Sprinklers Required in Electrical Rooms? [PDF]

8/17/2022

 
Awhile back I wrote a piece on sprinklers in electrical rooms. At the time I was asked relatively frequently about when sprinklers are required or allowed to be omitted in electrical rooms.
 
I guess intuitively, we recognize that electricity and water don’t mix well. We don’t want to address one problem (fire) by creating a new hazard (electrocution) with water in areas that it doesn’t have to be.
 
In principle, I personally have just about always provided sprinklers in electrical rooms unless they were specifically requested not to be provided by the owner or AHJ; and in those cases, I followed the code path in the IBC or NFPA 13 accordingly.
 
It seems as though the premise behind not including sprinklers is when the type of electrical equipment present a relatively low hazard or fuel source, and there is no storage. In that situation, a combination of 2-hour fire-resistance-rated enclosure with approved fire detection (assuming a smoke and/or heat detector here) will mean that a fire within the room will be recognized, and the rest of the building will not be compromised as a result.
 
Providing pipe within an electrical room isn’t always an easy feat. NFPA 70 tells us that electrical equipment requires dedicated zones, and pipe shouldn’t be run above panels without drip pans or other methods of avoiding drip hazards above electrical equipment.
Picture
Now are sprinklers in electrical rooms problematic? Generally not (in my experience).
 
Can pipe routing be made to avoid electrical equipment? Usually yes. I try to only run one branch line into the room, most often above the door (since no electrical equipment is on the door), and stick pipe only above walking pathways within the room.
Picture
Does the code or standards express any concern or guidance on this? Yes, both the IBC and NFPA 13 address the situation.
​
One line that is included in the IBC specifically says that sprinklers “shall not be omitted from any room merely because it...contains electrical equipment”. To me, that’s a fairly explicit way of suggesting that the presence of electrical equipment alone isn’t a justification for omitting sprinklers. Now there are code allowances and necessary provisions to do so, but the suggestion is not to simply avoid sprinklers just because there is electrical gear.
 
Despite it being awhile since that article, I have had a few requests to make this one into a flowchart, which I’m happy to present today. A special thank you to Alex Riley, PE, who contributed to the code research for this flowchart.

Picture
GET THE FLOWCHART PDF
Char
8/17/2022 10:55:40 am

When asked to omit as an AHJ I will never completely allow them to be omitted. Depending on size and the room and assuming it’s a 2 hour rated room, I have allowed just sidewalls over the doors. It’s out of the way and effectively offers sufficient coverage, even if there are some shadows. And add smokes of course. This offers early detection and protection of the weakest element (the door) under ideal conditions, such as all fire stopping is in place.

Why might you ask will I never totally eliminate given that there is usually no fire load? Because electrical rooms become storage rooms once the AHJ leaves.

Shawn Daly
8/18/2022 10:52:49 am

The final choice for the 2019-2022 NFPA 13 thread concerning storage seems confusing. It says "Is storage permitted in the room?2" but the footnote 2 confirms storage is never permitted in such a room by NFPA 13 2019. Additionally, shouldn't the answers be swapped? If the answer is NO, shouldn't the flowchart indicate sprinklers are not required (green selection?)

Joe Meyer
8/19/2022 04:21:56 pm

Hi Shawn!

Thanks for the feedback. In 2019, the committee changed the standard to say that no storage is permitted whatsoever, including "noncombustible" storage.

And yes, we had a few quick comments about that updated and if you download it again you'll see the corrected version. We posted an email about this too.

Thanks so much Shawn!


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT