An Open-Spec for Fire Sprinkler Systems - Part II

5/8/2024

 
Last week I posted the start of an open specification and asked for feedback - and boy did you all not disappoint!

If you haven't read that post, it's where to start. We laid out a few ground rules about what we're trying to achieve.

I genuinely appreciate the review, the comments, and the emails. I'm very encouraged by what we'll be able to build together that can improve things for all of us.

Who knew putting together specifications could be so fun? Joking - sort of.

As you're able to skim through this updated draft, which now includes Part 1 (General) and Part 2 (Products), here are some of the areas worth paying attention in a little more detail:

#1 - CHANGED SECTION NUMBER
We've updated the specification section number to reflect that this isn't just a wet-pipe specification; it's intended to consolidate many pages of redundancy into our main goal; a concise, easy-to-read and easy-to-edit specification.

#2 - NOTE TO NOT FALL BELOW CODE MINIMUM
There's a line added under C in the "1.1 DESCRIPTION OF WORK" that reads "at no time shall work be less than the applicable codes and standards listed below. Proposed alternatives, discrepancies, or questions shall be addressed by written Request for Information."

My goal here is twofold; one is that we're protecting the consultant and enabling the contractor to push back in written form. 

At the end of the day, we need a code-compliant system. The days of turning a cheek or intentionally being above code because a PE said so should be over. 

The concept with this inclusion in the specification is that if the contractor sees something (anywhere) that is less than code, then they have an avenue to have it addressed formally and an opportunity to clean it up in the project.

On the opposite side, the consultant has some relief in that they're clearly not advocating or instructing the contractor to fall below code unless it's in approved written process (such as an approved code-alternative).

I hope this to be a win-win opportunity for code-compliance at the end of the day. Like the others - curious on your take.

#3 - OPTION FOR PROFESSIONAL ENGINEER TO BE AN FPE OR "KNOWLEDGEABLE AND EXPERIENCED" IN FIRE PROTECTION
There's a tangible value to being a Fire Protection Engineer (informally an "FPE") specifically. An over-generalization would be that the Engineer has taken the time to study and pass the Fire Protection P.E. Exam, which itself is no small feat. 

With that effort and focus (which often takes months of preparation even for seasoned Engineers) there's a line in the sand that speaks to that individual 'owning' fire protection as a key area of focus and effort. 

Being an Engineer who passed the Fire Protection P.E. Exam doesn't make someone more knowledgeable (outside of learning many new facets while studying) nor better than another Engineer, but it does reflect a certain level of dedication to the fire protection field specifically.

That said, we as an industry have far fewer Fire Protection Engineers than Professional Engineers in other disciplines (my at least an order of 10-to-1), so mandating that all shop drawings be performed by or under the purview of a Fire Protection Engineer can be impractical.

It's a bigger discussion point for sure, but I've modified the specifications to either call for an FPE specifically, or to mandate a Registered Professional Engineer "who is knowledgeable and has experience in the field of Fire Protection."

I'd be curious on your take with this as well.

#4 - MOVED QUALIFICATIONS TO 1.5 QUALITY ASSURANCE
More of a practical shift here, we had a few requests to move the licensing and qualifications to the Quality Assurance section in 1.5 and out of the Submittal section of 1.4. Seems to make more sense here.

#5 - ADDED PART 2 FOR PRODUCTS
Since last week we've also drafted Part 2 where we cover Products. This should add a little more 'meat on the bone' and probably queue up plenty of contention points. 

Let me know what you like and what specifically you would change - all for building a better industry. Click below to view, and thank in advance for helping bring to life a needed resource!
Picture
chad
5/8/2024 12:01:30 pm

I applaud your effort to define the RDP out. The phrase "knowledgeable and has experience in the field of Fire Protection." Is too vague. It will be taken advantage of.

IMO, there should be experience and con ed documented. With an FPE you know they have sprinkler experience and understand the why. Not as clear with other RDPs.

I am not against it, there are some Mech Engineers who regularly do FP systems and can keep up with the FPEs.

Joe Meyer
5/15/2024 09:39:31 am

Hi Chad,

I agree on this; what phrasing (if any) would you propose on how to qualify a Professional Engineer who is not licensed in fire protection?

Before, it read "knowledgeable and has experience in the field of Fire Protection."

Couple possibilities:

(1) "who has minimum four years documented experience exclusively in a fire protection role"

(2) "and who has passed the CFPS, NICET Water-Based Layout III exam"

I guess the key question is - for someone who is not licensed specifically as a Fire Protection Engineer (Fire Protection P.E. Exam) - how do you know they're qualified?

If their responsibilities overlap multiple disciplines (mechanical, plumbing, or fire), how would you be able to differentiate qualifications in a quantifiable way?

Chad
5/15/2024 01:00:54 pm

Joe,

You make a good point here:

If their responsibilities overlap multiple disciplines (mechanical, plumbing, or fire), how would you be able to differentiate qualifications in a quantifiable way?

I am jaded by bad plans by non FPE PE's I guess.

I wonder if NICET Level III's for some work, like renovations where the hazard does not change, does that really need a PE? A fair chunk of work is renovations with no hazard change, so I think it does not. Of course it doesn't hurt for an FPE to review their work product, I acknowledge that's how it should be in a perfect world.


Your revised wording is also better.


Regarding material-

FDC- call out the correct labelling such as AUTO SPRK, AND STANDPIPE etc... or is that too much detail?

Jerry Clark link
5/8/2024 12:55:15 pm

For #3, maybe consider adding the term "Qualified Design Professional". I'm the AHJ for a NASA center in California, and the Agency adopted this term in our fire protection standard to take advantage of the licensing requirements for C-10 electrical, and C-16 fire protection contractors, which can save money and streamline smaller projects. We do limit their designs to simple modification of fire-rated construction, fire detection or suppression systems, or life safety systems in other than new construction or major renovations.

Chris Miller
5/8/2024 04:12:40 pm

Fire Protection backflow preventer should be here. We want RED backflow preventers, not BLUE ones. We need the fire protection flow data that comes with RED preventers.

The discharge of a RP can be a huge deal, We should add some more emphasize here so the Fire guy goes to see there is adequate drainage during bid time. There is frequently not.

Should standpipes be included in this section.....wet and dry. Same materials, but different reference standard.

Should Galvanized pipe be included for Dry systems? Where does the nitrogen generator and air mainteance devices go? Maybe a 2.8 Section that says Dry Pipe Accessories.

Great work....keep it flowing...

Chris



Brett
5/10/2024 01:03:54 pm

Joe,

A few suggestions I have:

To align with CSI recommendations and how the DoD is slowly updating their specs, I suggest writing in imperative mood when possible and using the word "must" instead of "shall". For example:

"Pipe and fittings for the fire sprinkler system(s) shall be in accordance with NFPA 13" becomes "Provide pipe and fittings for the fire sprinkler system(s) in accordance with NFPA 13."

Is this supposed to include standpipes or just basic sprinkler systems? NFPA 14 is referenced, but there are no hose valves and many of the requirements point to NFPA 13 when it wouldn't apply in a standpipe only system.

Add an option to refer to the drawings for applicable codes and standards.

Control valves item 3 isn't a full sentence.

Include schedule 30 pipe as an option.

Include manual air vents as an option.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT