MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

New Hose Valve Requirement for Forward-Flow

2/21/2024

 
Last week we updated the NFPA 13 shop drawing checklist with references to NFPA 13 2019 and 2022 Editions.
 
While code updates like this are traditionally modest, the NFPA 13 Committee revamped the entire list of requirements for “working drawings” in the 2022 Edition. It was gutted.
 
We’ll expand on that more next week.
 
This week I’d like to key in on one very impactful change that I think will affect many of us in how we design systems going forward.
 
FORWARD-FLOW REQUIREMENT HISTORY 
A forward-flow test has long been required in NFPA 25 (dating back to at least 2002).
 
The purpose of the test is to verify that a backflow preventer is capable of fully-opening in a fire – or at least to the extent that it allows enough water to flow to satisfy the sprinkler system’s demand.
 
A means of conducting a forward-flow test has long been required, but not necessarily readily implemented. For many lower-hazard systems, it was a test that was possible by flowing out of a fire department connection or main drain.
 
WHY NOT FLOW OUT THE FDC?
White it was possible to do a forward flow through an FDC, this approach was never practical. I can’t stand on a high horse here – it was the approach I long used from a design perspective.
 
It’s not practical because conducting a forward-flow test out of an FDC would typically require a system to be shut off, drained, check valve reversed, put back into service, tested, shut off, drained, check valve put back into place, and put back into service. And that was if the clappers on the FDC were removed or restrained in a way to allow enough water to pass through. It’s a tall ask.
 
USE THE MAIN DRAIN?
Flowing out the main drain could be a solution for forward flow, but practically speaking how much water can flow through a 2-inch main drain, especially if there’s an OH1 or OH2 demand? Do we have a way to verify how much water we’re flowing, so that we know the test passed?
 
Some have used our own calculator to estimate the amount of water flowing through a main drain by using this orifice flow calculator - https://www.meyerfire.com/blog/a-new-fire-sprinkler-test-drain-flow-calculator
 
That calculation is based on pressure flowing through an opening – either an orifice or pipe diameter – and doesn’t incorporate the losses that occur through the length of a main drain or the fittings along the way. It’s going to be too generous on the amount of flow coming through a main drain – which is good if we’re wanting to know how much water a plumbing drain needs to accept – but bad if we’re trying to prove forward flow based on it.
 
I would suspect that a supply-side calculation (where the available pressure dictates the flow) through a fully-open main drain would be the best way to predict hydraulically how much flow a main drain could flow. If that’s well above the system demand (including hose allowance), then a main drain could be the means to flow.
 
But a 2-inch main drain is very likely not an answer for forward flow for most systems.
 
I’ll leave that discussion open – perhaps there’s a tool we could construct to account for main drain losses and perform that supply-side calculation.
 
PERMANENT MEANS FOR FORWARD-FLOW
Somewhat fortunately for those of us who like black and white guidance (myself included) –the NFPA 13 committee closed up the gray area in the 2019 Edition by requiring that an arrangement for conducting the forward flow test, at the minimum flow rate of the system demand (including hose allowance), would be provided “without requiring the owner to modify the system to perform the test.”
 
This comes from NFPA 13-2019 Section 16.14.5.1.1.
 
In the 2022 Edition, the committee went further.
Picture
A fixed means of forward flow, like hose valves on a test header or system riser, will become far more commonplace once the 2019 and 2022 Editions of NFPA 13 are adopted and enforced.
​

A 2-1/2” HOSE CONNECTION FOR EVERY 250 GPM 
A test connection is now required for forward flow tests, where now a 2-1/2” hose valve is required for every 250 gpm (950 L/min) of system demand. This total flow must include the hose allowance where applicable. Generally, if there are interior hose valves, then this would need to get added in.
 
So - an Ordinary Hazard Group I system that may have a demand of 270 gpm (with 250 gpm outside hose allowance), would still need two 2-1/2” hose valves for the forward flow test fixed in place downstream of the backflow preventer.

For larger systems, or those with interior hose connections? We could be looking at three or more hose connections just for forward flow. This comes from NFPA 13-2022 Section 16.14.5.1.1. That’s a noteworthy change.
 
For a code-minimum, sprinkler-system-only type of project, that’s a tangibly different cost and look to a part of the system.
 
Does this have to be a test header on the outside of the building? Not necessarily, though that would be nice for future testing.
 
Could the hose valves be on a riser in a room that has exterior access? Depending on the room and goals for the building – that could be reasonable.
 
There are two provisional sections that allow existing hose connections to be used for the test (16.14.5.1.2), and other means to test are allowed “as long as the system doesn’t require modification to perform the test and is sized to meet the system demand.” The later comes from NFPA 13-2022 16.14.5.1.3.
 

Picture
Is a fixed test-header on the exterior of the building required?
No, but it could be convenient for future testing in areas where theft is less of a concern.
​
HAVING TEETH 
But in general – we don’t have a “use the FDC” workaround any longer.
 
For those in IT&M, we finally have a sticking point to give an ability to do this test without tinkering with the system.
 
For those in design, we finally have a magic section of code that we can show to justify providing a means of the forward flow test.
 
For those in review and inspection, we have the teeth to enforce it.
 
Hopefully, in the long-run, having systems tested for forward flow will identify backflow preventers aren’t functioning and we no longer have them in buildings ready to fail when a fire happens.
 
Hopefully, this pushes buildings to a bit safer and helps us a be a little more confident in the system’s ability to fight a fire.
 
SHOW ON WORKING DRAWINGS
While the means is an installation question – NFPA 13-2022 Section 28.1.3(18) requires that working drawings locate and identify the means of forward flow.
 
It’s no longer a “how do you plan to do this test?” type of comment and will soon be “show the location and label the means of forward flow, per 28.1.3(18).”
 
MY FORWARD-FLOW STORY
Are we really just testing the backflow preventer here?
 
Well, yes. In part.
 
But actually flowing an entire system demand tells us quite a bit. It means that our water supply is capable of flowing the full system demand, and all the pipe in-between the water supply and the backflow is also open-enough to flow the full system demand.
 
I once had a project where a tap was made to the city supply main. It was a live tap or “hot tap,” where a drill punctured the side of the city main and a new 6” street valve was installed and our 6” underground came in and fed the building.
 
It was a brand-new 3-story building that was going to have overnight guests.
 
The tap wasn’t fully-made. In fact, as we found out later through a lot of cost and trouble, only a ¾” pilot drill bit made it through the city main. It wasn’t all the way drilled-in.
 
Instead of a 6” tap, we had a ¾” tap.
 
Static pressure to the building was fine.
 
We could run a main drain test just fine (the residual dropped, but the main drain isn’t flowing all that much). Remember – the initial main drain test sets the threshold to check against in the future.
 
We could flow the inspector’s test just fine.
 
When we conducted the forward flow test and opened a couple 2-1/2” hoses – we had no water. No pressure at all.
 
It wasn’t until we conducted the Forward Flow test that we knew there was a problem.
 
Where it not for the Forward Flow test, we would have had a brand-new building, which, by all other measures we would have thought was designed and installed properly – all protected by a system with water that was squeezed through a ¾” hole.
 
While the backstory of testing the Forward Flow may be more about the backflow preventer, the test does give us confidence in the supply up through the backflow preventer being able to handle the system demand.
 
If we measure the flow coming from the forward flow, and also stick calibrated gauges on the upstream cock and downstream cock of the backflow – we can know a whole lot about the health of our system that day.
 
What’s the static pressure? What’s the loss through the backflow? What’s the base of riser pressure at the system demand? How does that compare to our design?
 
We can get a lot of information just from this one test.
 
END SOAPBOX
That’s my soapbox rant for today. As with all we write and do on this site, I hope you’ve found it helpful.
 
Keep fighting the good fight, and have a great rest of your week.
 
- Joe ​
M. Newell
2/21/2024 11:02:20 am

I believe it is noteworthy myself included “borrowed” your design basis for the normally closed butterfly with a tee setup to flow out of a single clapper FDC as the easiest option.

This in my opinion would meet the requirement of the alternate means as discussed in the annex A16.14.5.1.3. It’s almost like it was written based off your article of forward flow testing from 2018.

We are still seeing a lot of installations that do not have means for forward flow testing so hopefully the expanded language and requirements will catch the eye of review officials.

kevin shaver
5/7/2024 08:59:56 am

Be careful when planning to flow out the FDC if it is an older Siamese they have 2 flappers inside causing it to block the flow

Sean
2/21/2024 11:21:18 am

I have commonly seen the use of a FDC check valve bypass, or "forward flow loop". This allows the system to perform the forward flow out of the FDC without making modifications. This is also supported by NFPA 13 Annex section A16.14.5.1.

Dwight Havens
2/21/2024 03:51:43 pm

Used the forward flow loop test to backflow out of the FDC with a single clapper. Worked great unless the turbulence caused the single clapper to slam shut in the side of the FDC being used to flow. Talk about water hammer.

A. Barnhizer
2/21/2024 04:06:36 pm

You've stated that the minimum flow rate is the system demand and MUST include the hose allowance. However, the standard then states "where applicable". NFPA 25 (2020) 13.7.2.2 states that the hose stream demand only be included when there are hydrants or inside hose stations located downstream of the backflow. I would have been nice if NFPA13 included the explanation of when the hose allowance is to be included in the minimum flow rate.

Joe Meyer
2/21/2024 04:18:10 pm

Yes - I think you're right on this.

Hose Allowance, for some (many?) systems, does not have an Inside Hose Allowance but it's entirely Outside. If there are no hose connections or hydrants inside, then the Hose Allowance would not apply here.

If there is an Inside Hose Allowance or Hydrant downsteam of the backflow, then those values would apply.

I was wondering the same and just had it confirmed with others I trust. Thanks for this - will update the article.

Cooper Ryan
2/21/2024 10:43:26 pm

My thoughts exactly. Backflow and underground would not necessarily be sized for the hose allowance. Thanks.

CONNOR R
2/21/2024 04:40:30 pm

I don't necessarily agree that the demand must include the hose stream for determining minimum flow and number of hose valve.

NFPA-13-2022 16.24.5.1 states "A test connection shall be provided downstream of all backflow prevention valves for the performance of forward flow tests required by this standard and NFPA 25 at a minimum flow rate of the system demand including hose allowance where applicable."

Note that you need to include the hose stream allowandce "where applicable" and the reference to testing per NFFPA-25.

NFPA-13-2022 Section 16.14.5.1.1 states to include a number of hose valves sized by the flow rate of "the system demand including hose allowance where applicable."

Note again, "where applicable"

NFPA-25-2023
Chapter 13 Common Components and Valves
13.7 Backflow Prevention Assemblies
Section 13.7.2.2 states "Where hydrants or inside hose stations are located downstream of the backflow preventer, the forward flow test shall include hose stream demand.

My interpretation is that the hose stream is only "applicable" when there are hose stations or hydrants downstream of the backflow preventer.

Connor R
2/21/2024 04:41:47 pm

Just realized this was already mentioned. I agree with the above comment threads on this topic.

Robert Bennett
2/27/2024 08:55:27 am

There is another way to both insure the flow is provided and the cost contained. We have used this approach with success in our county of 750,000 people. It does take some explanation to the designers, but once they get the idea it is easy.

Treat the main drain as a discharge volume and calculate the friction loss in the the pipe as a function of the quantity of water flowed. If a 2 inch main drain will not supply the required flow volume we encourage the designer to upsize the drain line to whatever size in needed to provide the flow. Adding a Tee or other form of water diverter reduces flow damage and further controls discharge direction.

In general terms for most systems with a 4 inch riser a 3 inch main drain will provide the needed flow for forward flushing of BPD. Give it a try on the next system you design and see how it calculates out. RJB


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT