MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Fire Sprinklers and Overhead Doors: A Love Story

1/30/2019

 
I've heard that in order to publish on the internet all blog post titles must have a gripping click-bait title. This was my best attempt. Sorry to disappoint, but there is no love story here.

Things are back on track this week - the last got a little busy at home last week when my wife and I welcomed our third child to the family. Even with the third, it's amazing how much joy and motivation kids can bring with their arrival. 

Needless to say I didn't have a whole lot of productivity last week, but I'm very glad you've tuned in. This week we're exploring requirements and challenges of sprinkler protection near overhead doors. 

Where Required

​Sprinklers are required under "fixed obstructions over 4 ft (1.2 m) in width." (NFPA 13 - 2002-16 8.5.5.3.1, 2019 9.5.5.3.1)

One common application for this code section is overhead doors in the "open" position. Annex material even specifically references overhead doors as an applied example of this requirement.

Sprinkler Protection Beneath Overhead Door
Sprinklers are required where the horizontal projection of an overhead door exceeds 4-feet.
Application of the 4-ft Obstruction Rule

If the overhead door doesn't create an obstruction over 4 feet (1.2 m) in width, then a sprinkler is not required to be provided beneath the door. This dimension is typically applied in the horizontal dimension only, and is measured as the horizontal projection of the edge of the door away from the wall.

Depending on how creative things want to be architecturally, sprinklers can be avoided beneath overhead doors when the door assembly doesn't create a 4-foot horizontal obstruction. This can be the case with small coiling doors, door tracks that only run vertically up a wall, or a combination of vertical and horizontal tracks that don't project more than 4 feet out away from the wall.

Hanger & Supporting Challenges

​NFPA 13 does not specifically address support for sidewall or upright sprinklers below an obstruction, but similar requirements can be extracted from criteria on pendent sprinklers served by branch pipe above a ceiling.

If a sprinkler's horizontal steel branch pipe feed is greater than 1'-0" for systems with 100 psi or more, or greater than 2'-0" for any steel system, then a hanger is required to support the armover (NFPA 13 2002-16 9.2.3.4, 2019 17.4.3.4).

This presents a natural challenge as the door track is typically only designed to support the forces of the door and is not considered to be building structure capable of supporting the sprinklers, pipe and fittings. While it's very common for installers to attach the hanger to the door track, many see this as a violation of the hanging rules of NFPA 13.

Fire Sprinkler Protection Beneath Overhead Door
Supporting sprinklers beneath the overhead door can be a challenge due to the height differences between the door and the ceiling/roof structure above.

Drainage & Dry Systems

Protection beneath overhead doors ramps up to another level of difficulty when used in dry systems. If a sprinkler beneath an overhead door on a dry system traps water, there needs to be a means to drain the trapped water and for dry systems in an unheated area, would require an auxiliary drain and drum drip.

While this might not present a challenge with a single overhead door, multi-bay vehicle buildings could wind up having a low-point drum-drip for every or nearly every other overhead door.

Aside from the cost, these drum drips are a maintenance nuisance as failure to drain these on a regular basis could result in a freeze and rupture of the drain assembly.

New Guidance on Sprinkler Position & Types Below Obstructions


Fortunately - in an update that I find very helpful - the latest edition of NFPA 13 now addresses where sprinklers can be located beneath obstructions.

Sprinklers are required to be either located beneath the obstruction, or with their deflector no more than 3 inches off the side of the obstruction (see below). This was clarified in 2019 based on fire testing & research.

NFPA 13 sprinkler obstructions
New guidance for sprinkler protection beneath obstructions - new to the 2019 edition of NFPA 13.

Where a sprinkler is adjacent to the obstruction and not directly beneath, it must be an "intermediate-level rack type" (NFPA 13 2019 9.5.5.3.1.3). These sprinklers are provided with a shield that prevents inadvertent cooling from sprinkler discharge above (the shield is ineffective and not intended to help "collect" heat).

Your Challenges?

What tips & tricks have you come across when dealing with sprinkler design around overhead doors? This site is created to start the discussion. Add your questions, tips & tricks in the section for your comments here.

Subscribe

Find this article interesting? Get more of my weekly articles & resources, for free, by subscribing here.
Karl B.
1/30/2019 01:49:09 pm

Mr. Meyers, first & foremost: congrats to you & your wife on your recent arrival!

I have often wondered why the issue of a sidewall sprinkler being placed below the overhead door is not considered to be in violation of the requirement of a sidewall sprinkler distance off a wall. Understanding that a sidewall would cover a large area without the pipe becoming an intrusion, if the design permits, does NFPA-13 allow the use of uprights below the overhead door? & yes, hanging certainly can be a challenge (keeping in mind that installing hangers can be a substantial part of overall project labor).

JOE MEYER
1/30/2019 02:02:01 pm

Thanks Karl! Much appreciated.

I suspect that any of the sprinklers submerged in the same position in a hot plume would activate similarly, independent of the sprinkler orientation (pendent, upright, or sidewall) - but that's a gut feeling more than a researched standpoint.

Using a sidewall has the benefit of using one less elbow while also extending the throw across the width of the door, which I'm sure is why they're commonly used below overhead doors.

That being said, I'd be interested in researching the backhistory on why the sidewall distance requirements off a wall exist.

Joe

Gregory Bartels
1/31/2019 08:33:33 am

Nice article, with good points.

In my field experience, I have seen the overhead door track used as a point of attachment for a hanger for the sidewall sprinkler piping. I have installed a few myself back in the day. We knew it didn't meet the criteria per NFPA 13 for a point of attachment for a hanger, but it was one of the things you did, because "everyone" is doing it, I guess. However, the hanger installed on the door track for us was not the primary hanger used to support the assembly, there was a hanger attached to structure at the top of the armover to the drop The bottom hanger was for added strength to keep forklift drivers from knocking it out of position.

If the system was a a dry pipe, and you need to drop down to cover the overhead doors, there would be a trapped section of pipe, which does make it a pain to add drains and service them, a maintenance concern, as you noted. I think in most cases, our drops were less than 5 gallons, so you could get away with a 1/2" or 1" valve, and not a full drum drip assembly. Still a big concern to make sure all were drained and checked to prevent freezing.

If you need protection under the overhead doors with a dry/preaction type system,, my suggestion would be to pipe lower hanging lines with uprights under the doors. Pitch them good to drain, adding a drum drip at lowest point, if you can't slope back to a low main. The customers sometimes complain about "low hanging" pipe, but they aren't losing that much height if done correctly, and it's better than a freeze up..

The best solution, is to talk the customer into "roll up" or sliding doors, with nothing to cover in the open position.

Gregory Bartels
Local 669 Instructor

John Kupcha
3/2/2019 11:46:02 am

I was a bit skeptical of the accuracy of the sprinkler head requirement with overhead doors. So I did some research of NFPA 13 and which has the overhead doors listed as a n obstruction. However, This was fact until I seen in NFPA 13R - 2013 Section 7.3 "Design Criteria - Garages. In Paragraph 7.3.2.1 it specifically states "Garage doors shall not be considered obstructions and shall be permitted to be ignored for placement and calculation of sprinklers". To make this even more interesting, in just 2 paragraphs down in paragraph 7.3.3.3 it states "Garage doors shall not be considered obstructions and shall be permitted to be ignored for placement and calculation of sprinklers." Yes, it repeats itself word for word.

makautomaticdoors link
4/18/2020 02:26:46 am

Its a really nice website. Thanks for giving full information about Sectional Overhead Doors.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT