MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Solutions for the Overlooked Forward-Flow Test

1/10/2018

 
Backflow preventers are included in fire sprinkler systems to protect public health from contamination by preventing water flow back into the public water grid. In an opposite manner, the forward-flow test for backflow preventers was created to ensure the sprinkler system can be served by enough water in a fire condition. 

Backflow preventers (double check or reduced pressure zone) type have potential to fail closed where not exercised over long periods of time. Reduced pressure zone backflow preventers are particularly susceptible with the potential for development of closed memory in their spring mechanisms.
Fire Sprinkler Reduced Pressure Zone (RPZ) Backflow Preventer
Reduced Pressure Zone type backflow preventers are especially important to exercise spring mechanisms to ensure full forward flow will be available in a fire condition (Ames/Watts 4000SS Model Shown)

The Test Requirement
​

NFPA 25 (2002 Edition Section 12.6.2.1, 2008-2014 Section 13.6.2.1, 2017 Section 13.7.2.1) requires annual testing of the backflow preventer at the designated system flow rate, including hose demand, where hydrants or inside hose stations are located downstream of the backflow preventer. Where a means is not provided at maximum demand, test shall be conducted at the maximum flow rate possible (NFPA 25 20002 Edition Section 12.6.2.2.1, 2008-2011 Section 13.6.2.2, 2014 Section 13.6.3, 2017 Section 13.7.2.3).
​
Fire Sprinkler Double Check Backflow Preventer
Section of interior of Double Check Backflow Preventer (single tube style shown from Ames/Watts 757 Model)

The Design Requirement
​

While testing can be conducted at the maximum attainable flow the system will allow, the system must be designed with a means of conducting this test. In my experience this is one of the most often overlooked requirements within fire sprinkler system design. 

NFPA 13 now requires a way to test the forward flow downstream of all backflow prevention valves at a minimum flow rate of the system demand including hose allowances (2013 Section 7.6.3.2.1, 2016 Section 8.17.4.5.1). Editions of NFPA 13 before 2013 simply stated that the backflow prevention assembly shall be forward flow tested (2002 Section 16.2.5.1, 2007-2011 Section 10.10.2.5.1).

Design Solutions to Accomplish the Forward Flow Test

Option 1: Use the Annual Pump Test and Header (When a Fire Pump is Present)


Perhaps the easiest option to conduct this test is to use a fire pump's test header to flow water out of the building. If the backflow preventer is installed on the service/suction side of the fire pump, then a separate forward flow test is not even required as the annual fire pump test already causes the backflow to be tested (NFPA 25 2002 Section 12.6.2.1.4, 2008-2011 Section 13.6.2.1.4, 2014 Section 13.6.2.1.2, 2017 Section 13.7.2.1.2). However, if the backflow is on the system/discharge side of the fire pump, then running a feed with a normally-closed valve to the fire pump test header allows the test header to serve both the annual fire pump test or the forward-flow backflow test.

Option 2: Bypass the Fire Department Check Valve

NFPA 13 (2016 A.8.17.4.5.1) poses one option to achieve a means for this test with the use of a bypass around the check valve serving the fire department connection. This bypass would need to include a supervised indicating valve that is normally in the closed position.

Fire Sprinkler Riser Assembly
Option 2: Provide a bypass around the check valve serving the fire sprinkler system with a supervised, normally-closed valve to enable forward flow tests out the fire department connection.

Providing a bypass around the check valve enables flow to be run out the fire department connection. This works well to take water outside the building and can be directed with testing hoses, however, care should be taken to address clappers inside the fire department connection when they are provided. Some clappers may be removed and replaced in the field to allow a full flow, while others may be directed to allow flow through one side of the fire department connection. Depending upon the system design, this may be a fairly easy method to meet the requirement.

​Option 3: Provide Hose Connections for Testing
​

If a riser has exterior access, another method of allowing testing of the backflow would be to provided hose valves on the riser itself. Hose connections could be made onto the valves and run to the exterior of the building for the test. Typically, each 2-1/2 outlet should be able to provide 250 gallons per minute of flow. Small low-hazard systems might only require two hose connections to enable this method.
Hose Connections on Fire Sprinkler Riser
Option 3: Provide hose connections on the system riser itself allows hoses to be attached and run out of the building.
Option 4: Size the Main Drain to Handle the Forward Backflow Test
​

NFPA 13 suggests that upsizing the main drain would provide a means to conduct the backflow test (2016 Section A.8.16.2.4.2). Depending upon the hazard of the system, this may result in a significantly larger opening in the exterior wall for drainage and for most systems would certainly be larger than a typically large 2-inch main drain. I can't imagine many architects like the look of a large downspout nozzle on the building, but it could be much more sightly than several of the other options listed.

Option 5: Install a Designated Backflow Test Header

One clear option that is always available is using a designated test header specifically for the forward flow test. Just like a fire pump test header, this would result in a through-penetration to the exterior where water can be clearly directed. Signage is important for any exterior testing equipment to clearly differentiate itself from fire department connections.

Fire Test Header
Option 5: Perhaps the cleanest option, run a dedicated test header to the exterior of the building for the backflow preventer achieves the intent of the forward backflow test

Option 6: Use Standpipe Hose Connections (where provided)

Lastly, where standpipe hose connections are already available in the building, these outlets could provide enough flow to test the backflow preventer. This test could be the most difficult to achieve, however, as doing so would require a coordinated effort with multiple hoses in different locations to flow outside the building.
Fire Standpipe Hose Connection
Option 6: Using standpipe hose connections is a built-in way to run the forward flow test for backflow preventers, but requires multiple hoses and a coordinated effort for testing

Summary
​

The forward flow test for backflow preventers is one of the most commonly overlooked requirement for fire sprinkler systems which could impact the actual performance of fire sprinkler systems. Solutions, while cost impacting, exist and are readily achievable to meet the requirement.

Interested in more articles like this? Subscribe for free here.


More Information

​NFPA 13: Standard for the Installation of Sprinkler System, 2013. National Fire Protection Association, 2002-2016 Editions.
NFPA 25: Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection, 2002-2017. National Fire Protection Association, 2002-2017 Editions.
Trieber, Bob. “Forward Flow Testing of Backflow Devices.” SQ, no. 4, ser. 2010, July 2010, pp. 11–12. 2010, doi:01/10/18.
DAVID
5/30/2018 11:43:01 am

I have seen from both the contracting perspective, and the engineering perspective, that the movement towards compliance has been…glacial, as slow as branch line restraint. I have seen the full range of methods by which to comply with the “means” to conduct this test, from the cheapest contractor, to the detail specifying engineer requirements. I would be interested on your thoughts on the following items that have been bugging me:
I have read that the intent of NFPA is to exercise, as you say, the backflow, and I agree. However I have seen some specifying engineers as a few AHJ’s require this as a means to test the psi loss of the backflow. I have seen specs go as far as to require signage to post the result of such testing for comparison later.
Is the test required for initial system acceptance? I believe 13 says yes.
Do you think it is required for backflows on 13R systems? I think 25 may indicate so, if not in 13R itself.
(BTW, kudos to the illustrator of these blog posts- nice work.)

Jessica
6/20/2019 10:18:25 am

I really enjoy reading your questions/comments! I think it's time you write a book Dave!

Mike
11/12/2019 10:33:53 am

I just wanted to piggy back on the comment regarding the illustrations on this site. I'm always impressed by the sketches shown on the site. I'd be very interested to find out how they're done. Are they truly sketched by hand? Or are they section cuts of highly detailed models? Very interested... they look great either way.

Joe
11/12/2019 10:39:35 am

Photoshop, actually. Some of these are by me (Joe Meyer), others I've hired illustration help, but they're completed the same way. We use models or images as references and hand sketch onto tablets using photoshop. The color gradients and depth are done afterwards.

Glad to hear you enjoy the images! Many more to come!

Gillian Babcock link
12/20/2018 12:19:38 am

My dad wants to make sure that the piping system at home is in perfect shape. It was explained here that when planning to have a backflow preventer, the machine and design should be tested. Furthermore, it's recommended to hire professional plumbers for quality backflow preventer installation services.

Bruce Seiler
9/10/2019 08:57:42 am

I agree, this has been a highly overlooked requirement in NFPA. I have been implementing the forward flow test in our department for about 15 years now and still have fitters and some project managers question the reasoning behind the requirements. There are a lot of AHJs which still don't know about the requirement and don't understand the testing of the backflow or pressure reducing valves for that matter. Education is key. We always invite the local AHJ and owner representative out to witness the forward flow test to educate those who are not requiring the test. Our main choices are the hose valve connections off the riser or a test header. My concern with the FDC clapper has stop us utilizing this as an option, but we have been asked to do this in the past. There tends to be more work involved during testing when this option is chosen.

Education is the KEY.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT