Things around here are always busy. The past few weeks have been no exception. With feedback from some Apple users, field-users, and those without Microsoft Excel - I've heard your pleas! We now have every single tool from The MeyerFire Toolkit now available online to subscribers! You can see the complete list of tools at www.MeyerFire.com - just hover over the "Tools" list. Now, you don't need Excel or a Microsoft operating system - access the quick tools you need from anywhere, anytime. Not a Toolkit subscriber? Join on here. Licenses are now multi-user so you can share these tools with your whole team. SFPE Atlanta March 10th & 11th If you're attending SFPE Atlanta's regional conference on March 10th & 11th - let me know! I'll be there for John Frank's daylong session on updates with the Fire Protection PE Exam. He's the longtime leader of SFPE's Online PE Review Course and we'll be doing some collaboration in preparation for the computer-based changes to the PE Exam in 2020. NFSA Annual Conference April 29th - May 1st If you'll be in Phoenix for NFSA's National Conference - check us out! I'll be teaming with the voice of the fire sprinkler industry - Fire Sprinkler Podcast's Chris Logan to speak on New Media in Fire Protection. In Phoenix we'll be dissecting what we've learned while starting up different media in the industry, what projects we're working on now, and what ways we all can capitalize on new opportunities in the media space. That presentation is set for Wednesday April 29th. Making the Jump - The New Consulting Practice For all those who have reached out on LinkedIn about my (relatively) recent jump into starting my own design practice - thank you!! Things have been very busy with a healthy amount of fire sprinkler shop drawing design & consulting work. If you have interest in following the work I'm doing as part of that endeavour, follow my updates here: https://www.linkedin.com/company/meyerfire/. There's a fresh video on a recent all-BIM sprinkler design. If we're not yet connected on LinkedIn, consider doing so. It's GREAT to hear from and chat with other passionate people about the fire protection industry and it's something I really enjoy.
As always, thanks & have a great rest of your week! While being located geographically in the middle of the United States, it may not seem like seismic bracing would be a major concern. After all, we don’t have the frequency of intense earthquake movement that covers news headlines like the west coast experiences. Despite the (fortunately) absent frequency, the New Madrid fault line runs near Memphis, Tennessee up to the bootheel of Missouri. [Note: Yes, we Missouri-folk actually describe a portion of the state as a “bootheel”. When you say it aloud, though, you have to add a little twang.] Back to seismic – this fault line has the potential for very strong seismic activity just as much as portions of California and the Pacific Northwest. As a result, seismic bracing is common for us in southeastern Missouri, in St. Louis, and even into central Missouri and southwestern Illinois. As we move away from the fault line, at some point, seismic movement would be less severe – even to the extent that bracing isn’t necessary. Where is that point? How do we determine when seismic bracing is necessary for fire suppression systems? Today’s article is covering just that. It’s an exercise I practice commonly as I essentially live on the boundary of where seismic is and is not required by code. International Building Code References ASCE 7 Seismic bracing has roots in NFPA 13. As is the case between a “code” and a “standard”, however, NFPA 13 as a standard only tells us how to design and install the system. Code tells us when and where systems and components are required. The International Building Code Section 1613 for Earthquake Loads requires that “every structure… including nonstructural components that are permanently attached to structures and their supports… shall be designed and constructed to resist the effects of earthquake motions in accordance with ASCE 7”. [2015 Edition 1613.1] There are a few exceptions, most notably detached one- and two-family dwellings in some areas. ASCE 7 Requirements Based on Seismic Design Category ASCE 7, Chapter 13 (2010 Edition), for Seismic Design Requirements for Nonstructural Components, states: ASCE 7 Chapter 13 addresses Seismic Design Requirements for Non-Structural Components. Its scope covers the minimum design criteria for nonstructural components (like fire suppression systems) that are attached to the structure. ASCE 7 Chapter 13 suggests that seismic bracing is required for all structures, unless they meet an exemption. Section 13.1.4 specifically lists exemptions from seismic design requirements. These Exemptions include:
Additionally, ASCE 7 Section 11.7 states that Seismic Design Category A need only comply with Section 1.4 (not Chapter 13). So What is a Seismic Design Category? A Seismic Design Category is a “classification assigned to a structure based on its Risk Category and the severity of the design earthquake ground motion at the site.” (ASCE 7 Chapter 11 Definitions) In short, it’s a classification on the entire structure, ranging from A (least risk) to F (greatest severity). Seismic Design Category A structures encompass buildings of ordinary occupancy located on sites with stiff soils and have little risk of experiencing earthquakes. Seismic Design Category F, on the contrary, are required to remain functional following a strong earthquake, such as hospitals and emergency communication centers, and are located very close to major active faults. What Impacts Seismic Design Category? Several contributing factors are combined to give the seismic design category. They principally include:
Structures that are of high importance following an earthquake, such as a hospital, are of greater importance and carry a higher risk category. Soil conditions greatly impact the ability of the building to response to motion. Stiff soil or rock conditions generally allow the building to better respond to an earthquake. Loose soil, or soft clay don’t give buildings the ability to move with the ground, and therefore create worse seismic reaction forces within the building. Lastly, and probably the most obvious, the building’s proximity to a major fault line. The closer to a fault line, the greater the seismic forces from an earthquake event for the same earthquake. How to Determine Seismic Design Category? The International Building Code Section 1613 allows the Seismic Design Category to be determined either by IBC 1613 or ASCE 7. The International Building Code Section 1613 details the step-by-step process to determine the Seismic Design Category. This involves using data from site soil testing, the Risk Category, and earthquake severity parameters from provided maps. ASCE 7 has similar provisions in Chapter 11, detailing similar inputs of Risk Category, Mapped Response Parameters, and site conditions. In practice, however, there are third-party tools that help make this process much easier. Here are a few available, for free online:
With the Risk Category, Address, and Site Information, a Seismic Design Category can be quickly determined for a building. These reports also give important design parameters that will be used for Seismic Calculations for the design of the system. What if I Don’t Know The Site Class? With new construction, structural foundation design requires geotechnical testing and reports which give these values. The structural engineer will assess the report, and typically place the building’s Seismic Design Category in their front-sheet notes or in structural specifications. This isn’t the case with interior remodels or work within existing buildings. No soil testing is done and sometimes no structural work is done. When this is the case, the International Building Code requires a Site Class D to be used (IBC 1613.3.2). This could be made more conservative by the building official if geotechnical data determines that Site Class E or F soils are present at the site. So Does My Building Require Seismic Design? Back to the original question – once we know the Seismic Design Category, it’s easy to determine where fire suppression systems require seismic design. If the Seismic Design Category is A or B, then Seismic Design Criteria does not apply. If the Seismic Deign Category is C, D, E, or F – then Seismic Design Criteria applies. Under this later scenario, all the requirements of NFPA 13 for Seismic Design now become an enforceable requirement for the system design. Here’s a summary of the code path: Summary
Seismic Design Criteria for Fire Suppression Systems depends upon the Seismic Design Category for the Building. This Seismic Design Category incorporates the importance of the building, it’s proximity to seismic fault lines, and soil conditions at the site. While the determination path through codes & standards might not be as clear as other system requirements, seismic design is nonetheless a crucial component for the performance of a fire suppression system and an important consideration in the design of the system. Like this article? Consider subscribing here. Already subscribed? Consider sharing with a colleague who might benefit from this. We love to poke fun at millennials. It’s like the holy grail of tradition. “Kids coming out of school these days – you know? It’s ridiculous. They want twice the pay and half the work of when I came out of school. They don’t want to learn. They’re lazy. There’s not enough talent. There’s not enough interest. They don’t work hard.” Ever heard that before? How about this one - “Young people think they know everything, and are always quite sure about it.” Yeah – that last quote wasn’t exactly about millennials – Aristotle wrote it in the 4th Century BC. Every young generation is clearly, obviously, unexplainably worse than the one before it. Right? I mean criticizing the next generation has been going on for all human existence. I’m sure cavemen used to scorn at how the young have no eagerness to strike rocks anymore… But Millennials. Millennials are so… entitled. Yikes. Yeah – I wrote it. Entitled. The worst label of all. That E word. So Entitled. Millennials are so entitled that they don’t even own their own issues; those are of course caused by Boomer parenting. [see the half a million search results for “millennial poor parenting” on Google]. I mean clearly millennials are like the worst young generation we’ve ever seen? Right? Back Off Another Joe/Millennial Soapbox OK. So maybe the problem isn’t that bad. Maybe I exaggerate a little. Maybe I write too much in the third person considering my age technically qualifies me as a millennial. And yes, maybe I do also blame my parents for all my nonsensical fears (thunderstorms and sinkholes, come on Mom!). I was probably accused of being entitled a couple years into my post-college career. I felt good about the work I was doing, felt like I was understanding the curve, and I am sure it was showing in my attitude. A couple big project issues plus a bad annual review and I was quickly sized back to reality. But entitlement doesn’t go away easily. It was around that time that some coworkers went to a career fair at an area state college. One of the college students (a junior) inquired about the company. He got the normal pitch on working culture, opportunity, training and the whole bit. He then asked about management positions. After laughing it off my coworker realized the student was serious. He was looking for a management position as a quasi-21-year-old with zero real world experience! After returning to work and sharing the disbelief, it’s easy to see entitlement in others when at that same time I probably couldn’t see it in myself. I did get over it though. It wasn’t through shame or being a “company guy” or bad annual reviews. It was by starting my own side-hustle. Takeaways from the Art Shop I had always enjoyed creating sketches. During college I had a few architectural studio courses where we learned architectural sketching traditions. I enjoyed drawing and took some of those lessons to open a small art shop online. That experience brought so many positive perspectives into my life. It started with only one sale in the first two months of opening. It was a wonderful feeling. Then one good review led to another sale in month three. In month four I had two sales. Month five I doubled again. With each touchpoint I worked on improving the customer experience. I learned quickly to be responsive to customers. I learned how to deal with unsatisfied customers – which meant putting frustrations aside and owning-up to every misstep. I learned how taxation is theft (ok not really – but it is a major downer). Probably one of the most important things I learned from the basic art shop is that I had to take ownership of the work result. It never mattered how hard I tried to draw. If I created something that offered no value to others, it wouldn’t sell and had no value. That’s the real-world economy. People pay for value. How was I to bring value to a customer? How could I improve the value I offered? How could my presentation and correspondence be improved to help convey value? I thought about all of those things, constantly. That also began slowly translating to the workplace. Just because I put in effort – if the end result was incomplete, sloppy or just wrong – then I was not producing value. The essence of entitlement is believing that showing up is enough. It’s not. The value we provide for the world is our all-in engagement with doing great work. Employee vs. Ownership Perspective Starting that art side-hustle slowly and fundamentally changed my perspective about business and serving people. As I see it – there exists an Employee and an Ownership mentality. An Employee mentality asks – “why doesn’t our company pay for X?”, “they underpay everyone here”, “they never pay for good software”, and on and on. The Ownership perspective is looking holistically at the business. “How can we better serve our clients?” “How can we improve work culture?” “How can we improve productivity?” An Ownership mentality links personal responsibility to their work and representing a brand. I didn’t have to have a stake in a company to begin to develop that perspective. Businesses exist to make money. If businesses didn’t make money for a long period of time, then they fold and cease to exist. That’s reality, and that’s not a bad thing either. But just adopting an Ownership perspective brings about a world of possibilities. Company limitations don't become obstructions - they just become a problem that needs a creative solution. That art business grew, and grew and grew. Just three years in I sold over 600 pieces in a year. Wild. Especially for an ameateur artist who's dayjob is being and engineer. That shop still exists at www.etsy.com/shop/artbyjosephdalton. There’s not much time into it anymore now that the fire protection content is top priority – but I’m so thankful I started that shop because the lessons it taught has been invaluable. Want to change your perspective? Start that side hustle you’ve always wanted. It just might unlock a fresh way of looking at the world. Enjoy this article? Here are other career-related articles: Being Deliberate About Your Future Does Your Job Title Matter? Knowledge is Not Just in Education Fahrenheit 451 & The Thirst for Knowledge Heartache of Failure in Life Safety Design Enjoy this? Consider sharing with a friend.
Last week we explored when duct-detectors are required under the International Mechanical Code (IMC). While the IMC is the most commonly-applied standard in the United States, it's not the only standard that dictates terms for duct detectors. Many international projects under NFPA 5000 or government facilities under Unified Facilities Criteria (UFC) pull in smoke detection requirements from NFPA 90A. This week's post covers a cheatsheet for duct-detection requirements under NFPA 90A. Selfishly I've been wanting a quick go-to when covering fire alarm design, and now I'll have a copy for the two most common standards. Around here we laminate cardstock color prints for these cheatsheets. If you'd be interested in purchasing a set of cheatsheets, let me know by commenting here. If there's enough interest I'll set up something in our store.
Thanks & have a great week! On every project containing fire alarm design I come across the same question repeatedly - does this unit require a duct detector? In short, there's two prevailing standards that determine whether duct detection is required. The first (and most common in the United States), is the International Mechanical Code (IMC). Section 606.2 identifies areas where smoke detection is required for the purpose of mechanical unit shutdown. The other prevailing standard is NFPA 90A, the Standard for Installation of Air Conditioning and Ventilating Systems. I'll address those requirements in a later post. Back to the question at hand - there's essentially six different scenarios a mechanical unit can fall into under the International Mechanical Code. These do not include the requirement for multi-level duct risers over 15,000 CFM, but rather whether an individual unit requires detection at the unit. Here is a quick cheatsheet summary concerning those scenarios: If you review or design fire alarm systems regularly, take a look and let me know what you think. If you know someone who might also benefit from cheatsheets like this, send them a link or tell them to subscribe here. Hope you find this helpful and have a great rest of your week! Design-specifications have had a tradition and sometimes contemptuous past in the world of fire protection design. Sometimes called “design-build spec”, “performance-specification”, “delegated design”, “deferred submittal documents”, “scope drawings”, or “design-spec”, these all mean relatively the same thing; the engineer is not providing a working submittal of how a fire suppression system should end up in the field. Back in 2008 advocacy groups from the Society of Fire Protection Engineers (SFPE), National Society of Professional Engineers (NSPE), and National Institute for Certification of Engineering Technologies (NICET) adopted a joint position on the role of the Engineer and the Engineering Technician as they relate to fire protection systems. A summary and full-length document are here. The position statement does a good job of identifying the relationship between engineering documents and a working shop drawing submittal. It maintains that the role of the Engineer is to support the proper protection of the public’s health and safety. A licensed Engineer is required to understand a broad sense of fire protection beyond just suppression, and also has specific state requirements for licensing and authorization. While the position statement does a good job of identifying roles and defining the relationship between an engineer and a technician, real-world experience says that many “design-build specifications” fall short on good practice. I’ll save my frustrations on the lack of quality engineering documents for another day (it is not a regional issue). There is a ton to explore on that topic. I will however offer up what I like to use as a practical checklist for design-build specifications. Not all owners want to pay consultants to flush out all the details of a system. I get it. But if an owner is paying for anything at all, then the documents should address basic requirements and cost-impacting elements of design. If a set of plans just outlines an area and says “per NFPA 13”, then someone isn’t doing it right.
This cheatsheet is a collection of the items I’m looking for when I help contractors bid jobs. It’s a shortcut to all of the items that have a design and cost-impact to a job. If you, as a consulting engineer, address every single one of these items clearly and within code, then pat yourself on the back my friend, you are a gift. If your documents don’t address each of these items (yes, including flow test information), consider making it a part of your regular practice. None of the items on this list are major time consumers, but by accounting for them you’ll allow better bidding from contractors and much less contention after bids are due. Please, please: don’t loft up vague project requirements to contractors and hope for the best. Invest in being a knowledgeable and quality practitioner of this great industry. It'll more than pay itself back to you. What are your thoughts? What type of bid documents are you used to seeing? Join the conversation and comment here. Awhile back I researched and built a translator for various versions of NFPA 13. It's built to quickly find where a code section has migrated between different editions of the standard. There's a free version here which connects the 2016 and the 2019 Editions of NFPA 13. Based on feedback and the positive response to that tool, I've just finished a similar edition translator for all of the published versions of the International Building Code. It covers Chapters 1 through 11, 15 and 30. Here's a quick video of how it works: If you're interested in giving this a try, you can get it as part of a 30-day trial for the MeyerFire Toolkit here. https://www.meyerfire.com/toolkit-trial.html. It's been busy around here tinkering with new tools since I went on my own in October of 2019. I am not by nature a programmer, but as the son of two accountants I'm pretty sure Microsoft Excel is just in my blood. I've gotten lots of positive feedback from users on the Toolkit and I'm happy to announce this week some major improvements aside from the new IBC translator: 1. A La Carte Tools Coming Some users aren't designers or engineers and would only use one or two tools. I get it. In the next couple weeks I'll be breaking out individual tools and pricing them for less, separately. The first one offered this way is the Water Supply Analysis tool that will be up this week. 2. Instant Activation Codes One of the biggest frustrations I've had on the development side is with quirky activation code servers. They drive me nuts. Over the past month I've dramatically simplified the process, so that new purchases automatically get clear activation codes exactly 2 minutes after their purchase. Clean and simple and it's working much better than before. 3. Toolkit Going to $195 in February With over a half-dozen new tools, the price of the Toolkit is going up to $195 starting in February. If you're interested but haven't bought yet, pick up a license now and you'll lock in your $150 subscription. 4. New Licenses Are Multi-Device & Sharable with Coworkers Lastly, based on the biggest piece of feedback I've gotten, with the $195 price-bump starting in February a single license will allow multiple installs, so that you can use on multiple devices and with members of your company. If you have a design staff with multiple users, it only makes sense that you're able to use and share files with coworkers. If you have a single-user license now and want to upgrade, shoot me an email at joe@meyerfire.com and we'll get the upgrade set up. Should you want to learn more about the Toolkit, you can do so here. Hope you have a great rest of your week! Now that I live with one hand in creating shop drawings and the other in consulting, I don't come across this question quite as often as I had. In general, people don't call unless they know they need fire protection help. When I worked for MEP firms, I came across this question all the time. As in evaluating this on every single project. "Does the building code require a fire sprinkler system?" The adopted building code is the first stop in determining whether a fire sprinkler system is required or not (not standards, such as NFPA 13). In the International Building Code, this is generally Section 903.2 for fire sprinkler systems. You'd first determine your building occupancy (from Chapter 3), then go to 903.2 to see if your facility's footprint is large enough, has enough occupants, or meets the other nuanced criteria to bring in a fire sprinkler system. I have gotten caught ignoring the special applications - in my case a windowless basement that didn't have enough openings which drove sprinkler requirements. We got sprinklers in, just later in design than I would have liked. This cheatsheet below is a summary of the requirements among various occupancies and other drivers for fire sprinkler systems, according to the latest IBC (2018 Edition). It is worth noting that local code adoptions, insurance requirements, or the International Fire Code can also introduce the need for fire sprinkler systems.
As you may know I'm a fan of cheatsheets, so I hope you find this helpful. If you think it'd be beneficial to also cover other IBC editions, let me know in the comments here and I can get that moving too. Thanks & have a great week! Oprah had an annual favorite-things list. I've always thought that would be fun to do - except I can't offer everyone a Pontiac G6. Sorry about that. My wife says the kids need to eat. I will however continue to make lists of my own. This one isn't necessarily a "favorite-things" but rather interesting topics and tools I plan to keep an eye on for 2020. A Long-Awaited Computer-Based PE Exam The Fire Protection Principles and Practice of Engineering Exam (PE Exam) will finally become computer-based in 2020. This has been discussed for many years and will bring Fire Protection in line with several other disciplines and the Fundamentals of Engineering (FE Exam). Likely a much bigger change to the 2020 Fire Protection PE is replacement of the treasure-trove of references (over 9,000 pages) into a single exam reference guide which is being developed by SFPE. This single resource will be all that is allowed in the exam room. While the exam focus and content should be relatively consistent from past years, preparation for 2020 will be a different challenge than in years’ past. Around here, I’ve already been contacted by numerous people seeking the publish date on both the 2020 MeyerFire PE Prep Guide and the PE Exam’s Reference Book. The 2020 MeyerFire PE Prep Guide will follow the official reference book by a month (which is rumored to debut sometime in Spring 2020). I’m keeping my fingers crossed that the official reference book will be early enough to give everyone ample time (including instructors) to study and absorb it. At least for 2020, the Fire Protection PE will only be given on a single-day (October 22, 2020). Going computer-based might someday afford year-round testing availability like the Mechanical PE Exam is starting this year. That will certainly be another interesting change when it happens. The Fire Protection PE Exam's joining the twenty-first century with its first computer-based exam in 2020. Viking’s New Window Sprinkler Viking just released a new listed Specific-Application Window Sprinkler. Use of window sprinklers have long been a strenuous and often misapplied technology, but the new Viking lineup could offer additional options in this space. I'm very interested to see how the new sprinkler gets used in the market. The brand-new window sprinkler is only the second entrant to a complex & niche application. If you haven't checked lately, it's already in our live Sprinkler Database. Nitrogen’s Rise Have you seen it? I have. Nitrogen inertion is becoming more and more commonplace each year. This year is the first I’ve seen a project specify a nitrogen-inertion system upfront with a dry-pipe sprinkler system. Finally! As an industry I feel like we're all slowly learning and educating owners on the major cost-savings these can have, but until recently I've yet to see them specified on a project. It's good to see other consultants getting traction with owners on the topic. Projects under the United Facilities Criteria (UFC 3-600-01) allow a hydraulic c-factor of 120 in dry systems with nitrogen included, which are now mandatory for dry systems. This is a great benefit I hope the NFPA 13 continues to consider adopting. It can be difficult enough to convey to owners the cost/benefits of avoiding corrosion in sprinkler systems with a higher upfront cost, but if we get a hydraulic kick-back for inclusion of nitrogen systems then the conversation could be made substantially easier with owners. Depending on the system size, a hydraulic benefit might help contractors to voluntarily provide nitrogen systems and save on pipe sizing throughout. New & Better Tools for Revit I live entirely in BIM (Building Information Modeling), so I’m always on the lookout for great Revit families, tools and workflows. The past couple years have really ramped up the race for fire protection tools in BIM, including Victaulic’s Revit Add-In, AutoSPRINK’s RVT lineup, HydraCAD for Revit, and a few others. I’m very encouraged that there is finally interest in this space and that the developers in it seem to be doing very well. Revit Add-In productivity-boosts have made even small projects like this home design I completed in 2019 possible at a very reasonable time and cost. I just started using the RVT platform in 2019 and have found major productivity boosts by doing so. If you use Revit and haven’t checked out these platforms, 2020 might be the year to check them out.
Why This Site Exists I don't (usually) just write to entertain myself. I put together this site to help start the conversation on fire protection. If you're relatively new around here - I'd like to introduce myself. I'm Joe. I'm no an end-all expert in the field, just a normal guy who loves being in fire protection. I worked for and learned under a couple engineering consultants before starting my own practice in 2019 where I now write, build tools and design full time. This site is all about bringing together experts from the different corners of fire protection to discuss and share best practices. We're all about improving your workflow and your knowledge with resources and ideas - plus giving a medium for you to share your expertise to everyone's benefit. Thank you for hangin' around and I look forward to sharing in a great 2020 with you! This time of year is just the best. I feel extremely fortunate to have three young kiddos at home, a supportive and all-around great family, and an extremely rewarding career in fire protection and doing what I do here at MeyerFire.com. Whether you subscribe, dabble occasionally on the forum, or just stop in to use tools here and there, THANK YOU for a really wonderful 2019. One of the tasks of wrapping up a year is revisiting what resonated the most in 2019 of all the content here. If you just joined in this year or know someone who would benefit from this content, please consider sending a link.
While we're at it, here are the Top Ten Tools & Articles of 2018 and the Top Ten Tools & Articles of 2017. Hope you have a relaxing and rewarding holiday week wherever you call home! |
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS