How to Determine Fire Flow (IFC Method)

3/6/2019

 
Determining fire flow can be a tricky subject. This week I'm breaking down one common method of determining fire flow requirements and hopefully exposing some myths about the process.

Not an Exact Science

First, determining the exact amount of water required to manually suppress a fire is dependent upon so many variables. The amount of water used could depend on the building size, hazard, outdoor conditions, speed of fire growth, fire department response time, whether the building is protected by sprinklers, and on and on.

The methods used to calculate fire flow are different methods at estimating the amount of water required to manually suppress a fire. It is not an exact science.

What is Fire Flow?
​

I'll start by what fire flow is not. Fire Flow is not the volume of water required for the fire sprinkler system. I couldn't count the number of projects where Fire Flow has been assumed to be sprinkler-related.

​Fire Flow is formally defined as the "flow rate of a water supply, measured at 20 psi (138 kPa), that is available for fire fighting." (IFC 200-2018 Appendix B Section B102)
Fire Flow
Fire flow is used to determine the quality of a water supply to an area. It's used as an aid to determine pipe size and arrangements to delivery water to a specific area.
​Fire Flow is important for emergency response at it is the total capacity of the system that the fire department has available for use in response to a fire.

How Is Required Fire Flow Determined?

In short - it depends.

There are many methods for determining fire flow. The most common cited in US circles include the Insurance Services Office (ISO) Method, Iowa State Method, and the Illinois Institute of Technology (IIT) Method. At least a dozen other methods exist (for more on these, the Fire Protection Research Foundation provides great analysis in Evaluation of Fire Flow Methodologies research paper).

The International Fire Code (IFC) offers Appendix material that provides guidance for determining the required fire flow, which is based on the ISO Method. It is not a mandated code requirement unless a jurisdiction adopts the Appendix.

Many jurisdictions I've worked with do not have an ordinance that adopts the appendix, but when asked they are typically open to using the IFC Appendix B method of determining fire flow. The International Fire Code, which is widely adopted in the US, only requires that an approved water supply "capable of supplying the required fire flow" be provided to buildings.

This process will be explored in more detail here.
​
1. Determine Baseline Fire Flow

The first step in this overall determination of water supply to a site is to determine the required fire flow.

Using the IFC Method, Appendix B has a reference table that stipulates a minimum fire flow and flow duration based upon building size and construction type (2000-2012 Table B105.1, 2015-2018 Table B105.1(2)).

2. Reductions & Increases

Once a baseline value for flow and duration is taken from the table, it can be reduced based on the presence of sprinkler system.

Section B105 details the adjustments that are available for buildings with a sprinkler system. A reduction of up to 75% can be permitted for buildings with a fire sprinkler system.

It's important to note that up through the 2012 edition of the International Fire Code, a reduction of fire flow had to be approved, meaning the AHJ must agree on the reduction. This may not make a difference if a jurisdiction hasn't adopted the appendix and the entire calculation has to be approved anyways, but in the case where Appendix B is adopted and you're under IFC 2000 through 2012, you'll need AHJ buy-in to use the reduction.

The 2015 and 2018 edition of IFC removed the approval necessity for sprinkler flow reductions.

As part of this process the Fire Chief is also authorized to decrease the required fire flow, based on building isolation or impracticality. Alternatively, the Fire Chief is also authorized to increase based on unusual susceptibility for the facility. These stipulations come with Section B103 of Appendix B (all editions).
Fire Flow
Fire Flow is used to quantify the available water supply for manual firefighting operation.
3. Verify Provided Fire Flow 

The best way to verify fire flow for a location is to conduct a flow test at the site itself. This of course can be difficult to impossible for new-construction projects on virgin sites. 

For developed areas or building expansions, this may not be difficult to accomplish.

I have a current project we're working on that is a major building expansion. Fire flow needed to be assessed based on the new expanded building and whether a single 8-inch feed would still meet the minimum requirements. A flow test on the site itself confirmed that we are just short of required fire flow which prompted a healthy discussion with the AHJ.

4. Calculate from Flow Test to Site (if necessary)

Sometimes a flow test can't be conducted on the site itself. 

When this is the case, a hydraulic calculation can be run between the water supply source (nearby flow test, a water tower, reservoir, or pump) and the project site to estimate what the available fire flow will be. This calculation incorporates the pressure loss of the pipe network as water is constricted between a source and a project site. The best way to confirm actual fire flow (in my opinion) is to verify with a flow test once any extension is installed. 


Easy Tools for Fire Flow & Water Supply Analysis

There's a new tool in the arsenal around here that directly addresses fire flow requirements.

It's the Fire Flow Calculator that's now a part of the Toolkit. If you're already a Toolkit subscriber, download it today.

​The Fire Flow Calculator uses the IFC method based on your project parameters to quickly grab the baseline fire flow and duration, and make adjustments for sprinkler protection. Now you have extremely quick access to determine required fire flow, and the documentation to support your process.

This is a tool I'm happy to debut and have used with great client feedback.

​On a side note, Toolkit subscribers also now have access to last week's Design Checklist with user-provided feedback. The download update includes both tools. Give them a download and let me know what you think!

Subscribe

Don't get these weekly articles? Subscribe here and get a free guide for canopies & overhangs.

< PREVIOUS
NEXT >
TL501 SERIES:
  1. What is the Sprinkler Database?
  2. How to Use the Obstruction Calculator for Beams?
  3. How to Use the Obstruction Calculator for Soffits?
  4. How to Use the NFPA 13 Translator?
  5. What is Driving Design; the K-Factor or Density?
  6. How to Estimate Clean Agent Quantities?
  7. How to Calculate a Domestic Demand?
  8. How to Select an Optimal K-Factor?
  9. How to Quickly Calculate Friction Loss?
  10. How to Analyze Fire Pump and Water Supplies from a "Big Picture" perspective?
  11. How to Determine Fire Flow with the IFC Method?
  12. How to Quickly Estimate Hydraulics for a Sprinkler System?
  13. How to Estimate a Water Storage Tank Size?
  14. How to Calculate Hanger Spacing by Weight?
  15. How to Calculate the Size of a Trapeze Member?
  16. How to Summarize Notes for Fire Alarm and Suppression?
  17. How to Calculate Thrust Block Size?
  18. How to Quickly Classify Combustible & Flammable Liquids?
  19. Calculate the Volume & Air Compressor Size for a Dry System?
Dwight H Havens
3/12/2019 11:07:40 am

Good blog putting fire flow requirements providing the why on the level that most business owner/developers can understand.

Unfortunately, Appendix B has not specifically addressed fire flow requirements for the multi-story stick-built (Type V) with NFPA 13R systems.

Mitch Hart
4/15/2019 10:03:48 pm

I was needing a little help validating the methodology for fire flow requirements in my city. They do not allow you to verify fire flow per #3. Conducting a flow Test. Our city always uses hydraulic calculations to determine acceptable flow in an area. However, in their hydraulic model they always assume that the water usage that day is 19,000,000 million gallons which was established by taking the highest usage in the history of our community of all time, which occurred in 2012 when we had 30 plus days of 100 degree weather of 18M gallons and adding a 1Million to that. Our average daily usage in our community is around 10 to 11 million gallons per day. Anyway, the local engineers say that methodology is consistent with the International Fire code. What are your thoughts? Thanks Mitch Hart 501 626 2121. I would love to know what the IFC requires.

Joe
4/16/2019 06:12:12 am

Mitch,

Great point for discussion.

I've posted this question in the Daily Forum page here: https://www.meyerfire.com/daily/how-to-best-determine-the-available-fire-flow

Rob
4/24/2019 11:11:53 pm

You mentioned that the IFC is based on the ISO Method, how close are they and can you provide any more background on that? If a building meets IFC, would you expect it score very well under an ISO evaluation?

JOE
4/25/2019 05:50:36 am

Hi Rob,

Great question. I've opened this up for dialogue and hope to explore it in more detail here:

https://www.meyerfire.com/daily/fire-flow-international-fire-code-vs-iso-method

prachod
4/25/2019 08:51:13 am

As mentioned in your blog "'Using the IFC Method, Appendix B has a reference table that stipulates a minimum fire flow and flow duration based upon building size and construction type (2000-2012 Table B105.1, 2015-2018 Table B105.1(2))"'. There is similar table in NFPA 1 which shows minimum fire flow and duration based on building construction and area only. However, there is no credit given to the commodity or occupancy hazard in the building. In this way, we are treating steel work shop (any light hazard) and high plastic storage (high hazard) with the same fire flow requirements.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT