|
It does not necessarily come up often, but the volume of a fire sprinkler system does carry several requirements. Dry and Preaction systems carry water delivery requirements, while all systems carry requirements for drainage. Today I'm summarizing requirements related to when volumes of fire sprinkler systems are important to consider. Dry System Capacity Systems under 500 gallons (1900 L):
Systems between 500 and 750 gallons (1900 - 2850 L):
Systems over 750 gallons (2850 L):
Hazard No. of Remote Sprinklers Initially Open Max. Time of Water Delivery Dwelling Units 1 sprinkler 15 seconds Light 1 sprinkler 60 seconds Ordinary I 2 sprinklers 50 seconds Ordinary II 2 sprinklers 50 seconds Extra I 4 sprinklers 45 seconds Extra II 4 sprinklers 45 seconds High Piled 4 sprinklers 40 seconds Note for Dwelling Units: Dry systems must discharge water in 15 seconds, regardless of system size (NFPA 13 2002 11.2.3.9.1, 2007-2016 7.2.3.1). Inspector's Tests are used to test water delivery times for dry systems when water delivery time test is required. See this article for details and components on inspector's test and drains. Pre-Action System Capacity Single-Interlock and Non-Interlock Systems:
Double-Interlock Systems of 500 gallons or less (1900 L):
Double-Interlock Systems over 500 gallons (1900 L):
Dry and Pre-Action System Drainage Auxiliary Drain Location:
Trapped Sections less than 5 gallons (20 L):
Trapped Sections more than 5 gallons (20 L):
Wet System Drainage
Trapped sections of pipe less than 5 gallons (20 L): One of the following is required (NFPA 13 2002 8.15.2.5.2.3, 2007-2016 8.16.2.5.2.3.):
Trapped Sections between 5 and 50 gallons (20 - 200 L):
Trapped Sections 50 gallons (200 L) or more:
Subscribe & Share Want more like this? Subscribe to our free weekly articles here. Already subscribed? Send to a friend or share on LinkedIn.
Mike
2/21/2018 08:11:43 am
Great summary Joe!...
Noah
2/22/2018 07:17:41 am
Mike,
Mike
2/22/2018 09:08:30 am
We used the Victualic model accelerator. The tech rep for Victualic advised that there is a nut at the bottom of the unit that can be loosed which will change the sensitivity of the accelerator. The unit will then react to 3-5 psi drop, rather than the out-of-the-box 2 psi drop. 2/22/2018 08:27:26 am
Great Article! I don't do residential, so I was not aware of the 15 sec. water delivery requirement for dwelling units. I am always amazed at what I find in the field when it comes to drainage. Careful planning to achieve drainage could have eliminated many of the auxiliary drains I find. It has been a long time since I have seen an auxiliary drain piped to an accessible location.
Ed duran
3/7/2018 08:31:04 am
Will you share it?
Joe Meyer
3/7/2018 10:38:07 am
Stay tuned in the next few weeks via the blog; I'll have some opportunities to get all of these calculators. Thanks Ed! Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
November 2026
|
RSS Feed
