MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Extending Dry Sidewall Reach Just Beyond 20-ft

2/7/2024

 
Have you had a project with an overhang that needed sprinkler protection and extended just beyond the throw of a dry sidewall sprinkler?
 
It’s a smooth, flat or nearly-flat overhang that’s, say, 21’-6” wide, and in an environment that will dip below 40 degrees F at some point.
 
What are your options then?
 
OPTIONS
All of the extended coverage dry sprinklers we know on the market cap out at 20’-0” horizontal throw. That would have been our best option.
 
We could look at using a dry system. There’s the additional cost of the valve, slope requirements, a hit on the remote area size, more corrosion potential – and on and on. It’s costly.
 
We could look at an anti-freeze system. Those come with more restrictions than they used to, but at a minimum would involve an RPZ and now pre-mixed antifreeze solution. Additional cost.
 
Heat trace the pipe? That’s problematic, at best. It needs to function 100% of the time that it’s needed, or pipe will freeze. It needs to be supervised. It needs to be maintained. And when in conjunction with pipe insulation it looks terrible.
 
In short, an overhang that’s just beyond the reach of a dry sidewall sprinkler can take us to a whole new cost tier in the design of a sprinkler system.
 
CODE-COMPLIANT CREATIVITY
We had just this situation on a project a few weeks ago, and tried to think creatively to get a code-compliant solution that’s best for the owner, yet doesn’t spike the cost for a dry sprinkler system that only serves four sprinklers.
 
Now normally, sprinkler design tends to be a one way street. An architect designs a building. It gets bid and handed down to the sprinkler contractor. The sprinkler contractor “makes it work” with what they’ve been given.
 
If a consultant is on-board, this would be a great opportunity to pick off challenges like this and advice the architect and owner on ways to mitigate this cost spike for a small project. Perhaps the overhang is designed at 19’-6” instead of 21’-6”. Perhaps they build it with all non-combustible materials if it otherwise didn’t have storage below.
 
Those could be helpful changes that reduce the overall cost in a major way, but may not be a major detriment to the owner’s goals for the building.
 
#1 SHORTEN THE OVERHANG
Regardless, we suggested that the width of the overhang be actually shortened to allow a sidewall’s throw to cover the distance and prevent the need for a whole dry system.
 
That didn’t go anywhere.
 
#2 EXTEND THE REACH OF A DRY SIDEWALL
We then asked if a soffit could be built to allow a sidewall it’s spacing of no more than 20’-0”.
 
The soffit wouldn’t have to be heated. It could simply be framed (hopefully of non-combustible studs) with sheetrock or a “Hardie Board” or some other skin. It could be almost completely empty on the inside.
 
The goal would be to give a dry sidewall sprinkler a back to collect heat and be installed properly.
 
KEY RULES
There’s a few notable rules that come into play here, though.

  1. Extended coverage sidewalls need to be within 6” (150 mm) of the wall which they are mounted (Section 11.3.5.1.2.1, NFPA 13 2022 Edition).
  2. If the soffit is more than 8-inches (200 mm) in width, then a sprinkler is required below the soffit (also Section 11.3.5.1.3.1, NFPA 13 2022 Edition).
 
So working backwards, a soffit that is say, 2’-0” wide and 2’-0” tall would allow a dry sidewall sprinkler to:
  1. be mounted to the side of the soffit within the 6” of the ‘wall’ which it is mounted,
  2. allow the height of the sidewall to be 6” from the deck above,
  3. allow the dry sidewall length to be long-enough to have the dry barrel run all the way through the width of the soffit and extend into the warm heated interior space, and
  4. limit the throw distance of the dry sidewall to less than it’s maximum of 20’-0”.
 
But then, we need coverage below the soffit too, right?
 
This could be accomplished with a flexible dry pendent, such as the V3517 dry flexible pendent sprinkler. Just like the dry sidewall, the flexible dry pendent could contain water back on the warm interior space.

Picture

DIGGING DEEPER
We also would want to offset these locations on plan, so a pendent isn’t immediately under a dry sidewall. Offsetting the locations in plan could help potential cold-soldering concerns.
 
We’d also want to be sure that both the dry sidewall and the dry flex pendent would be able to be replaced at some point in the near future. NFPA 25 used to require sample testing or replacement every 10 years starting at 10 years after installation, but the 2020 edition bumped that starting point up to 15 years and the 2023 Edition bumped it again to 20 years after installation (NFPA 25 2017-20 Section 5.3.1.1.1.6, 2023 Section 5.3.1.1.1.5).
 
To accommodate replacement and testing, we might need a way to get access to the inside and the soffit in the future (access panels or future cutout).
 
COST & CONSEQUENCE
After all this effort – will the soffit cost more? Sure.
 
Would it cost as much as a dry or anti-freeze system? No, it shouldn’t.
 
Does it help with corrosion and IT&M in the future, considering we wouldn’t have a dry valve and an additional nitrogen system or air compressor? Yes, that’d help too.
 
Just an idea that might help address those “in-between” situations that could spike cost for a smaller-sized project that otherwise wouldn’t need it.

What are your thoughts? Have you tried this before? What tips would you suggest?
 
Hope you’ve found this interesting and perhaps moderately helpful, and I hope you have a great rest of your week!

Leaders in Flexible Drops

8/31/2016

 
Two weeks ago we covered Benefits and drawbacks of flexible sprinkler drops, and last week we covered Considerations with flexible sprinkler drops. This week we offer a summary of industry leaders in the U.S. market with flexible drop technology. Know someone we're missing? Contact us so we can be sure to provide a thorough summary.
Summary of Leaders in Flexible Drop Technology in the U.S. Market
Having trouble viewing? This table best appears on www.meyerfire.com. Click the link to view.
Supplier
Lengths (inches)
Approvals​
Max. Sprinkler K-Factors
Bend at Nut?
Max 90 Deg. Bends (applicable sizes)
Min. Bend Radius
Source / Website / Pressure Loss
EasyFlex
24, 36, 48, 60, 72
UL/FM
K5.6 for 1/2" outlet (UL/FM)
K8.0 for 3/4" outlet (UL/FM)

No bend within 2.52 inches from connection nut
1 (24)
2 (36)
3 (48)
4 (60, 72)
4 inch (UL)
8 inch (FM)

Link
FlexHead
24, 36, 48, 60, 72
UL/FM
K5.6 for 1/2" outlet (UL/FM)
K14.0 for 3/4" outlet (UL/FM)
K22.4 for 1" outlet (FM)

No limit
3 (24, 36)
4 (48, 60, 72)

3 inch (UL)
8 inch (FM)

Link
Sidewinder
30, 48, 60
FM
None Listed
Not within 2.5" of connection nut or reducer
3 (30, 48, 60)
6 inches (FM)
Link
SprinkFlex
28, 40, 48, 59, 71
UL/FM
K8.0 for 1/2" reducer (UL)
K11.2 for 3/4" reducer (FM)
K5.6 for 1/2" outlet (FM)
K8.0 for 3/4" reducer (FM)
Not within 2" of connection nut
2 (28)
3 (40, 48, 59, 71)

3 inch (UL)
8 inch (FM)

Link
​VicFlex
31, 48, 60, 72
UL/FM
K8.0 for 1/2" reducer (UL)
K14.0 for 3/4" reducer (FM)
K5.6 for 1/2" outlet (FM)
K14.0 for 3/4" reducer (FM)
No limit
3 (31)
4 (36, 48, 60)
5 (72)

2 inch (UL)
​7 inch (FM)
Link
If you find this information helpful and think someone you know might benefit, please send them a link to our Blog and ask them to subscribe. We grow and share information among experts through word of mouth by our subscribers.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT