Standpipes: Floor vs. Intermediate-Level Landings

7/1/2019

 
This week I'm wrapping up some coverage of fire standpipe systems. In case you missed it, here are the recent articles on this topic thus far:

   An Introduction to Standpipes
   Addressing Egress & Clearances for Standpipe Hose Connections
   Standpipe Connection Location by Code Edition

Whether a standpipe hose connection should be located on a floor-level landing or an intermediate-level landing has been a classic tactical and design discussion in the fire protection community.

Defining Floor versus Intermediate Landings
A main floor-level landing is the horizontal portion of a stairway where the stair risers stop and occupants can enter a floor level, leave a floor level, or turn to walk on the stair itself.

Intermediate-level landings are the horizontal portion of a stairway where the stair risers top and occupants can turn to continue onto the stair.
​
Picture
Defining floor-level versus intermediate-level landings.
 
Landings offer a resting space when transcending stairs as well as limit the distance someone is likely to fall down a flight of stairs. Stairs that jog back and forth with landings offer some benefits. They help limit the building area dedicated to stairwells, they create a consistent door location on each floor, and they to help break up long stretches of stairs. 

Do hose locations matter?
They do. Hose connection locations have implications on the tactical approach for firefighters, the ease of installation for contractors, the complexity of design for designers & engineers, and the cost implications for building owners.

Fire Standpipe in Building
Standpipes at floor level landings offer a simpler overall installation with design benefits.

Benefits of Connections at Floor-Level Landings
Benefits to standpipe connections at floor-level landings include:
  • Avoid Crossing the Stair with Sprinkler Feeds: The main benefit to floor-level standpipe connections may simply be that it avoids the biggest drawback of intermediate-level landings: crossing the stair itself.

    Combination sprinkler/standpipe risers with floor-level hose connections can be equipped with floor control valves right above the hose connections. These floor-control assemblies can be easier to access and can run right into the floor-level ceiling it serves. No need to jog vertically to get into a ceiling, no need to run a sprinkler feed underneath and across a stair to get into a ceiling, and no need to carefully evaluate where knee-knockers and head-height issues could be created.

    Standpipes with floor-level landings can result in a much simpler overall design and installation.
Fire Standpipe Sprinkler System
Crossing the stair with sprinkler feeds from combination sprinkler/standpipe risers on intermediate-level landings can create head-height issues or knee-knockers, depending upon the approach. Standpipe hose connections at main-level landings help avoid these issues.

  • Easy to Supply: Supply feeds from the service entry or fire pump are often from the ground-level ceiling space which can tie right into a standpipe with a floor-level landing.

    Intermediate-level landings aren’t always located adjacent to rooms with ground-level ceilings. Some intermediate-level landings are located on the exterior of buildings and face away from the building, making it difficult to run a supply main (often 4 or 6-inch) to the intermediate landing.

  • Possibly more consistent hose location: Not all stairs have a single intermediate landing between floors. Stairs added to existing buildings, old buildings, or in unusual assembly buildings like stadiums, arenas and theatres can have multiple intermediate landings, be round, or not have consistent landings. Situations like this can make floor-level hose connections favorable in that they should be easier to find with consistent locations.

  • Shorter Hose Length Runs: One principle not often addressed is the hose length required to reach all portions of a building.

    The International Building Code allows AHJs to require additional hose connections when the most remote portion of a non-sprinklered floor is greater than 150 feet from a hose connection, or 200 feet for sprinklered floor (2000-18 Editions Section 905.4(6)). It may not sound like a big difference, but the 15-20 feet of additional travel distance to a hose connection could be just enough to require additional hose connections.​
    ​
Standpipe Hose NFPA 14
Connections at intermediate level landing requires that designers and engineers account
​for the additional hose length needed just to cross the stair. 
​

Benefits of Connections at Intermediate-Level Landings
With all the benefits to designers, installers, and overall simplicity, why would intermediate-level landings be considered? Mostly it’s about first responders and the tactical approach in firefighting.
​
Standpipe Intermediate Landing
Connections at intermediate-level landings offer more tactical than design benefits.

​Benefits to intermediate-level connections include:

  • Prevent congestion at doorways: During a fire, occupants could egress or queue at stair landings. Floor-level landings could be a congested area at this time that could make hose hookups difficult for first responders.

  • Keep firefighters below smoke plumes: Traditionally, with intermediate-level hose connections, firefighters will connect hose on the intermediate-level connection below the fire floor. As hot gases come through the stair door when people egress, this approach keeps firefighters out of and below the path of rising smoke coming through the door and up into the stair during a fire event.
 
Conversations with AHJs
Regardless of approach, code stipulates a prescribed method but allows the AHJ the latitude to shift the landing location as he or she sees fit. Like other nuances of suppression design, it can be very beneficial to make the call and confirm an approach well before submitting plans.
 
Other Considerations
Here are a few important considerations that accompany standpipe design:
​
  • Don’t forget the lowest-intermediate connection: NFPA 14 requires standpipe hose connections at the intermediate-level immediately below the floor level. If the ground-level of a building does not have an intermediate-level landing below it, then it still must have a hose connection on that floor level. Otherwise, firefighters would have to climb stairs to reach a hose connection which is opposite of the intended firefighting approach.

  • Roof Access: Where roofs have a slope less than 4 in 12 (a 33.3% slope), the IBC requires a hose connection at the highest landing of a single interior exit stairway serving the roof, or a hose connection on the roof where no exit stairways serve the roof (IBC 2000-18 Editions Section 905.4(5)).

  • Horizontal Exits, Covered Malls, Exit Passageways: While I focused on stair-landing hose connection requirements, there are important other locations where they’re required as well. Reference IBC Chapter 4, Section 905.4, and NFPA 14 Section 7.3.2 (2003-2019 Editions) for all required locations.

Enjoyed this content? MeyerFire is all about starting the conversation on fire protection. If you found this read helpful, share on LinkedIn or send to a colleague.
​
Don’t get these articles sent to you weekly? Subscribe here and join us in creating better fire protection.
Robert Shieh
7/12/2019 03:48:10 pm

Is there a reasoning why we only need 1 standpipe connection on the roof?


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT