very tall (highrises) or are deep underground, or are very wide by nature could all have portions of the building which would be difficult to reach.

Applicable Codes & Standards
In the US, the International Building Code (IBC) and International Fire Code (IFC) are often the first stop for standpipe requirements. While the two codes mirror each other, the International Building Code requires standpipes based on:
  • height (a story located more than 30 feet above the lowest level of fire department access, or 30 feet below the highest level of fire department access) (see IBC Section 905.3.1)
  • unsprinklered assembly occupancies (see IBC Section 905.3.2)
  • covered and open mall buildings (see IBC Section 905.3.3)
  • stages (see IBC Section 905.3.4)
  • underground buildings (see IBC Section 905.3.5)
  • helistops and heliports (see IBC Section 905.3.6)
  • marinas and boatyards (see IBC Section 905.3.7)
  • rooftop gardens and landscaped roofs (see IBC Section 905.3.8)

Once it has been determined whether a standpipe system is required or not, the IBC and IFC defer to NFPA 14 to prescribe how the system is to be installed.

Standpipe System

Class of Standpipes
Standpipes can be classified in several areas. The first is the class of standpipe, which relates directly to the hose connection type and the intended user. Based on 1-1/2 inch hose failures and the associated testing that goes along with them, 1-1/2 inch hose stations are much less common today.

I've found many situations with sprinklered buildings where hose stations have been removed as they are no longer required and are a burden for testing and maintenance. Here are the standpipe classifications, with Class I being by far the most common in the US today:
  • Class I: provides 2-1/2 inch (64 mm) hose connections for fire department and trained use.
  • Class II: provides 1-1/2 inch (38 mm) hose stations to supply for building occupants or initial fire department response
  • Class III: provides 1-1/2 inch (38 mm) hose stations for building occupants and 2-1/2 inch (64 mm) hose connections for fire department and trained use

Types of Standpipe
The other defining description for standpipe is when water is delivered, and at what relative pressure. Types of standpipes include:
  • Automatic dry: normally filled with pressurized air where water is delivered automatically when a standpipe hose cap is removed. The water, when delivered, is capable of supplying the system demand.
  • Automatic wet: normally filled with water capable of supplying the system demand automatically.
  • Manual dry: normally filled with air and without a permanent water supply. Water is required from a pumper truck in order to meet system demand.
  • Manual wet: normally filled with water that is not at a pressure capable of supplying the system demand. Manual wet systems require  water to be pressurized by a fire department pump in order to meet system demand.


Components of a Vertical Standpipe
Standpipes are not always vertical standpipes, but for multi-story buildings they are the most prevalent and are the topic of discussion this week.

Flexible Coupling
  • Purpose: Flexible couplings are included near floor levels to prevent catastrophic damage to the suppression system from the building structure while the building structure is moving in an earthquake. Flexible couplings allow the vertical pipe within a standpipe (or sprinkler system) to tolerate the horizontal building movement and still stay connected.
  • Where Required: Within 12 inches above and 24 inches below floor level in multi-story buildings. [NFPA 13 2002-16 9.3.2.3(2), 2019 18.2.3]
  • When Required: When the building requires seismic protection (seismic design category C, D, E, or F). Couplings are also provided at each floor level (often just above the floor level) to aid in installation.

Isolation Valve
  • Purpose: Standpipe isolation valves allow shutdown of a single standpipe without interrupting the water supply to other vertical standpipes. This can play an important role with maintenance, repair, modification, or during active firefighting scenarios.
  • Where Required: Isolation valves are required on all standpipes (including dry standpipes). [NFPA 14 2003 6.2.2, 2007-19 6.3.2]

Penetration Clearance
  • Purpose: Clearance around floor penetrations are important for seismic bracing, again to prevent damage to the system from the building structure during an earthquake.
  • Size: The diameter of the hole or sleeve must be 2-inches larger for pipes 1 to 3-inches in diameter, or 4-inches larger than the pipe for pipe 4-inches or larger in diameter. [NFPA 13 2002-16 9.3.4.2 and 9.3.4.3, 2019 18.4.2 and 18.4.3]
  • Where Required: Where pipe passes through platforms, foundations, walls or floors, except where flexible couplings are located within 1-foot of each side of the penetration. [NFPA 13 2002-16 9.3.4.5, 2019 18.4.5]

Pressure Gauge
  • Size: Not smaller than ¼-inch (6 mm). [NFPA 14 2003 5.6.1, 2007-19 5.5.1]
  • Where Required: For standpipes, a pressure gauge is required at the top of each standpipe. [NFPA 14 2003 5.6.1, 2007-19 5.5.1]

Riser Clamp
  • Purpose: Riser clamps are used to provide support to vertical pipe.
  • Where Required: Within 24-inches (610 mm) of the centerline of the riser, to support the riser horizontally. In multi-story buildings, riser supports are required at the lowest level, at each alternate level, above and below offsets, and at the top of the riser. [NFPA 13 2002 9.2.5.3.1, 2007-16 9.2.5.4.1, 2019 17.4.5.4.1] Support above the lowest level to prevent movement upward when flexible fittings are used. [NFPA 13 2002 9.2.5.3.2, 2007-16 9.2.5.4.2, 2019 17.4.5.4.2]

Standpipe Hose Connections
  • Purpose: To provide a point of connection for firefighters to connect hoses and get water to manually fight the fire.
  • Where Located: At 3-feet (0.9 m) to 5-feet (1.5 m) above floor level. [NFPA 14 2003 7.3.1, 2007-19 7.3.1.1]
  • Where Required: We’ll explore this in greater detail in the articles to come. There's volumes of information about these requirements, but for reference be sure to check NFPA 14 2003-19 7.3.2-7.3.4 and IFC 905.4-905.6.

Want to follow the rest of this series, or know someone who might be interested? Subscribe here.
Juan Saenz
6/26/2019 07:44:45 pm

The contents of your blog have become a transcendental source of information to educate myself and get to know more about the industry.

Thank you so much for taking the time to keep updating your website and adding new topics for further discussion.

The content is very interesting and useful!


Justin Stirling
11/8/2019 08:27:16 am

Can someone explain the process for determining if a standpipe system needs to be designed for seismic considerations?

Iakovos Sismanoglou link
12/16/2019 01:23:23 pm

Hello,

Thank you for your article, it's very helpfull.

However I have 1 big question:

WHERE EXACTLY IN THE IFC OR IBC OR NFPA SAYS THAT THE STANDPIPE RISER MUST BE VISIBLE OR UNOBSTRUCTED?????
Is there anything anywhere that prohibits me of sheetrocking that standpipe riser or installing inside a wall??? Ofcourse the hose outlets will be exposed but what about the riser???

Margaret
5/20/2020 10:29:23 am

Are isolation valves allowed to be installed after dry valve?


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT